Two Motors on One Soft Starter

05/06/2011 7:15 AM

Usually we run one motor with one soft starter. Is it possible to run two motors with one soft starter and how?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Two motors on one soft starter

05/06/2011 7:26 AM

Why is it necessary?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Two motors on one soft starter

05/06/2011 9:01 AM

It's cheaper, and how.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Two motors on one soft starter

05/06/2011 9:04 AM

Oh, go on. Do tell.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4

Re: Two Motors on One Soft Starter

05/06/2011 9:36 AM

I can imagine one or more ways to do it (depending on some related factors--do you want to run the motors simultaneously, on the same process / shaft), but it would require extra equipment and is almost surely not worth the effort.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Two Motors on One Soft Starter

05/06/2011 11:04 AM

It's done all the time. There are caveats though:

  1. The motors must be the same size. Mixing motor sizes generally ends up with some sort of unsatisfactory ramp of one or the other motors, or both.
  2. Both motors must start at the same time. One can stop separately if you have separate contactors, but the soft starter has no way of re-starting a second motor once it's done ramping unless the first one is isolated from it after accelerating (see #6 below).
  3. You need separate Over Load Relays for each motor, but tied into the soft starter to shut it down if EITHER motor overloads. If you have separate contactors you can shut down only one however. But if you do, and then start only one motor next time, your Current Limit settings will no longer be meaningful. There are however some soft starters that allow "dual ramps" so they can be configured to use a "1 motor" and "2 motor" ramp scenario if one of the OLRs trip.
  4. Its a good idea to over size the soft starter by about 10% of the combined FLA of the motors. Soft starter overload ratings are a numbers game played by 90% of the manufacturers, with most having very little room for error. Having two or more motors increases the possibility of unbalanced currents which the soft starter may respond to by staying in Current Limit longer, which increases the stress on the soft starter.
  5. You have to pay very close attention to the Short Circuit protection of each motor. Sometimes you can get lucky and have only one SCPD ahead of the soft starter that will fit within the code limits of the smaller motors, but sometimes not. If not, you have to have a Main SCPD for the soft starter and then SEPARATE systems (fuses or CBs) for each motor circuit, which again can drive the cost up higher than just buying two soft starters. If you are looking at small motors (i.e. 63A or under), a good compromise is an IEC Motor Protective Switch that has the SCPD and OL in one.
  6. Forget the idea of "recycling" the soft starter. That power scheme requires more control complexity and contactors than most people realize. It ALWAYS ends up more expensive than just buying two sot starters.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#6
In reply to #5

Re: Two Motors on One Soft Starter

05/10/2011 3:25 AM
__________________
shamith gambhir, electrical engineer
Register to Reply Score 1 for Good Answer
Register to Reply 6 comments