XLPE Cable

04/22/2011 3:55 AM

Hi everbody,

In medium voltage ( 34.5 kV , 22 kV or 11 kV ) ıf we change cross section of the XLPE cable from 3x( 1x95/16 mm2) to 3x( 1x120/16 mm2) or capacitive reactance will increase. And also it isn't same for overhead lines. Do you agree with me?

In addition to this in LV or MV how can we calculate the cross section of XLPE or NYY cable?If we measure the radius of cable without PVC part of cable which formulas must we use to calculate the cross section of cable?

What's your opinions?

Best Regards,

Musa UÇAN

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: XLPE cable

04/22/2011 4:31 AM

Well you've out done yourself, that makes even less sense than your last question

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: XLPE cable

04/22/2011 4:46 AM

I dont know of capacitive reactance in XLPE. I will explain cross-sectional area and diameter with house wiring cable. We buy stranded cable with 1mm^2 or 1.5 or 2.5 right. Now in 2.5mm^2 we have around 35 strands each 0.3mm in diameter. So each strand has an area of (0.15x0.15x3.14)=0.07065mm^2 So 35x0.07065=2.5approx.

Register to Reply
Member

Join Date: Nov 2010
Posts: 7
#3

Re: XLPE cable

04/22/2011 5:32 AM

Dear TonyS,

I have been working in a water treatment system in İstanbul Leather Zone for 6 years. This system was establisted 21 years ago.

In this area H2SO4 injures all the system ( PLC cards, soft starter, electronic cards etc. ). Now theres no writting about cross section on this cable's PVC .

However we have to replace this cable in a short time so we have to determine cross section of this cable by using measuremet and calculation.

In addition to this, last question and this first question todat are about my homework about master program. I investigated earth fault protection for embedded generator paralled with grid.

Best Regards,

Musa UÇAN

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: XLPE Cable

04/22/2011 9:00 AM

This may come as a strange concept to you. But has it occurred to you to look at the cable terminations? A good engineer would tell you at a glance.

You can't tell a cables composition by O/D!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#5

Re: XLPE Cable

04/23/2011 7:30 AM

dear,

Cross section of any conductor of any voltage grade of cable is the "compacted cross section". Not the area of stranded conductors added together.

Simple language, You crimp the conductor by Copper Lug. Cut the lug in cross section at the crimped spot. Then measure the area of conductor.

This will be the cable size.

__________________
Exploring the Science of Electricity
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: XLPE Cable

04/23/2011 8:28 AM

Sorry but crimping a lug reduces it's CSA. As the crimp is compressed it extends in length slightly.

I found out the hard way, the perfectly cut 500mm cable was to long for the terminals after crimping!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#7

Re: XLPE Cable

04/24/2011 2:00 AM

LT XLPE CABLE

Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

harry potter (1); hithuanand (2); musaucan (1); TonyS (3)