Sov

04/09/2011 3:22 PM

hai ,can u tell me the working principles of solinoid valve. what is fieldbus in instrumentation . In a pressure transmitter how I can calculate the value in pressure unit if I get the mA .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: sov

04/09/2011 4:38 PM

A solenoid valve changes state when it is energized and/or de-energized.

Fieldbus is a generic term for a digital device communication protocol and control architecture that also includes physical layer specifications. Profibus, Modbus, and Foundtion Fieldbus are specific examples.

With linear pressure transmitters there is a proportional relationship between the range of the pressure and the range of the output mA. For example when the pressure is at 50% the output should be 50%.

Register to Reply
Active Contributor

Join Date: Oct 2010
Posts: 16
#4
In reply to #1

Re: pressure transmitter

04/10/2011 3:24 PM

if one transmitter range is 0 to 25 bar,i get output 15 ma ,hw I calculate through pressure

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: pressure transmitter

04/10/2011 3:34 PM

0-25 bar = 4-20 mA

0 bar=4mA

25 bar=20mA

What does 15mA =?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: pressure transmitter

04/15/2011 1:30 AM

If you set 25bar to 20mA,what will happen if pressure exceeds 25bar?. It would be advisable to allow a safety margin for small over-pressure. You can set 25bar at,say, 18mA.

__________________
pnaban
Register to Reply
Participant

Join Date: Jun 2011
Location: India
Posts: 3
#8
In reply to #7

Re: pressure transmitter

06/21/2011 4:17 AM

No you should not set 18 mA for 25 bar it will lead to wrong measurement.

And if we consider the case where 25 bar is set to 20mA and pressure exceeds from 25 bar then transmitter will send fault current 22mA proportional to preesure and after that it will clamp to 22mA (if its not NAMUR compliant).

__________________
Regards, Yogi
Register to Reply
Anonymous Poster #1
#6
In reply to #1

Re: sov

04/13/2011 5:38 AM

Sir, pressure transmitter will never come with square route . its always linear relation only if u dont know how to say dont confuse others..

take care

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#2

Re: sov

04/10/2011 2:01 AM

The solenoid converts electrical energy into mechanical energy which, in turn, opens or closes the valve mechanically. For working please refer http://www.pneumaticpart.com/solenoid-valve/Solenoid-operational-principle.html

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Sov

04/10/2011 11:12 AM
Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

A Saleem (1); Ace Boeringa (1); Anonymous Poster (1); lyn (2); mrswamy (1); pnaban (1); Yogi-igoY (1)

Previous in Forum: Question about BMS   Next in Forum: Electronic Circuit Drawing

Advertisement