This is probably a simple question for you guys.
Can anyone tell me that the max trip current should be set at, the book just says its variable and can be set to correct level, but what id the correct level?
The term "Hi-pot" implies that you are in USA/Canada. Can't help you in that case, someone else surely will.
For what it is worth, i give below an extract of IEC 60947-1 which specifies 100mA for power-frequency tests. Seems rather high to me, but there it is ...
The relay should be set as per the current rating of the equipment. The condition of the equipment under test would decide the current drawn from the High voltage test source. Generally the charging current drawn depends on the capacitance of the equipment under test and the test voltage. For example a conventional High voltage source may not be able to supply the charging current drawn by a large size generator ( more so when the windings under test are water cooled). In conventional windings also if the outer surface of the windings are badly contaminated then also it may draw heavy current from the HV source. So best way would be to go as per the recommendations of the manufacturer of the HV source manufacturer.