Smart Grid

05/02/2011 12:51 AM

Dear Friends,

I am crazy about Smart Grid ... My doubt is : How the two way power flow is possible in smart grid?

Can you suggest any books or website which are good at smart grid basics

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Smart Grid

05/02/2011 12:54 AM

Much the same as in any system of paralleled generators. If the prime mover source (fuel, water flow, etc.) can support the kw drawn off, and if the voltage of the individual generator is ever so slightly above the grid (bus) voltage, then power will pass from the generator to the grid (bus).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Associate

Join Date: Jul 2010
Posts: 39
#2
In reply to #1

Re: Smart Grid

05/02/2011 3:00 AM

Dear Tornado

Thanks... In a power line, there is 2 sources so power can flow in full duplex mode or half duplex mode?

Register to Reply
2
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#3
In reply to #2

Re: Smart Grid

05/02/2011 7:30 AM

I don't think full or half-duplex is a good way to describe the flow of power. Duplex started being used as a term related to communication circuits in which half duplex usually represented a communication circuit that could communicate in only one direction at a time. Hmm, should I elaborate further--naah.

In the system as Tornado described so well, the power flow direction changes as the voltage from a generator varies--when the generator voltage is above the system voltage, power flows from the generator to the grid. When the generator voltage is below the system voltage, power flows from the grid to the generator.

The flow in those two directions is over the same wires / circuit.

I suppose you could draw an analogy to full and half duplex, but I'm not sure how I'd make the analogy. As I said above, the flow in those two directions is over the same circuit, which somewhat argues for calling it full duplex. But the flow is not simultaneous in both directions which argues for calling it half duplex.

I wouldn't use the term duplex in this context.

Register to Reply Good Answer (Score 2)
Associate

Join Date: Jul 2010
Posts: 39
#4
In reply to #3

Re: Smart Grid

05/02/2011 2:50 PM

Thanks ya I accept duplex cant be used here. Can you say Is it possible to control power flow from a source independent of load/

There is a generator 100kVA and solar power home capacity 10kVA(5 kVA own use+5kVA for exporting to Grid) which also connected to grid load increased to 120 kVA in this situation how we can avoid home from overloading and we can overload the generator to compensate extra 15 kVA power

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#5
In reply to #4

Re: Smart Grid

05/03/2011 12:24 AM

You cannot control power independently of load.

You "might" be able to control voltage, or possibly even amperage, but you often do that by adjusting the load, so whats the point?

Here are some formulas.

However, that being said, I suspect the real answer to your question lies in Thevenin's Theorem, and its applications. If you don't know how to thevenize your circuit, then why the heck are you playing with such complex circuitry?

__________________
If it was easy anybody could do it.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#7
In reply to #4

Re: Smart Grid

05/03/2011 1:16 AM

you have a 100kva generator and 10kva PV panel both connected to the grid, with a load of 120kva, right?

in this case your deficit is only 10kva, none will be overloaded, the deficit will be compensated from the grid, if your control system is "smart" enough

__________________
dont say it, write it
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#6
In reply to #3

Re: Smart Grid

05/03/2011 1:11 AM

rhkramer,

I would vote your post as good answer, but there s a small error to rectify before,

the power flow is related to frequency difference not to the voltage, the voltage difference will cause a flow of reactive power only

regards

__________________
dont say it, write it
Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#9
In reply to #6

Re: Smart Grid

05/03/2011 6:03 AM

Maybe the OP is asking if his system returns power back to the grid, will the electric meter run backwards?

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#10
In reply to #6

Re: Smart Grid

05/03/2011 8:14 AM

Good point, thanks!

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #6

Re: Smart Grid

05/03/2011 12:12 PM

Hi,

Since reactive Power is a condition dictated by the load (unless a synchronous machine is used as a motor, over-excited to produce capacitive power to compensate...), If the voltage output is manipulated, don't you think that the result is actually increase or decrease of the active power being shared? In this case, of course, the reactive power share is de facto also shared (or shifted to the other gensets on the grid).

The frequency is supposed to be fixed in a parallelling system. The fact that you try to increase the speed of the genset, will only mean that you are taking more of the load, which is translated by the AVR to an increase of the voltage to force more current to the grid. The increase of field current creates a load on the shaft and therefore keeps the actual speed the same.(hence the frequency stays the same). If the speed is increased dramatically, the magnetic coupling of the genset to the grid will be compromised and the set will be out of synch ... consequences???

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#18
In reply to #6

Re: Smart Grid

05/05/2011 7:39 PM

Le Noble (Post #6)

This is incorrect! The frequencies have to be the same. Only the voltage and phase can be used to control the power flow (real and reactive).

While the grids are intrinsically bi-directional, the protections are not. This is one area where the work has to be done. Some (if not most) transformer protections do not accept reverse power.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#20
In reply to #18

Re: Smart Grid

05/06/2011 1:21 AM

your quote :Only the voltage and phase can be used to control the power flow (real and reactive).

euhh!!!!

please tell me how,with the phase, you control real power flow in this case (100 kva generator connected to an infinite grid )

With due respect..

__________________
dont say it, write it
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#21
In reply to #20

Re: Smart Grid

05/06/2011 1:28 AM

I don't think "phase" and "real" should be highlighted together. Voltage-real and phase-reactive seem to be better matches.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#22
In reply to #21

Re: Smart Grid

05/06/2011 1:45 AM

Voltage-reactive

RPM-real

this is the good combination

while in synchronism, there is no phase difference, both systems are in phase (this is the meaning of word synchronised, as per my poor understanding of english)

you control the real power flow and amount to an element on the grid by the RPM of its prime mover, with reference to the grid frequency

I used the word frequency ( wich is usually directly linked to RPM) to respect the technical background of the OP, and not to confuse him while talking about RPM of a PV system, but unfortunatly this confused our Canadian friend Marot.

Sorry for this,

I hope my idea is clear

Regards

__________________
dont say it, write it
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#23
In reply to #22

Re: Smart Grid

05/06/2011 6:28 PM

Actually, I am not confused, this is my line of work. (Note that in my post, I didn't say what controls what. I only said that the voltage and phase are your only variables for controlling the power real or reactive).

Your understanding of the control is an over-simplification of what is really happening.

Once you close the breaker and connect the generator on the network, you loose control of the synchronous generator RPM as it becomes fix until you over do it and get a pole slip. Asynchronous generators work differently.

Under lock (synchronized), your RPM governor becomes a power control. When you change the power setpoint, you change the phase between the generator and the network. In theory, you could change it by +/- 90 degrees. In practice it is much less. The phase shift affects mostly the real power but the reactive power is also changed. When you change the voltage, the reactive power is changed and the real power change as well in a smaller amount.

The reason for this is that the power flow depends on the vectorial combination of the generator phase and voltage. They are linked together by trigonometric relationship with the impedance. In most systems, the phase angle is small, therefore the voltage has a larger effect on the KVARS than on the KW.

If you are going to design an automatic controller for a generator, you need to take this into consideration together with the complex impedance of the generator and possibly the network impedance.

At your level, you simply plug the sucker in and play with the controls until it sort of work or the protection trip...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#24
In reply to #23

Re: Smart Grid

05/06/2011 6:48 PM

your quote:

At your level, you simply plug the sucker in and play with the controls until it sort of work or the protection trip...

What do you know about my level? I simply replied within the technical level of the OP, who is not interested neither in your level nor mine,

Cheers

__________________
dont say it, write it
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#25
In reply to #24

Re: Smart Grid

05/07/2011 1:23 AM

Sorry Le Noble, you showed us your level when you could not understand how phase angle (also referred to as power angle in electrical machine theory) controls real power flow into or out of a machine. As Marcot explained, once a machine is connected to a grid the instantaneous relationship between axis of the rotor field poles MMF relative to the MMF from the system rotating around the stator determines whether the machine is producing power or absorbing it. It is a generator if the rotor is "ahead" of the MMF, and a motor if it is "behind" it. The net MMF is "stretched" but does not lose synchronization as more fuel is forced into the prime mover, so the term phase is a correct way of viewing the relative positions of the MMFs.

Exactly the same thing happens with reactive power except it is the amount of net MMF in the air gap that determines which way the VARs flow. If the excitation system provides more field current hence more MMF than the stator provides from the system, then the machine is overxcited and this excess MMF leaves as VARs that are flowing out of the machine and vice-versa. There is a quadrature relationship between real and reactive power so that despite what you may read on many posts on CR4, real and reactive power act relatively independently of each other; i.e., against an infinite bus increasing the fuel supply increases real power (kW) with minimal effect on reactive power, similarly increasing field current increases reactive power (VARs) with minimal effect on real power. In isolated or loosely coupled systems there is an entirely different set of dynamics and interactions involved so this analysis needs modification.

As far as an inverter is concerned, the control circuitry looks at the incoming system sinewave and forces the circuitry to create a sinewave that leads the system thereby creating a positive phase (power) angle that "pushes" real power into the grid. The circuitry also controls the inverter output voltage relative to the system to control reactive power flow. To the OPs original question, that is how both real and reactive power flow is bidirectional.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#26
In reply to #25

Re: Smart Grid

05/07/2011 2:44 AM

BlaBlablabla...

Again dont talk about levels , while you know nothing about mine.

I am not here for a fencing to show levels, I am replying the OP in a simple language could be understood by all levels.

To an end user what is easier to understand the theory of rotating fields, like MMF vector amplitude E = KNΦf = KNΦpnS = K' ΦnS, and the direction of rotating field when the stator field is locked to the synchronism frequency of stator, or just with simple words anyone can understand,

increase the field excitation current (which increase the generator voltage) to increase your part of KVAR,

and increase / decrease the RPM of your prime mover (wich increase / decrease the phase difference between two vectors)to increase/decrease the part of real power..

BTW, I referred to a post by you about similar thread

http://cr4.globalspec.com/thread/67687#comment715508

I didnt see any mention for the phase, rotating vectors,who is ahead who is behind....you talked about just speed voltage,

is it question of level?

cheers

__________________
dont say it, write it
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#8
In reply to #1

Re: Smart Grid

05/03/2011 6:01 AM

Actually, I think changing the excitation (voltage control) will cause reactive current to flow between the generators. Increasing the engine throttle on one will increase the amount of real power (kilawatts) delivered to the load and decrease the kilawatts from the other generator. The more the throttle is increased, the more the rotor field leads the stator field. On the other hand, if the throttle is reduced enough, the rotor field will lag the stator field and the generator will act as a motor and absorb power from the bus.

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#11
In reply to #8

Re: Smart Grid

05/03/2011 10:46 AM

This is an overall reply.

Generators on the same net HAVE TO BE on the same frequency, or better shut down before destroyed by excessive current. Setting that abnormal case aside, in an well regulated net just 5 cases should arise among generators:

1,. Same phase, same voltage. The load is shared based on the output impedance of the individual, paralelled generators.

2,. When there is a deviation from 1,. If the output voltage tries to be higher on one, it shares a higher portion of the load.

3,. When the voltage tries to be lower, the portion of the load is lower. If it is low enough, the generator acts as a motor instead.

4,. When the voltage phase of one is ahead of the other, it adds an inductive component to the real power.

5,. When the voltage phase is retarded, it adds a capacitive component.

Power companies charge extra to large customers for 4,. and 5,. having to perform phase correction duties on the top of delivering real power. For them, these circulating currents are a nuisance to be eliminated.

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#12

Re: Smart Grid

05/03/2011 11:05 AM

To the basic idea "Smart Grid".

Let me explain in my best Shakesperian English: There ain't no smart grid (outside the internal power companies interconnects), and there won't be neither:

There are already enough industrial Internet attacks (see Stuxnet for example) to show the blooming idiocy of opening it up to any and all hackers.

I interviewed a number of women, what the think of the utility controlling her washer.... etc. Meaning: she want to wash at noon, the utility turns off her washer, allowing it only at midnight. Answer: over your dead body!!! When she needs it, she wants it. Period.

You are free to disbelieve. So, go home, and ask your better half, and report back. In the meantime, good luck!! Forcing the needs of the significant half of the population? Riled up they will vote away your funding in no time flat.

Register to Reply
Associate

Join Date: Jul 2010
Posts: 39
#15
In reply to #12

Re: Smart Grid

05/03/2011 12:19 PM

Thanks leveles Now I am answering for your view about smart grid not technical content

Smart Grid is not only control your washer it integrates Solar panel or wind mill in your house to Grid system. So you can export power when you have excess power. Also, developing countries like India we are facing several hours blackout due to faults which is also can be reduced. So people those who wants green can participate in Smart Grid others don need.

I did ma UG thesis in Demand Side Load Management when I found 30 HP motor in our college as fully controllable since it is a sewage treatment plant motor.

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#17
In reply to #15

Re: Smart Grid

05/03/2011 10:44 PM

You are absolutely right in your sentiments, ,and applicable to your circumstances. Me having arguments with solutions for your problems? No. And I do not care what you install. Whatever fits you is ok.

BUT, smart grid obviously means different things for you and me. I was responding to the standards proposed. They contain unhealthy ideas any large energy producer have to be concerned about. And, I repeat, the standards proposed were designed WITHOUT the input of our women (by the last account 50% of the voting population, and mostly running the household). So, buddy, are you sure, you really want to make pronouncements without them??

Register to Reply Score 1 for Off Topic
Associate

Join Date: Jul 2010
Posts: 39
#29
In reply to #17

Re: Smart Grid

05/23/2011 11:04 AM

Mr.Dave is correct.

I understood him Thanks for his good explanation.

I have doubt that to export power from home to grid. Our home power source should synchronise with grid. So how is itp ossible. Since, I went to power station for Internship where it took 2 days for synchronising 500 MW generator to grid.

Register to Reply
Participant

Join Date: May 2011
Posts: 1
#13

Re: Smart Grid

05/03/2011 12:12 PM

Try "Perfect Power" by Bob Galvin and Kurt Yeager. In partiucular the book addresses the issue of bi-directional power via the application of microgrids. Bob is the former chairman/CEO of Motorola and Kurt Yeager was the CEO of the Electrical Power Research Institute (EPRI) for many years until he retired recently. It a great "insiders" look at the issues and opportunities involved with the National Grid, Smart or otherwise.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2010
Posts: 39
#16
In reply to #13

Re: Smart Grid

05/03/2011 10:40 PM

Thanks a lot...

But in India it is not available. I called to book shops. they said they don have. Can you please send the publisher of this book or e-book link.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#19
In reply to #16

Re: Smart Grid

05/05/2011 10:46 PM

Google and Amazon to the rescue...

http://www.amazon.com/PERFECT-POWER-Microgrid-Revolution-Abundant/dp/0071548823

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
2
Active Contributor

Join Date: Mar 2010
Location: Texas
Posts: 22
Good Answers: 1
#27

Re: Smart Grid

05/19/2011 11:25 AM

The best way to look at an electric grid is to compare it to a river. A customer digs a ditch and taps into the river to receive water. If the customer's level of water in his ditch is lower than the river the river water flows into the ditch (user). If the customer puts water into his ditch instead of taking it out his water level will be higher than the river. Under that condition his water flows into the river.

Hope this helps Dave

Register to Reply Good Answer (Score 2)
Associate

Join Date: Jul 2010
Posts: 39
#28
In reply to #27

Re: Smart Grid

05/23/2011 11:03 AM

Dave I understood Thanks for ur good explanation.

I have doubt that to export power from home to grid. Our home power source should synchronise with grid. So how is itp ossible. Since, I went to power station for Internship where it took 2 days for synchronising 500 MW generator to grid.

Register to Reply
Active Contributor

Join Date: Mar 2010
Location: Texas
Posts: 22
Good Answers: 1
#30
In reply to #28

Re: Smart Grid

05/23/2011 11:46 AM

Synchronization is done by an inverter that electronically synchronizes. The lock-in can be done nearly instantaneously to a few minutes depending on the control system used. I am involved in smart grid energy storage.

Dave

Register to Reply
Active Contributor

Join Date: Mar 2010
Location: Texas
Posts: 22
Good Answers: 1
#31

Re: Smart Grid

05/23/2011 11:47 AM

Try searching the internet. I work at a much higher level but there are many simple slide presentations on the net about smart grid.

Register to Reply
Associate

Join Date: Jul 2010
Posts: 39
#32
In reply to #31

Re: Smart Grid

05/24/2011 10:15 AM

Thanks as u said I referred many websites today but I cant find website which are very good at technically related to Smart Grid

Could u suggest any websites

Regards,

Mansoor

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#33
In reply to #32

Re: Smart Grid

05/26/2011 2:43 PM

What type of "technically related" info do you need? Here's a sample of useful sites from Google University...

http://www.oe.energy.gov/smartgrid.htm

http://www.smartgridnews.com/

http://en.wikipedia.org/wiki/Smart_grid

Try getting the book referenced in Post #19 o f this thread.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 33 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

btpatterson (1); Dave K. (3); flyinghigh (1); LAA_Lucke (1); Le_Noble (6); leveles (3); mansoor_vm (7); marcot (2); RAMConsult (3); rhkramer (2); Rixter (1); Tornado (2); Yusef1 (1)

Previous in Forum: Xantrex 1800 Watt Solar Package   Next in Forum: Modern Solar Heat Collectors, What Happens If the Energy is Not Used?
You might be interested in: Smart Cameras, Smart Card Chips

Advertisement