Generator Voltage Variation and Frequency DOP Problem

05/06/2011 1:03 AM

Hi,

We have 6nos of standby 3 ~, 50 Hz,1400KVA, 1120kw, 2021A, MODEL: CAT 3512 diesel gensets.

At 1 of them, there is a problem of voltage variation(+-40V) when we put load at it. e.g if it is operated at say 1100 A, the voltage are 400V: when load is increased to 1200A, voltage may go to 420V or 375V etc. This variation remains till the generator operates. (Voltage reg response time, Exciation I prob).

At 2nd, its rpm goes down when operated at load resulting in low freq. primarily, if it was operating at 1300A, the load at once reduces to 600A, then generator picks rpm and freq goes to 50Hz.

Can any one plz guide me how to overcome these probs. Thanks in advance for your valuable/useful comments.

Regards.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Generator voltage variation and frequency dop problem

05/06/2011 2:19 AM

Are they operated in Synchronisation or are they operated in stand-alone mode?

I would suggest to have a thorough check on the AVR & the Governor of the DG Sets.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Generator Voltage Variation and Frequency DOP Problem

05/07/2011 12:28 AM

What is "DOP"?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Feb 2011
Location: Pakistan
Posts: 18
Good Answers: 2
#3
In reply to #2

Re: Generator Voltage Variation and Frequency DOP Problem

05/07/2011 4:13 AM

Go for TA test form gen vendor.

Register to Reply
Participant

Join Date: Apr 2011
Posts: 2
#4
In reply to #2

Re: Generator Voltage Variation and Frequency DOP Problem

05/07/2011 4:23 AM

@ Electricalexpert65: Its standalone mode, No synch.

@ Tornado: Sorry Sir, Its typing mistake, DROP not DOP.

Thanks for your replies.

Rgds.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5

Re: Generator Voltage Variation and Frequency DOP Problem

05/07/2011 7:30 AM

Not enough information:

1) On this unit, you should check and see if the Voltage variation is accompanied with a change in the frequency (rpm of engine).i.e., when you increase the load to 1200A, is there a frequency (rpm) increase with Voltage increase or drop in rpm with voltage decrease (or the opposite...). Also, is the voltage variation on the 3 phases or on one or 2 of them only.

2) On this unit, how does the load drop to 600A? is it that you shed some load (put off) to reduce it to 600A manually and then the rpm pics up? OR the engine by itself just drops its output to 600A with the same load connected still?

Finally, some observations: The Voltage in 1) cannot be going Up and down sporadically, without some different reasons, unless you have a loose connection or bad joint in the AVR which starts to misbehave at high load (high excitation current produced by the AVR). But this is speculation and needs more input as mentioned.

On the 2nd engine, it could be that the governor that controls the fuel rack is behaving: mechanical or electrical problem, depending on the installed system.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6

Re: Generator Voltage Variation and Frequency DOP Problem

05/08/2011 8:18 AM

QAMAR:

I don't know for sure about the problem you are facing since generator is not my expertise but I am pretty sure that the gurus here will give you a hand troubleshooting the problem. Hope that you will give them more details about that.

Some of comments would not solve the problem immediately but after we go through all of them, we will have a clearer view on over the things which I think they are much valuable. Most of guests and new comers come on here just want to have an immediate correct answer for their problems. It will not work out that way.

Could you do me favour by updating the problem after you find it out? This would be used as an experience which I think it will help the others in the future. Consider the time it has taken for you to log on here and the other times of other people to read and look for the answer. Your updating would be highly appreciate.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Associate

Join Date: Jun 2008
Location: San Antonio, Texas
Posts: 47
Good Answers: 1
#7

Re: Generator Voltage Variation and Frequency DOP Problem

05/09/2011 8:24 AM

Wondering last night why is it that we can't install step up generators at our homes & 'create' more energy? Transformers are mounted on telephone poles & make it possible for a limited amount of current to be stretched to cover more homes & more demand. What is it that I don't understand? We would require less of the energy providers & save ourselves some cash. Carlos