Anonymous Poster #1

Life of the Maintenance-Free Battery

03/31/2011 4:00 AM

I need help regarding the maintenance-free batteries, we are connected the batteries with UPS & in continuous charging for full days/weeks the power failure is very rare condition.

My questions are

1. My battery life is less than the manufacturer's data ,I need to increase my battery life,what are the actions i have to take.

2. The life of the battery decides which factors.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#1

Re: Life of the Maintenance-Free Battery.

03/31/2011 7:01 AM

Research this site...

http://batteryuniversity.com/

Reply
2
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Life of the Maintenance-Free Battery

03/31/2011 3:29 PM

By battery life what are you referring to? The age of the battery or the AH output? By maintenance free is it a gel cell or sealed lead acid? Anybody ever check the charger output to ensure it's charging to spec? You said batteries are they charged in series or parallel? If in series just one bad battery can reduce the total output. How old are the batteries?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply Good Answer (Score 2)
2
Active Contributor

Join Date: Sep 2010
Location: Hyderabad
Posts: 11
Good Answers: 1
#3

Re: Life of the Maintenance-Free Battery

03/31/2011 11:55 PM

My Ans are

1 )The designed life of the battery can be achieved by following manufacturers O & M.

2) The life of the Battery decide the following factors,

a)Number of cycles (charge/discharge).

b)In each cycle depth of the discharge.

c)In each cycle capacity of charging.

d)Charging current limits.

e)If any over charge.

f)Float to boost and boost to float charging current setting.

and somany

__________________
"Everything you can imagine is real." -- Pablo Picasso
Reply Good Answer (Score 2)
3
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#5
In reply to #3

Re: Life of the Maintenance-Free Battery

04/01/2011 2:05 AM

The reasons that most batteries fail prematurely are related to one or more of the following:

1. Excessive cycling

2. Improper charging

3. Lack of temperature control

4. Installation

5. Manufacturing problems

6. Operational issues

Note: User has control over most of the conditions that lead to premature failure.

1. Excessive Cycling:

Every time a battery cycles (a discharge followed by a recharge), the electrochemical generator has to go to work, which involves converting acid and paste. As the paste on the positive grid changes from PbO2 to PbSO4, there is a large increase in volume, which puts pressure on the paste. The more the paste is expanded and then later contracted, the more the wear and tear on it. This means that deeper discharges are more harmful to the battery. Also, cycling a battery causes accelerated corrosion of the grid structure, which leads to shorter life. This is especially true for lead calcium batteries, which happens to be the most popular technology in use today.

The lead calcium battery's cycling capability depends on the depth of discharge. For example, it is only capable of 50 deep cycles (the removal of more than 80% of energy), but can deliver 300 cycles for a 25% depth of discharge cycle. A UPS battery which normally only delivers about 25% of its stored energy during its 15 minute rated reserve time can deliver 300 such cycles. If the load on the battery is less than 30 seconds (momentary power glitch), it can handle thousands of these short cycles.

2. Improper charging

Battery manufacturers specify a voltage range for their various cells that must be adhered to. If the voltage on a given cell is allowed to go either higher or lower than the recommended value, it will have a detrimental effect on the life of the battery. It should also be noted that the specified voltage range is very temperature dependent. The right voltage for a battery at 77°F would be too high if the battery was operated in an ambient temperature of 90°F. It is important for a user to understand the interaction between voltage and temperature. Low float voltage

(Undercharging) - Undercharging causes sulfate crystals to form on the plate surfaces, since there is not enough current flowing to keep the battery fully charged. Sulfate crystals that harden over a long period of time will not go back in solution when proper voltage is applied and, therefore, result in a permanent loss of capacity. Extended undercharging will also cause a loss of active material from the negative plates.

High float voltage (Overcharging) - Overcharging causes excessive gassing of hydrogen and oxygen. This leads to loss of water in flooded cells and dryout in VRLA cells. High float voltage also causes higher float current, which in turn causes accelerated corrosion and shedding of active material from positive plates. The recombination of gases to form water in VRLA cells generates heat, and heat causes higher float currents. Therefore, excessive gassing in VRLA cells can lead to thermal runaway.

3. Lack of Temperature Control

Batteries are very temperature sensitive, and efforts should be made to maintain the operating temperature near 77°F. The proper temperature will optimize battery life and is especially critical for VRLA cells. The recombination of gases within a VRLA cell can only take place at a certain rate. If this rate is exceeded, gas pressure will build
up beyond the safety valve level, and gases/water will be vented out and permanently lost. At 77°F, the highest float voltage at which a cell can still recombine all the gases driven off the plates is approximately 2.32 volts. If the cell temperature increased to 90°F while holding the voltage constant, the cell would dry out and possibly
go into thermal runaway. Thermal runaway leads to a melting down of the jar and, under worst-case scenario, will lead to an explosion and fire.

It should be obvious from the above discussion that all VRLA applications should have tight temperature controls and/or temperature compensated chargers.

Low temperature - Battery capacity is diminished at low temperatures. For example, at 62°F, capacity is approximately 90% versus 100% at 77°F. At low temperatures, a higher float voltage is required to maintain full charge and, if the charger is not adjusted properly, cells may be undercharged, leading to the problems described under low voltage.

High temperature - High temperature causes loss of life. For every 15°F rise in operating temperature, the life is cut in half. High temperature causes increased float current, which means increased corrosion and, therefore, the loss of life. High temperature also causes gassing, which means loss of water in flooded cells and dryout and thermal runaway in VRLA cells.

4. Installation
A lot of battery problems stem from improper installations. Some of the more common ones are the following:

Loose intercell connections - These can lead to abrupt failures, including fires.
Damaged post seals - Improper cell handling or not supporting cables can damage post seals. This allows acid to migrate up the post and corrode the post to intercell connection.

Not replacing shipping caps with vent caps - In flooded batteries, this creates internal gas pressures that will force gases to escape past the post seals, causing post corrosion.

5. Manufacturing Problems

Manufacturing problems actually represent a small number of the total. Some of the more common problems, which may not show up for years, are the following:

Faulty post seal design - A leaky post seal allows acid to migrate up to the post/intercell connection area, causing a connection problem. Sometimes a new design appears to work well, but then suddenly starts failing after six to eight years in the field.

Internal connection problems - Quality problems in the connection between grid tabs and the interconnecting bus have been reported from time to time. In multicell jars like six or twelve volt modules, the intercell connection between adjacent cells may fail as a result of a poor lead burn.

6. Operational Problems

· Discharge without recharge - A fully discharged or near fully discharged cell will be damaged and possibly ruined if not recharged within 24 to 48 hours. As a battery discharges, the electrolyte starts changing from an acid solution to almost pure water when the battery is fully discharged. Lead dissolves in water, and some of the plate material mixes with water to form lead hydrate. Lead hydrate causes the plate surfaces to turn white and, because it is conductive, it forms a short circuit between the plates, rendering the battery irreversibly damaged.

· Over discharge - Over discharge causes abnormal expansion of the active material in the plates, which leads to permanent damage and also recharges problems. This can happen in lightly loaded UPS systems that experience in extended power outage.

· Excessive discharging (same as excessive cycling) - Some users have local requirements that call for testing their critical backup systems either weekly or monthly. If this testing includes cycling the battery, it will severely limit the life of the batteries.

Failure Analysis Summary

Battery system failure modes can be broken down into the following two major categories:

1. Abrupt failure - This is a sudden loss of the battery system without any warning while the system is trying to perform its intended mission. This is the worst-case scenario, as it will lead to very expensive failures. In a data center application, even a momentary loss may result in millions of dollars worth of damage. An abrupt failure is cause by an interruption in the conduction path.

Typical failures are:
· Faulty intercell connection - This could be an installation problem or a severely corroded connection.
· Internal conductance path problems - Remember, the current has to flow through the post, to an internal bus, to the grids, through the paste and electrolyte, to the opposite polarity plate, and then back out through the other terminal post.

Abrupt failures can result from a totally corroded grid that is breaking apart and only able to pass a low current flow. It can also result from a terminal post that has lost its copper insert. High current batteries have a copper insert in their posts and, if this copper is exposed to acid through a small void in the lead coating, the copper will dissolve and leave only a small lead coating to carry the current. VRLA cells that have totally dried out can also be viewed as conductance path failures, since they have no effective path between adjacent plates.

2. Low capacity failure - This is a failure to support the load for the required period of time. Low capacity results from both mechanical conductance problems as well as electrochemical problems. As a battery ages and its conductance path (grid corrosion, paste to grid connection) starts to deteriorate, the internal resistance increases. When the battery is placed under load, the voltage drop across the internal resistance will cause the overall battery voltage to reach the end voltage before its rated time.

The VRLA battery has the additional problem that, as it loses water due to dryout, it loses capacity. In essence, it loses the energy storage required for a full capacity battery.
The capacity problem is a slowly developing problem that is easily detected and, most of the time, does not cause expensive outages, since it is rare that full capacity is required during an outage. Typically, an outage is a short momentary event, and an emergency generator is usually part of the backup scheme.

It should be obvious from the preceding discussion that almost all battery problems can be detected by an increase in a cell's internal resistance, and close monitoring of this parameter can avoid disastrous failures.

Resistance measurements are mandatory for applications that cannot tolerate a loss of power. The only battery test that can provide better information on a system's state of health is a full capacity test, which is also recommended on a scheduled basis.

(I think this information may help you to find out the solutions to increase your battery life).

Vinu Answers...Sure Answers.

__________________
Sure Answers Always
Reply Good Answer (Score 3)
Power-User

Join Date: Mar 2010
Posts: 101
Good Answers: 11
#4

Re: Life of the Maintenance-Free Battery

04/01/2011 1:38 AM

If your battery life is less than the specs. then you have installed some

"stale" batteries, i.e. ones that have been sitting on a shelf for a few years, which is not good for any battery, and far worse for sealed, maint. free batts. Or, on those occasions, when you do discharge the batts, you take them down to their maximum discharge, which is like running a good horse a mile or so past his ability. Yes, he can do it, but not without eventually breaking down a lot sooner, than later.

Try to keep these batts at no lower than a 50% discharge and they will serve you for many more years than taking them down hard to a full discharge. It is better to put a bank on to add 50% more capacity to maintain this state, than run them into the ground and have to replace the entire bank often. You are dollars way ahead by adding a cushion to the bank.

Also, with sealed batts, you have to have a "smart" charger that will not let them get too much gas built up inside of the case, which will lead to premature failure. Gel batteries will give you a longer life than the AGM batts, but are more costly. You will have to justify the cost per your pocketbook vs. performance.

You've not provided much info regarding what you are providing power to, and how you are controlling the charge and power switching, for how long, and what it's critical demand is, so you are left with some pretty generic answers from the forum.

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Life of the Maintenance-Free Battery

04/01/2011 7:31 AM

Lots of good data here already that covers just about everything required.

My question to you is do you understand it all?

Charging all the time is fatal to ANY battery type....

Even always charging to 100% charge on any Lead Acid type of battery and then cutting off the charge, is in the long term fatal, for a long LA battery life you need to stop charging at about 70% of a full charge.

Letting a non leisure (car type) Lead Acid battery discharge below 12.6v for more than an hour or so will also reduce its life over time. Letting even leisure batteries stay discharged for long periods will not improve their service life either.....

Assuming a 12 volt lead acid battery of any type:-

In my experience, a good charger for a long life charges to 13.4 volts and stops charging, no trickle charge. If trickle charge is a requirement, make sure that the battery charge drops, albeit slowly and does not rise justwith the trickle charge. Cheack most carefully......

At a preset low (I use 12.6 volts) it switches on the charger and charges to 13.4 volts again.

As long as the mains is there, it should cycle like this.

You should never let the battery go to 100% full charge (gassing!), and only when the mains drops should it ever go below 12.6 volts for a short time....

If you want to cycle at a higher capacity, then cycle it between say 12.8 and 13.4 volts for example.

Just make sure that at the highest point of charge, no gassing or heating takes place......

Using the values I have mentioned, you do not need to adjust for temperature compensation either, which saves some logic in the charger!!!

Follow the manufacturer's advice for maximum charge and use half or less than recommended....

These "cycles" seem to keep a battery fit over very long periods in my experience....I have a 9 year old leisure battery in my caravan that still works fine......for example.

Remember that gassing is dangerous as the gas produced can be ignited with a small (static even) spark and damage a battery and you too if you are near to it!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Life of the Maintenance-Free Battery

04/01/2011 7:38 AM

I think the thread has mostly answered the questions. I want to know what is your current battery life? How close is it to what you expected? That answer will help you get a more pin pointed response.

Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#8

Re: Life of the Maintenance-Free Battery

04/01/2011 11:37 AM

I do have some questions and it may be OT, but how can you tell what type of battery you are dealing with when there's no information whatsoever printed on the exterior of the battery case? Are certain type of batteries standard depending on the end use?

I understand what others have posted...that's no problem....but.....

I have two batteries that always give me trouble. One is a 12 VDC car battery and the other is a 12 VDC tractor battery. The car is only driven possibly once a week....battery was replaced a few months ago and then it died last week after having driven the car about 20-25 miles the day before. Absolute dead as a door nail dead....not even a click from the starter solenoid nor interior lights come on when the door is opened. I did check to see if the alternator is charging, and yes it is....providing 13.4+/- VDC on the tester. No problem on that front. Before that, the battery was fine and held it's charge, even if the car hadn't been driven (and charged) for even a month. I've looked everywhere in the car to see if a trunk or glove box light bulb was illuminated when the car was off. Nothing found. The battery terminals are very clean and exhibit no crud as of yet. I'm beginning to wonder if there's an electrical short in a wiring harness. After the battery

The lawn/garden tractor is only used once a week, except in the prime grass growing period of spring and early summer, where it is most likely run twice a week. Typical run periods are 3/4 hour for the front yard and an equal amount for the back yard. I haven't found any shorting out in the wiring, starter or the ignition switch. Most of the time (if it has not been charging) the engine barely turns over if at all. When charged it turns over like a champ. It's a 17.5 HP B&S engine in a Craftsman tractor, 7 years old.

Any help would be greatly appreciated as these battery problems are driving me up the wall!

Maybe someone will know what to look for and then I can have an idea what type of battery I am dealing with....it make a great bit of difference for me because I have a BatteryMinder charger where I have to know what the battery is and make the appropriate charging selections.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9
In reply to #8

Re: Life of the Maintenance-Free Battery

04/01/2011 11:55 AM

I might have a few ideas on your car. Take a 10Watt 1 Ohm resistor (Radio Shack item) and put it between the negative post on the battery and the negative cable. You have to remove the negative cable first of course. Take a volt meter that can read millivolt and greater. If the car has a clock or computer you will have a slight constant draw, somewhere less than 30 millivolts....consider that normal. If you get a bigger draw something isn't right. You can start with your fuses box(s). Pull one at a time and see if the draw falls off. If it does that's your circuit of concern, forget the rest after you've repeated the test on all fuses. Good luck!

Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#10
In reply to #9

Re: Life of the Maintenance-Free Battery

04/01/2011 1:39 PM

Thanks very much Fredski! Very helpful shade tree techie advice!!!

I'll give it a try tomorrow after visiting Radio Shack...hopefully something shows up!

Ummmm, would this procedure work on large Amp "Fuse Blocks" as well?

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11
In reply to #10

Re: Life of the Maintenance-Free Battery

04/01/2011 1:49 PM

If you mean a 12 V DC circuit, yes. The idea is twofold. First you're determining if you have a draw that doesn't belong. Second you narrow it down to the circuit that's giving you a problem so the 99% of the (other) wiring and other components are irrelevant. Once you remove a fuse and the voltage drops you know there's something in that circuit. Start at the block and work towards the load to identify the pinched wire, short, corrosion, sticking switch, etc.

BTW, if the draw is big enough it will really heat the resistor up, so be forewarned.

Reply Off Topic (Score 5)
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Ayyavaru (1); CaptMoosie (2); Fredski (3); mjb1962853 (1); Oregoon (1); ozzb (1); Vinu_Answers (1)

Previous in Forum: Earth Fault Loop Impedence   Next in Forum: Air Gap Tolerance in Electrical Motors

Advertisement