ELCB

04/05/2011 11:53 AM

hi friends

i just want to know how to connect ELCB for 3 phase motor? because here we get only 3 phase but no neutral.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: ELCB

04/05/2011 12:29 PM

L1 L2 L3 ignore N

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Associate

Join Date: Mar 2011
Posts: 48
#2
In reply to #1

Re: ELCB

04/05/2011 1:01 PM

only L1 L2 L3 In this condition as far i know the ELCB will not trip.

i already tried this

Register to Reply
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: ELCB

04/05/2011 1:25 PM

It won't trip on the test button. That will be connected between one of the L terminals and N. If you want the test facility either run a neutral to one of the N connections or connect one N to earth.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: ELCB

04/05/2011 10:13 PM

Tony is right. I wonder why it should not work. During normal conditions, motor being a balanced load, currents in L1, L2 & L3 would be equal and hence there woud not be any residual current. When there is an earth leakage, this balance is affected and the ELCB must operate, if the leakage current is above the ELCB sensitivity level.

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#5

Re: ELCB

04/06/2011 4:47 PM

The other posters are correct to say that the ELCB should work fine with a 3-phase circuit that has no neutral, the line currents will sum to zero.

As far as the test trip goes, I guess that different manufacturers do this differently. The 4-pole RCCBs that we use here (GE brand fwiw) have an internal resistor that the test trip connects between L2 (upstream) and L3 (downstream), so if the neutral is not being used, the test trip still works. This is marked on the little diagram that is printed on the case.

__________________
paulusgnome
Register to Reply
Associate

Join Date: Mar 2011
Posts: 48
#6
In reply to #5

Re: ELCB

04/07/2011 9:28 AM

is there any different types of RCD's available which we can use only for 3 phase without neutral?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: ELCB

04/07/2011 1:16 PM

All of them. It's just that the test button will not work without a neutral.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); loyd (2); Paulusgnome (1); PWSlack (1); TonyS (2)

Previous in Forum: POWER ESTIMATION   Next in Forum: Process control instrumentation technology problem

Advertisement