Overvoltage Problem in Residential Unit

04/03/2011 10:03 AM

Dear All, Like to share a recent incident and will like to seek advice and solution from the forum. Was in charge of a residential unit and reported that all the elect appliance including surge arrestor to aircon outdoor condensor burnt out n damaged. After site investigation, fault is mainly concluded as overvoltage with the individual single phase voltage 230v raised to 400v. Note this is a 3phase incoming unit. Our preliminary suspect causing the overvoltage was floating neutral due to loose neutral cable or loss of neutral ref. However,after thorough check, the neutral cable are well with the elect distribution system in order. We are unable to conclude the cause of this problem. However, we observe that the utility powermeter is a digital 3phase direct on line type. We are wondering the possibility of the meter's internal component fault leading to the overvoltage. Will appreciate all advice and view from the forum.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Overvoltage Problem in Residential Unit

04/03/2011 10:43 AM

Only a well trained person examining the failed hardware can possibly attest to the nature of the hardware failure, but it seems to me a very remote possibility that any measurement instrument could cause an overvoltage condition. I would more likely suspect one of a variety of likely intermittent conditions coincided to produce your failure. Here are a few possibilities:

  • Lightening induced voltage spike occurred somewhere on the power grid. This residence happened to just lose the return to earth potential lottery.
  • Loose connection on one phase of a three phase motor somewhere in the grid that is moving a large mass.
  • Insulation/isolation breakdown of a step down transformer in the grid powering this residence. This can come from anything from varnish cracking, oil loss in the transformer, to a now dead animal that bridged from the low voltage line to the high voltage line.
__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Overvoltage Problem in Residential Unit

04/03/2011 11:40 AM

This sounds like a 230Y/415 3Φ system; say A,B,C,N. If phase A and N are shorted, then voltages B-N and C-N go to 415. In other words, an overvoltage condition on phases B and C.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Overvoltage Problem in Residential Unit

04/03/2011 4:24 PM

Sorry but to me that doesn't follow unless the N-E bond is lost at the time of the fault and then restores it's self after the fault.

Sorry to shoot at your theory especially as I can't think of an alternative other than lightening.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster #1
#4

Re: Overvoltage Problem in Residential Unit

04/03/2011 4:52 PM

..

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#5

Re: Overvoltage Problem in Residential Unit

04/03/2011 9:26 PM

In some areas, the code requires that the null have a separate barker. You have surge and C phase and null O, trips the barkers. If the AC was working at the time, the barker did not trip nor the command turn off the contactor and in the compressor the coil OB gets burned out, between O and B will be 400 volts.

Register to Reply
Participant

Join Date: Apr 2011
Posts: 3
#6
In reply to #5

Re: Overvoltage Problem in Residential Unit

04/04/2011 12:36 AM

Dwar Jerybaciu,

About your view pertaining to the aircon problem, it seems very possible as the aircon outdoor condensor and surge arrestor was burnt out. Similar incidents were also experienced in our local industry.

Will appreciate if you can explain and give more details about the cause that you have mentioned?

Thanks.

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#9
In reply to #6

Re: Overvoltage Problem in Residential Unit

04/04/2011 7:53 PM

For overvoltage to occur, as LAA Lucke was writing, one of the phases shorted to the neutral temporarily. Fore this to occur, one of the possibilities require that at the time of the surge, at least one try phase motor has to run, with inadequate protection (factories, trying to save costs, make the automation as cheap as possible). Consider that an appliance has o short and the breakers (fuses) for that phase and the null tripped (supply C and O outside). That motor that was running with 3 phases will run with only 2. If the protection that that motor is inadequate, then one of the coils can burn out and intrerrupts the contact between B and null (O) before the protection brakes the supply (A and B) to the motor. If the barker for phase B does not trip, then between B and (O) you will have 400 volts, because (O) is through the coil AO in contact with phase A. Of course, when that happened, everything that is ON and hooked up on phase B is toasted, which in turn, tripe the breakers for A and B. You can say this if only on one phase has its consumers burned out.

Register to Reply
Anonymous Poster #2
#11
In reply to #6

Re: Overvoltage Problem in Residential Unit

04/09/2011 3:31 AM

Yes, you are right. All aircon PCB board, surge arrestor, fluorescent ballasts, lamps, home appliances etc were burnt.

There are a total of 8 units on a floor sharing the same incoming source but only 1 unit is affected. During the site investigation, it observed the LED light (varh/Imp) of the concerned KWH meter was litted very brightly and remained ON for 20sec duration, abnormal to the rest of the KWH meters for other apartment. The KWH meter brand is Elster 1700.

This incidents also happened in our local industry since 2010 before Christmas.

We do not know how to solve this problem and it become an open verdict case.

May you share with us how to resolve it in your country?

Thanks.

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#12
In reply to #11

Re: Overvoltage Problem in Residential Unit

04/09/2011 10:08 AM

The cods differ from country to country, and you MUST follow them. Personally what I do is put a transformer 1:1 that will supply the three phase consumers. This way I will have galvanic separation, and if this happened again I will know that the problem comes from the supplier.

Register to Reply
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#7

Re: Overvoltage Problem in Residential Unit

04/04/2011 2:45 AM

Are u using any mcb's or mccb's for protection and isolation of power to your residential unit. if you are using so there is a chance of opening or improper closing of neutral contact in any one of the MCCB. In this sutuation there is a chance for such high voltage.once switching off and on may solve this problem. if you are not using any mccb's (4pole). there is chance for drop in insulation resistance for any one of the phase and neutral.

__________________
key questions why, what & how - just think
Register to Reply
4
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8

Re: Overvoltage Problem in Residential Unit

04/04/2011 3:00 PM

This is a Neutral Problem. You said that 400V was experienced between phase and Neutral instead of the 230V.

Cause: The neutral coming into the premises is from the local distribution Transformer. Even if all your internal wiring was OK and sound, the incoming Neutral could have failed ouside, or One of the phases shorted to the neutral temporarily, failing to blow the supply fuse or trip the supply CB from the transformer to the line supplying your section / house.

Solution: Make sure that the Neutral is grounded properly within the building (after the Utility supply) BUT Better check with the utility if they have no objection on that: The rules differ from country to country etc. But The Problem is still the same: Neutral to Phase fault without tripping the supply, or the tripping was too slow and the damage occured, OR the Neutral was lost externally from your building, even for a short period??

Register to Reply Good Answer (Score 4)
Participant

Join Date: Apr 2011
Posts: 3
#10

Re: Overvoltage Problem in Residential Unit

04/09/2011 1:45 AM

Dear All,

I like to express my great appreaciation for the spontaneous comments and views posted pertaining to this issue.

I will like to update that we have taken up the issue with the utility provider regarding to possiblity of direct digital kWh meter failure causing the current issue.

We have received the incident log data of the concerned meter, with mutiltple fault log indicating "Phase Fail", coinciding with our power outage and site investigation activities.

We will like to seek advice from the forum on the following:

1. As reflected in the incident data log, the definition of "Phase Fail" is denote as any one or more phase voltages supply to meter are <80% of rated voltage (230V/per phase)/missing phase voltage supply to meter.

We will like to ask whether "Phase Fail" should also include over-voltage as our electrical appliances should not have destroyed due to undervoltage scenario?

2. During our site investigation, we observed that the LED light (varh/Imp) of the concerned meter was litted very brightly and remained ON for 20sec duration, abnormal to the rest of the meters for other apartment.

We will like to ask about the possible explanation to this abnormal phenomenon.

For discussion purpose only, the concerned meter is from Elster.

Thank you while we look toward for all comments and views to the issue, hopefully a closure to the matter.

We will update if we have further progress.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13
In reply to #10

Re: Overvoltage Problem in Residential Unit

04/09/2011 1:57 PM

If a supply phase shorted to the neutral wire, upstream of the meter, and the neutral connection, upstream, failed, then the meter will record a phaise fail. But the problem is that the voltage downstream will experience high values (400V) between the other 2 phases and the supposed neutral wires.

1: The overvoltage is not sensed by the meter since there was none: The phase to phase voltage is still the same (400V). The neutral is missing --> the voltage experienced by the different appliances will no longer be pinned to 220 or 230V. It will float from o to 400V, depending on the appliances that were connected and ON at the time.

If as confirmed, the wiring in the buildings was safe without any faults, then the problem is still with the supply company.

Register to Reply
Register to Reply 13 comments