Medium Voltage Cable Insulation Test (Megger)

04/04/2011 9:02 AM

Dear Members what happens to the insulation of the underground cable after it is pulled. we tested the 8.7/15 KV cable for 5KV DC before pulling the result is 30 G Ohms but after pulling it is now 600 G Ohms,, what can be the possible reason for this difference , also if it comes out to be in (k ohms) after pulling..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jun 2008
Location: beverly hills
Posts: 116
#1

Re: Medium Voltage Cable Insulation Test (Megger)

04/04/2011 10:05 AM

Hi,

As long the insulation test result is within the acceptable requirement, no issue.

Regard's

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Medium Voltage Cable Insulation Test (Megger)

04/04/2011 10:52 AM

Goodness, what did you do--break the wire?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Sep 2010
Location: Saudi Arabia
Posts: 14
#3
In reply to #2

Re: Medium Voltage Cable Insulation Test (Megger)

04/04/2011 11:03 AM

30 G to 600 G means ???????????

20 G to 200 k means ???????????

Register to Reply
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #3

Re: Medium Voltage Cable Insulation Test (Megger)

04/04/2011 2:03 PM

What were you measuring with your megger - conductor to shield? When you are getting such high insulation resistance values, they represent fractions of microamps leakage current (30G ohms = 0.167 uA at 5kVDC). Even a little difference in humidity in the air or on the surface of the insulation can make a lot of difference. So 30G on the reel to 600G when pulled into place probably means that the air's relative humidity was lower at the second test, or you cleaned & dried off the end of the cable better.

The second, from 20G to 200k, means that you probably contaminated the bare end of the cable, so that you now are getting 25 milliamps of leakage - Way too much! It is vital to control environmental issues when working with HV cables. A little moisture trapped when the cable is terminated can lead to (often catastrophic!) failure later. You need to clean and dry the cable ends before you go any further.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Sep 2010
Location: Saudi Arabia
Posts: 14
#5
In reply to #4

Re: Medium Voltage Cable Insulation Test (Megger)

04/04/2011 2:20 PM

Thanks i got the point .

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6
In reply to #4

Re: Medium Voltage Cable Insulation Test (Megger)

04/05/2011 8:43 AM

I agree, my first thought was quality of connection. He also mentioned it was now buried. Unless it's buried as a coil I have to assume it's run a decent length. I wonder how long the test leads are on his megger for the second test?

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7
In reply to #6

Re: Medium Voltage Cable Insulation Test (Megger)

04/05/2011 9:12 AM

But you don't megger across the length of the cable, only at the end, between conductor & shield or conductor & ground, or else from phase to phase conductors. Don't need long leads for that.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Off Topic (Score 5)
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Fredski (1); PeterT (2); ronron (1); Tornado (1); yousafali15 (2)

Previous in Forum: Machine Flexibility Upgrade 1   Next in Forum: Power Calculation

Advertisement