Spacing Between132 kV Single Core Cables Laid in Cable Trench

04/06/2011 1:56 AM

Two nos. 3 phase 132 kV circuits comprising of 1000 sq.mm cu.conductor XLPE insulated single core cables are to be laid side by side in flat formation (not trefoil ) in a burried in earth type cable trench at a depth of 2 meters for a route length of 2.5 kM in an integrated steel plant under it's expansion project.

Can any expert indicate the recommended spacing between the cables of each circuit as well as the distance between the middle cables of the two circuits?Also please give the details of the reference documents/relevant links in support of your recommendation, if possible.Thanks in advance for your help.

__________________
Learning is a never-ending process.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Feb 2011
Location: Dubai, UAE
Posts: 63
Good Answers: 7
#1

Re: spacing between132 kV single core cables laid in cable trench

04/06/2011 4:29 AM

There is no recommended spacing. As the separation distance between XLPE cables is reduced one has to apply higher de-rating factors accordingly.

The de-rating factor charts and other sizing criteria are provided free on request by the cable manufactures.

In your case the designer should have taken into account certain separation while selecting a particular size for the given loading and is liable to declare that minimum spacing requirement to the contractor and the supervisors.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#2
In reply to #1

Re: spacing between132 kV single core cables laid in cable trench

04/06/2011 5:07 AM

Apart from Continuous Current rating/derating factor related issues, is there any safety related issues considering the level of voltage handled in this case?

Will it be possible to attend to a faulty cable of one circuit with out exposing the maintenance personnel to any safety hazard while the other circuit laid in the same trench continues to feed the BUS ? If not,what should be the safe distance between the two circuits ?

Will a brick or precast slab partition between the two circuits help? If yes,should it be provided all through the entire route or only at the location of cable joints ?

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: spacing between132 kV single core cables laid in cable trench

04/06/2011 5:40 AM

It is always a compromise between economy & safety. Best is to keep maximum possible seperation, but at what cost? So, a nominal spacing is maintained depending upon the site conditions and duly applying rating factors for the cables. I suppose the cables are insulated. So, what is the worry of having access to a live cable while working on a dead cable nearby? Isn't the cable insulated to the full voltage? Of course, a concrete seperation slab would definitely help from causing an inadvertant mechanical injury to the cable.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#5
In reply to #3

Re: spacing between132 kV single core cables laid in cable trench

04/08/2011 5:49 AM

So, a nominal spacing is maintained depending upon the site conditions and duly applying rating factors for the cables.

Can you please give the value of recommended nominal spacing between the cables in our case ( refer the initial post at the top).

__________________
Learning is a never-ending process.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: spacing between132 kV single core cables laid in cable trench

04/08/2011 9:10 AM

Vide Clause 6.3.3 of IS 1255 (Indian Standard Code of Installation & Maintenance of Power Cables): "Laying Cables Direct in Ground - Clearances: The desired minimum clearances are as follows:

Power Cable to Power Cable: Clearance not necesary; however, larger the clearance, better would be the current carrying capacity".

So, no clearance is mandated by the Standard. If you want to know the de-rating factors, you may refer to any cabl manufacturer's catalogue.

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#7
In reply to #6

Re: spacing between132 kV single core cables laid in cable trench

04/09/2011 8:22 AM

Thank you electricalexpert65 for your help.But ,the IS 1255 you have mentioned pertains to power cables upto and including 33kV only.Will it be applicable for 132 cables too ? Or there are other IS/Standards/Guide lines ? Can you or other experts in the forum throw some light on this ?

__________________
Learning is a never-ending process.
Register to Reply
Participant

Join Date: Feb 2011
Posts: 3
#4

Re: Spacing Between132 kV Single Core Cables Laid in Cable Trench

04/06/2011 11:55 PM

Hi,

Spacing between the power cables can consider depends up the current carrying calculation and type of bonding.

Register to Reply
Participant

Join Date: Feb 2011
Posts: 3
#8

Re: Spacing Between132 kV Single Core Cables Laid in Cable Trench

04/09/2011 11:53 PM

Hi,

Spacing will not solve the problem. IEC 60287 will give you the solution for the above said. Thermal resistivity of soil to be tested as per IEC requirment 1.2 degree m k/w.

If you achieve the same, i hope you can go upto minimum spacing 250mm to 300mm.

During the calculation following things to be considered

1. Open cut road crossing

2 If, any existing parallel cable circuits

3. Ambient temperature.

regards,

gopinath

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

A.A.Khi (1); electricalexpert65 (2); gopimint (2); spradhan (3)

Previous in Forum: Power Transformer Breather, Silica Gel   Next in Forum: On Load Operation of Cockroft Walton DC Generator

Advertisement