Previous in Forum: How to Setup the IOC Test with the Time Delay on Doble F2253   Next in Forum: How to Build an AVR for a Three Phase Generator?
Transformer Flux Linkage
04/15/2011 11:31 AM
How can one improve the flux linkage between the primary and the secondary windings of a transformer?
Re: Transformer
04/15/2011 11:39 AM
Make it smaller.
Good Answers: 11
Re: Transformer
04/15/2011 12:01 PM
Wind the transformer bifilar.
Good Answers: 82
Re: Transformer
04/16/2011 10:09 AM
Yes, bifilar winding is very effective indeed in improving coupling and reducing leakage inductance. But it leads to high interwinding capacitance and poor insulation-voltage capability. For off-line transformers there will be safety issues and it's generally not allowed.
Second best in reducing leakage inductance is to interleave the primary and secondary windings, either side-by-side, or one above the other. E.g., P - S - P. If side-by-side, you can have plastic insulating spacers, if on-top you can separate windings with layers of tape. More than one set of interleaving produces better results, but is harder to make.
There are simple formulas to predict exactly what your leakage inductance will be. BTW, the leakage inductance is the same whether the core is present or not. The following is from Snelling, Soft Ferrites, 2nd-ed, pg 337.
There's an 1/M2 term in the leakage inductance equation, and you can see the configurations with M = 2, 4 and 6 providing reductions from 4 to 36 times. We won't go into all the problems that poor coupling and excessive leakage inductance can cause, or exacerbate, but it's often well worth any effort spent on improvement. I see the figure is hard to read after CR4's compression, so I've blown up the definitions of terms.
Thanks, Win
India - Member - New Member
Good Answers: 164
Re: Transformer Flux Linkage
04/15/2011 12:15 PM
Make it a shell type?
Good Answers: 119
04/15/2011 11:12 PM
Carl Pugh (1); kvsridhar (1); mjb1962853 (1); PWSlack (1); Winfield Hill (1)