Supply 1 Phase Motor

04/23/2011 5:58 AM

We have 3 phase transformer 480/(220/127 )and single phase motor 220V.

Can connect two phase to run the motor?

I hope to get good and technical answer as usual

Register to Reply
Pathfinder Tags: motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#1

Re: Supply 1 phase motor

04/23/2011 6:03 AM

If output of transformer is 220 phase to phase then you definitely connect the motor with two phase.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Supply 1 phase motor

04/23/2011 6:10 AM

Go for it, phase to phase

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3

Re: Supply 1 phase motor

04/23/2011 6:32 AM

Don't lie your yourself that your transformer is 480/(220/127). It means that this transformer can provide 220V of line voltage and 127V phase voltage?

If you connect this single phase 220V motor to a voltage 127V? How does it work?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Supply 1 phase motor

04/23/2011 6:46 AM

Well it's down to our ALI99 to confirm the output voltage of the transformer. He states phase to phase and phase to neutral voltages. One has to assume he's right.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#5
In reply to #4

Re: Supply 1 phase motor

04/23/2011 6:53 AM

This could be tricky... Could we connect 220V single phase motor to two-hot lines of 220V?

Tony, I meant him.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #5

Re: Supply 1 phase motor

04/23/2011 8:11 AM

Hehe From the voltage I'd guess it's one of those weird American things.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #7

Re: Supply 1 phase motor

04/23/2011 8:27 AM

Three-phase 208/120 is common in the U.S., but not 220/127, so far as I know.

(Many people get confused between distribution voltage and utilization voltage, (to say nothing of the "divisible by 11" canard). 480/277 is also common here, and 240/208/120 center-tapped. Most residential here is 240/120 single phase.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#11
In reply to #10

Re: Supply 1 phase motor

04/23/2011 8:39 AM

Where is Wikipedia from, from US?

I skimmed through it and found that American household can utilise two live wires to connect to general rotating machines. These machines will work out with lesser current.

So, two wire could be considered as two-phase? So you will be supplied with 240/120V single phase in US? Nevertheless, some of them are labeled to operate as two kinds of voltage? So, with two live wires connected to loads, you will say it two-phase of single-phase power?

Is this why Tony said "weird American thing"?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: Supply 1 phase motor

04/23/2011 9:22 AM

A typical U.S. residential 240/120 center-tapped system is still just a single phase. Larger appliances such as airconditioners, water heaters, and stoves are 240v, 1Φ; lights and convenience outlets are 120v, 1Φ. In most places, that is; you can get residential 3Φ, which you might want if you have a sizable hobby or cottage-industry workshop.

__C__
|.. |.. |
A--N--B

can represent a 3Φ 240/208/120 system. AB=BC=CA=240; AN=BN=120; CN=208 ("high leg"). A 1Φ 240/120 system is just A--N--B. (The dots are just to separate the vertical lines; the text system here does not preserve spaces, alas. [Ed. C.])

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#16
In reply to #12

Re: Supply 1 phase motor

04/24/2011 10:04 AM

Tornado; I have not seen any residential neighborhoods with more than a single high voltage feeder, & single phase step down transformers, hi-voltage to 120/240 volt single phase to homes/houses. if you were to have 220 volt wye/star, you are right 220/127 volts. perry

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#25
In reply to #16

Re: Supply 1 phase motor

04/24/2011 4:42 PM

That is certainly correct in our cities, and many rural communities. All the large appliances, such as stoves, are locally 240/120 single phase, ie 120/120 centre tap grounded. If you connect to a 3 phase 208/120 you notice a distinct drop in power when the high elements come on.

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#17
In reply to #12

Re: Supply 1 phase motor

04/24/2011 10:08 AM

Tornado; NEC code is A to N, C to N, 120 volts. B to N 208 volts perry

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#23
In reply to #17

Re: Supply 1 phase motor

04/24/2011 3:40 PM

Thanks for the correction; my fault for switching B and C. (Haven't seen a center-tapped Δ in a while.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#26
In reply to #23

Re: Supply 1 phase motor

04/24/2011 9:22 PM

"Thanks for the correction; my fault for switching B and C. (Haven't seen a center-tapped Δ in a while.)"

Actually you were not necessarily wrong. Starting in the 2008 NEC, you can now mark the High leg as C instead of B, as long as the marking is clear. This was apparently something they had to do to accommodate some types of metering systems. I just read an article or two on it but didn't totally delve into the why's too much.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#28
In reply to #26

Re: Supply 1 phase motor

04/24/2011 10:13 PM

JRaef; The power company uses the high leg, right hand rule in their meter sockets to keep every thing uniform, & we did the same hi leg right hand in the panel boards. perry

Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#6

Re: Supply 1 phase motor

04/23/2011 6:54 AM

dear must be a college student?

definitely, you can connect the 220v terminals across the motor.

All that will happen that un balanced current may flow thru the common point of secondary winding of transformer. If the star point is earthed, must be of strong cross section to take up that un balanced current.

__________________
Exploring the Science of Electricity
Register to Reply
Member

Join Date: Mar 2011
Posts: 9
#8

Re: Supply 1 phase motor

04/23/2011 8:21 AM

Phase to phase is 220

Phase to neutral is 120

if we can connect then how technically connect two phase to one phase? is there any recommendation?

if can not then why?

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#9
In reply to #8

Re: Supply 1 phase motor

04/23/2011 8:26 AM

The above "American thing" has said it all. Just go for phase to phase.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#20
In reply to #8

Re: Supply 1 phase motor

04/24/2011 12:09 PM

ALI99-

CAUTION! CAUTION! CAUTION!

This is not a simple question to answer since you have not given enough information particular to your situation. More information is needed to clearly answer what could potentially be a fatal answer. Much of what has already been given is full of presumptions and wrong answers. This could kill you or someone else who might think they have a similar situation. Look at some answers and they say the complete opposite of other answers.

Do yourself and others a very big favor, confer with someone who is very knowledgeable on the subject and can look at what you want to do and ask further questions. If you don't, it could be the most fatal question that was not asked!

One of the problems with this forum is that you can not confirm the knowledge of the repliers/posters. Some write very well but don't know much about the subject; some may not write so well but have the correct and safe answer; some have the right answer and can convey it well; some are completely wrong; and then there are some like me who don't reply to subjects that we are not extremely knowledgeable about but when we do answer about something we are fluent in we try to make our answers as clear and simple as possible.

Right now I don't have time to contribute to your questions but only two of the replies are correct (and they sound much different from each other)

Good Luck, old salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#21
In reply to #20

Re: Supply 1 phase motor

04/24/2011 1:01 PM

You had the time to write your condemnation of answers given in good faith.

Why not the time to enlighten us all.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#22
In reply to #20

Re: Supply 1 phase motor

04/24/2011 2:52 PM

Is this a drive-by accusation? You allege a potentially lethal flaw in several answers, some of which could be mine, yet do not identify the flaw and how to correct it?

There could be an issue of just what is or is not grounded on the OP's motor. This has been mentioned briefly and could bear a further look.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#29
In reply to #22

Re: Supply 1 phase motor

04/24/2011 10:24 PM

I would be curious to know why this was considered OT, especially given the turn the discussion has taken.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#30
In reply to #22

Re: Supply 1 phase motor

04/24/2011 11:52 PM

Tornado-

Yours was not one of the poorer answers. I was the one who rated your post #10 as a good answer. Your answers have been well written and clear.

I was unable to expand upon my post technically due to several nieces and other relatives waiting for me for Easter Dinner. Those things happen just like I don't have time now to go into the technical details because I just returned home from the party and have to get some sleep in order to teach a class tomorrow.

Having conducted numerous Haz Ops and unfortunately several fatal accident investigations during my career I feel I would be remiss if I did not warn individuals that some of the posts have the potential to cause very bad situations. For example, a motor must always be grounded. If a internal wire were to come loose the frame would probably become hot to ground, a potential fatal situation.

Sorry, no more tonight. Got to get some sleep.

Good Luck, old salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13

Re: Supply 1 Phase Motor

04/23/2011 11:33 AM

The OP's system is 3Φ 220/127, crudely diagrammed:

....C
.../|\
../.|.\
./..N..\
A¯...¯B

AB=BC=CA=220; AN=BN=CN=127.

Any 220v 1Φ loads can be connected AB, BC, or CA. If there are multiple such loads, they should be distributed as equally as possible among these three connections.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: Supply 1 Phase Motor

04/23/2011 4:35 PM

Most likely he has what we call a "high leg" or "red leg" delta secondary, it's common when there is only a small percentage of 1 phase loads here in the US. It's a 3 phase 240V delta secondary, but one set of windings is center tapped for a Neutral to be able to supply 120V loads. So A-B is 240V, B-C is 240V, C-A is 240V, A-N = 120V, C-N = 120V, B-N is 208V but you cannot use it.

All of that is immaterial to the issue at hand. A 240V (220V) motor can be connected between any two legs.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#18
In reply to #14

Re: Supply 1 Phase Motor

04/24/2011 10:20 AM

JRaef; why would you say that you cannot use the 208 volts from the hi leg? I have some 208 single phase motors that that wouldn't know better & go ahead & run. also many delta wound transformers only wind a single 120 volt winding from A or C, that way they save money. perry

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#27
In reply to #18

Re: Supply 1 Phase Motor

04/24/2011 9:33 PM

"JRaef; why would you say that you cannot use the 208 volts from the hi leg? I have some 208 single phase motors that that wouldn't know better & go ahead & run. also many delta wound transformers only wind a single 120 volt winding from A or C, that way they save money. perry"

OK, maybe I should have said "should not use it". The problem is, 208V here is expected to be 208 Line to Line on a 208V system. In that High Leg delta system, 208V is Line to Neutral from the high leg and although technically something like a motor may not care, in practice if someone sees a single colored conductor along with a white conductor in a box, they might ASS-U-Me it is 120V by convention and cause a fire by hooking it to something not rated for 208V.

Problem #2 is that in many cases, the 120/240V 3 phase 4 wire delta service is dropped from an open delta transformer arrangement, where there are two transformers; one of them center tapped for the 120V lighting loads. So the Neutral reference is only technically present in that one transformer and if you load the High leg too much on that open delta, you may not get 208V out of it. I have heard tell of people getting only 190V. It was not intended to be used, so there are no design specs as to how it reacts to a Phase-to-Neutral connection.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#15

Re: Supply 1 Phase Motor

04/24/2011 12:22 AM

If the motor windings are not grounded, Yes, connect up the 220 lines to the motor.

I assume the transformer is delta wye. ( Or is it a Scott T?)

Now the caveat. You need sufficient KVA for your motor. You will only be able to use 1/3 of the transformer rating. You will need to ensure additional loads are balanced on the other legs to not overload the windings.

Register to Reply
Anonymous Poster #1
#19
In reply to #15

Re: Supply 1 Phase Motor

04/24/2011 10:50 AM

GW; Da its a delta, why? could be a open delta, made with 2 single phase transformers, right? from a 3 phase source. why do you need to load the unused phases? guest

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#24
In reply to #19

Re: Supply 1 Phase Motor

04/24/2011 4:38 PM

You don't need to load the unused phase(s). BUT if you add loads they need to balance the transformer. The single phase load is sitting on "one side". You don't just add up the kva, but need to distribute it correctly.

Register to Reply
Register to Reply 30 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ALI99 (1); Anonymous Poster (1); GW (3); harry potter (1); hien.nguyenquoc (4); JRaef (3); old salt (2); perry (4); Signode (1); TonyS (4); Tornado (6)

Previous in Forum: Force Current And Force Voltag Analogy   Next in Forum: 50DD Current Disturbance Detector

Advertisement