UPS on Diesel Generating Set

05/03/2011 11:40 AM

Hello Gents,

Is there any technical disadvantages in connecting 120kVA rated UPS to 100kVA diesel generating set. Also, what percentage of load does the UPS present to the generating set.

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: UPS on Diesel Generating Set

05/03/2011 12:18 PM

What is the loading on the system?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Apr 2011
Posts: 8
#4
In reply to #1

Re: UPS on Diesel Generating Set

05/03/2011 12:34 PM

Thanks TonyS,

The UPS are ment to supply the office workstations(computers, printers and scanners). The esitmated demand load for all these workstation is about 80kVA. The 120kVA UPS had been procured and delivered to site by the client.

Please kindly advice if there are technical disadvantages in this system.

Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: UPS on Diesel Generating Set

05/03/2011 12:22 PM

what percentage of load does the UPS present share with the generating set?

Is that what you mean?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: UPS on Diesel Generating Set

05/03/2011 12:26 PM

No, the UPS just won't supply more than the combined output of the remaining battery power plus 100kVA. The load the UPS presents to the DG dependS upon the conversion efficiency of UPS at the load it is supplying.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Apr 2011
Posts: 8
#5
In reply to #3

Re: UPS on Diesel Generating Set

05/03/2011 12:42 PM

Thanks. I appreciate

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: UPS on Diesel Generating Set

05/03/2011 10:35 PM

Disadvantage? Usually it's an ADVANTAGE to have a UPS in conjunction with a DG. The DG needs time to come on line, critical systems, such as computers in mid--process, cannot tolerate more than a small fraction of a second of no power. So the UPS ensures a continuous flow of energy to the critical equipment, but only for as long as the batteries last. The DG is then making sure the batteries are kept charged.

As long as the fuel holds out of course...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: UPS on Diesel Generating Set

05/04/2011 6:45 AM

Another important factor in selecting the DG rating for supplying the UPS is the harmonics that the UPS presents to the DG.

This requires that the generator is oversized and the AVR is appropriately selected to suit the harmonic ridden voltage feedback signal it receives from the generator output terminals.

DG vendors have articles on the subject (for example - Cummins website).

__________________
Raghunath
Register to Reply
Member

Join Date: Apr 2011
Posts: 8
#8
In reply to #7

Re: UPS on Diesel Generating Set

05/04/2011 10:49 AM

Thanks Raghun. I appreciate your comments.

Kindly send me a link for more details.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: