Earthing System: Dirty/Clean Earth

04/11/2007 9:31 AM

Hi mates this is first time for me

I need to clarify this

  1. deferent between dirty earth and clean earth and why thy separate it at panel although at the end it was connected together
  2. How can you decide your ELCB sensitivity ex 300mA less or more
  3. If I have main panel feed branch panels and this panels feed individual load do I need to install ELCB at each end load or the one at main enough
Register to Reply
Pathfinder Tags: Dirty earth and clean earth
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Earthing System: Dirty/Clean Earth

04/11/2007 4:52 PM

Very simply

1. normal protection earth (dirty) and signal earth (clean) are kept separate and linked only at one point to prevent noise on the main protection earth from causing interference in sensitive electronics connected to the clean earth.

2. Depends on local regulations and standards. As a general rule of thumb only, 30mA for residential protection, 100 or 300mA for industrial.

3. Depends on local regulations and standards. As a general rule of thumb only, 1 ELCB can protect multiple feeders. If the feeders are powering variable speed drives or other devices with high leakage current to earth then this may not physically be possible thou.

Check your local electrical regulations for the actual requirements relevant to your country.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#2

Re: Earthing System: Dirty/Clean Earth

04/12/2007 2:40 AM

Dear Khalid,

1. As commented by Jack->#1

2. 10mA for Medical Electronic Equipment, 30mA for Human protection (power outlet), 300mA for Fire protection (Lighting system).

3. Normally main is Circuit Breaker, branch is ELCB but depend on the category as no.2 above. You have to consider the discrimination aspects and material cost.

regards.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#3
In reply to #2

Re: Earthing System: Dirty/Clean Earth

05/15/2007 3:59 PM

*************** Quote **************

2. 10mA for Medical Electronic Equipment,

*************** Quote Ends **********

<50 μA for under-skin Monitoring: Highly-Isolated