What is the general formula for calculating the size of Copper and Alluminium cable ?
1) if i have 35 mmsq copper cable, then what is the current capacity? Suggest me formula for both alluminium and copper cable of same size.
2) for 100 amps. current carrying, which size of Alluminium or copper cable required ?
I required exact equation for that.
Plz. help.
Thanks
Good Answers: 181
Re: Formula for Cable size and rating calculation.
04/14/2011 4:07 AM
BS 7671
04/15/2011 11:47 AM
Yep. It's all in there. GA.
04/14/2011 4:34 AM
I don't think there is any such thing as "the exact equation" for this. As a practical matter, conductor ampacity is determined by looking it up in electrical-code or manufacturers' tables, with various corrections applied for ambient temperature, conductor configuration, etc.
Re: Formula for Cable Size and Rating Calculation
04/14/2011 1:38 PM
http://www.energy-solutions.co.uk/cable_conductor.html
Check this chart. Be Sure to apply all applicable code derating requirements
04/14/2011 4:05 PM
This looks like homework. Laaazzzy, laaaazzzzy homework.
See the numerous previous threads on CR4 covering this commonly asked (homework) question.
Anonymous Poster #2
04/17/2011 10:34 AM
use it
Good Answers: 170
04/17/2011 1:06 PM
1) There are no thumb rules for calculating cable ampacities. Because, the cable impedance variation is not "linear"; only the resistance will vary linearly with respect to the cable size, whereas the reactances (both capacitive and inductive) are not linear with respect to the cable cross section. That makes it difficult to arrive at a formula for calculating the cable ampacity vis-a-vis its size.
Easier method would be to follow the cable manufacturers' catalogues and rating tables (and, don't forget to apply appropriate rating factors).
2) For carrying 100 Amps current, under Indian Industrial Installation Conditions, I would normally go for a 70 sq.mm Aluminium Conductor Cable.