VFDs for Exhaust Fans

04/21/2011 12:08 PM

Engineers.

The client is replacing the existing 3 phase standard induction motors for centrifugal supply blowers with VFDs in order to reduce his monthly electric bill..the humidified air from the centrifugal blowers is used in the building for cooling purpose.my question is should the client also install VFDs for the Exhaust centifugal fans.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: VFDs for Exhaust fans

04/21/2011 12:32 PM

what is your role big boy?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: VFDs for Exhaust Fans

04/21/2011 1:49 PM

If these fans can be run at part speed for sizable fractions of time, VFDs can save energy on both the supply and exhaust fans.

On the other hand, if the fans are typically used at full speed, or cycled off under light loads, VFDs will not save any (or much) energy.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#3
In reply to #2

Re: VFDs for Exhaust Fans

04/21/2011 11:36 PM

Agreed, though you are going to install VFDs on the supply fans which will change the building pressures, it may be possible to just cycle off the relief / exhaust fans since there is probably other sources of relief in the building, bathroom exhaust, elevator shafts. Which will save even more money.

Most importantly, is the design constant volume or VAV? If CV you will need to take a look at the refrigeration system to be sure it can operate properly on low load. You mentioned humidity if it is a DX system the humidity will be pulled out of the air and into the DX coil and down the drain.

Reading the OP though it sounds like big centrifugal "swamp coolers" so no you do not want to stop relief / exhaust if that is the case. Install the VFDs and run the relief / exhaust fans based on a 0-10 - 4-20 signal out put from a humidity transducer to the Exhaust fan VFDs to regulate speed. This will assure proper humidity control so the people or items in the building do not end up soaking wet due to slower speed delivery with higher water concentration and no way to remove the moist air.

__________________
To be or not to be........ok that's a trick question.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2010
Posts: 164
#9
In reply to #3

Re: VFDs for Exhaust Fans

04/23/2011 12:31 PM

DX system is not applicable here. The fresh air passes through water sprinkler than passes through pre- filters and than after passing through bag filters the air is now supplied to the plant area.The idea is to reduce fresh air temp by 5 to 6 degree C by water sprinkler.

Due to the dissipation of heat from motors as well as heat generated from the oil heaters install ,in the plant , it is necessary to exhaust the hot air into the atmosphere .

Is it necessary to replace the exhaust centrifugal fans when the management is keen to replace the Supply centrifugal fans

Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: VFDs for Exhaust Fans

04/22/2011 1:27 AM

I suggest that you look at the ROI before you think about installing any type of VSD, then look at buying harmonic filters.

Any type of VSD will induce further harmonics into your electrical system, and that alone will add to your monthly power bill.

So complete a power quality survey, do the maths on the cost of VSD plus filter, calculate how much you will save and see how long it will take you to re-coup your investment before you start saving money... plus take onboard the previous answers given

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: VFDs for Exhaust Fans

04/22/2011 10:49 AM

"Any type of VSD will induce further harmonics into your electrical system, and that alone will add to your monthly power bill."

How will it increase your monthly power bill?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6
In reply to #5

Re: VFDs for Exhaust Fans

04/22/2011 11:07 AM

my reply would take up way to much room in this forum to answer in full, as I'm sure you would not want a half answer..... do you have a email address that I can reply to? you can find mine in my profile

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#10
In reply to #5

Re: VFDs for Exhaust Fans

04/24/2011 6:05 AM

Harmonics add to your power bill by becasue of the additional loss of power, disapated in heat. (VERY short answer)

So you are paying to warm up the atmosphere rather than run you applicance or whatever you are powering, on our web site www.thccontrols.com the powerpoint presentation explains this in detail.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#7
In reply to #4

Re: VFDs for Exhaust Fans

04/22/2011 12:07 PM

As far as the VFDs in the market place today most come with the proper filters or chokes in them to assure a clean supply to the end device.

The problem with harmonics usually comes with a bad install or improper end device mating to the drive. The power feed wires and the supply to the end device (load) must be in separate conduit or noise on line may occur making it back the the MCC or main panels. Same with the motors. Be sure they are rated for VFDs, if not install Ceramic bearings to keep harmonic noise from getting to ground.

Costing more on energy consumption for a building after installing a drive, never seen that yet.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8
In reply to #7

Re: VFDs for Exhaust Fans

04/22/2011 12:15 PM

you are partly correct, but any induction load will induce harmonics and you need filter, usually active rather than passive. but you must remember I am talking about electrical harmonics, not mechanical ones as I think you are suggesting that these (mechanical ones) can be mitigated by using ceramic bearings.. unless you mean that these bearing will mitigate induced harmonics in the electrical system??

Not all VFD's have filters.. some do, but I know there are many brands/makes that do not. Thats why I said fitting a VFD will induce harmonics and cost more to run

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#11

Re: VFDs for Exhaust Fans

04/25/2011 9:34 AM

Dear,

Normally, Exhaust fans are running continously. If you run the fans at full speed, then , investment will be a waste.

If you reduce the speed by say, 5%, you may save consumption in the cube root proportionate, say 8 - 13 % of the previous load. Life of equipment will also increase.

But, you have to make a break even graph between

Capital Cost V/s Power reduction / cost saving by load reduction.

__________________
Exploring the Science of Electricity
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#12

Re: VFDs for Exhaust Fans

04/25/2011 5:35 PM

Absolutely. And for best results they should be controlled to maintain a very slight positive pressure in the building, in the order of .05" to 0.10.

If you are replacing the motors as you mentioned this would be the time to go to high efficiency motors. The pay back on this plus the VFDs will be very attractive and the on-going energy savings significant. Also check with the local utility for potential rebates. Good luck. Lou Bindner

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#13
In reply to #12

Re: VFDs for Exhaust Fans

04/25/2011 10:07 PM

thanks for your encouraging reply with special reference to building positive pressure.yes the plant management wants to go for high efficiency motors.I am not HAVC engineer will highly appreciate if you pass me the link to know more about positive building pressure.

Thanks

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (3); harry potter (1); JRaef (1); Lou Bindner (1); salahuddin zia (2); Stedou73ish (2); thccontrols (1); Tornado (1)

Previous in Forum: rating for Inverter   Next in Forum: Earthing wire for a motor

Advertisement