Earth Fault Loop Impedence

03/31/2011 2:36 AM

Trying to design circuit for 5 x 45kW 3 phase motor (50% duty cycle) run from 100KVA genset over distance up to 400metres. In determining circuit breaker size considering AS3000 I get lost as Table B1 has no reference for 80 amp circuit breaker (could limit current to 63 amps as motor will never require full load). I am considering 70mm (25mm earth) copper cable as this will easily accommodate voltage drop and short circuit temperatures.

help...?

__________________
Everything works out in the end, just not neccessarily how you want
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Earth fault loop impedence

03/31/2011 3:01 AM

For one problem (among several), you can run only one of these motors at a time. At a typical power factor of 0.8, one 45kw motor requires 56.25 kva. Not mentioning the voltage is a serious lapse. Circuit breakers are not sized based on partial motor loads. Etc.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#2

Re: Earth fault loop impedance

03/31/2011 3:52 AM

As I understand of 50% duty cycle mean motor will not run continuous,rather it will run half of the time and will stay in rest for half of the time.likewise 30 minuets on time and 30minuets off time. So if your conclusion of motor not running on full load is based on its duty cycles then I think its not a right consideration.

Or may be I am reading your post wrongly.

Register to Reply
Commentator

Join Date: Mar 2011
Location: off the beaten track, not quite whoop whoop nor humptydoo
Posts: 57
#3

Re: Earth Fault Loop Impedence

03/31/2011 5:00 PM

I was too vague in initial post, apologies. Genset will feed distribution board and split into individual circuit feeding one VFD and one motor. From distribution board to VFD is maximum length 400m. From observation and measurement on similar sites it is known that each VFD/motor draws no more than 25kW with less than 50% 'duty cycle', also on other site is 120KVA genset feeding 2 x 45kW + 2 x 75kW VFD/motors on individual circuit.

__________________
Everything works out in the end, just not neccessarily how you want
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Earth Fault Loop Impedence

04/01/2011 6:47 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Mar 2011
Location: off the beaten track, not quite whoop whoop nor humptydoo
Posts: 57
#5

Re: Earth Fault Loop Impedence

04/02/2011 8:18 PM

The interesting thing is the international response and the issue of differing voltages. I'm in Australia so I'm using 240/415v, without (easy) access to british standards. I think the equation i was seeking is:

0.8 x Uo x Sph x Spe / (7.5 x Ia) x 0.0225 x (Sph + Spe)

Uo = nominal voltage

Sph = phase CSA, Spe = earth CSA

7.5 for C-curve breaker as VFD = soft starter

Just in case of interest - the motors drive CSG well pumps and lower water level by ten metres and then shut down until the water rises back up. It is hard to judge the frequency of running intervals and running time, but these reduce with the life of the well. Next week I'll take some measurements on 45kW motors running at 90% torque to get an actual current draw. I hope this will confirm the lower actual currents as opposed to the thoeretical maximums.

__________________
Everything works out in the end, just not neccessarily how you want
Register to Reply