CT Sizing of Transformer Ground Cable

05/11/2011 11:44 PM

Dear all,

Is it normal to have half sizing of the nominal current of transformer to detect Earth Fault/Restricted Earth Fault?

I have 5MVA 11/.38 kV transformer, with 5000/5 CT on the secondary side.

I'm planning to install 2500/5 or 2000/5 CT for the ground cable to detect Earth Fault/REF, as I know the setting value is always low.

Thank you for all of your help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: CT Sizing of Transformer Ground Cable

05/12/2011 4:52 AM

For REF protection all the four CTs to be of same specification and turns ratio.

Earthing of transformer neutral is to be after CT.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#2
In reply to #1

Re: CT Sizing of Transformer Ground Cable

05/12/2011 5:26 AM

As can be seen in the drawing, there is one CT, on the right side, for grounding cable (green cable).How do we calculate the size of the CT? What class should be used?

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#6
In reply to #2

Re: CT Sizing of Transformer Ground Cable

05/12/2011 12:25 PM

Local_Eng:

What I see, is the only one smaller green wire connected to the neutral bar. It is Ground Return Sensing Method, isn't it? You just need to size the CT to operate at the current that the grounding wire can carry.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#16
In reply to #2

Re: CT Sizing of Transformer Ground Cable

05/15/2011 10:35 AM

I assume that you are talking about non-restricted earthfault protection. If so, the CT size depends upon the required protection level that you want. At the same tim if you keep it so small, then during a high fault, the CT might saturate. It has to be a balancing act. The class can be 5P10.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: CT Sizing of Transformer Ground Cable

05/12/2011 5:36 AM

That's earth fault for the system, not restricted earth fault.

To be honest the earth (ground) looks far to small, what size are the conductors?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#4

Re: CT Sizing of Transformer Ground Cable

05/12/2011 6:17 AM

Yes.. It's an earth fault for the system.

The cable size is 185mm2. How do we calculate the size of the CT then?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: CT Sizing of Transformer Ground Cable

05/12/2011 7:50 AM

Your going to have to look at the entire transformer set up if you want restricted earth fault. The neutral earth connection will have to be moved for a start.

Your existing 5000/5A CT's are too small for the maximum transformer rated current of 7600A. What are they used for at the moment, or is it just the E/F C/T you refer to?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: CT Sizing of Transformer Ground Cable

05/12/2011 3:14 PM

What country is this in (this is an international forum)?

Are you using a neutral earthing (or grounding) resistor to limit the earth fault current (may explain the small size of the earth wire)?

Do you know what your (approximate) fault current is and what transformer relay protection settings (especially the time delays relating to earth fault disconnection) are?

Thought I better ask for clarity.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#8

Re: CT Sizing of Transformer Ground Cable

05/12/2011 9:57 PM

Dear all,

A REF protection requires all CTs with the same CT ratios. Therefore, total five CTs (for 3 phase lines, 1 neutral and 1 neutral earth conductor) are all 5000/5A.

If the protection relay is micro-processor type, the CT ratio for the neutral earth conductor can be selected with a different CT ratio from other 4 CTs. Please refer to your relay manual.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#11
In reply to #8

Re: CT Sizing of Transformer Ground Cable

05/13/2011 8:27 AM

What does REF mean?

Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#12
In reply to #11

Re: CT Sizing of Transformer Ground Cable

05/13/2011 8:48 AM

Dear all,

REF: Restricted earth fault is differential protection for transformer Wye winding.

Each of all conductors brought out from the winding must have a CT of the same ratios. The total of the CT secondary currents is zero, if no earth fault on the winding. If non-zero, an earth fault is inside the winding.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#13
In reply to #12

Re: CT Sizing of Transformer Ground Cable

05/13/2011 8:57 AM

Thanks!

Register to Reply Off Topic (Score 5)
Commentator

Join Date: May 2011
Posts: 80
#9

Re: CT Sizing of Transformer Ground Cable

05/12/2011 11:59 PM

@ TonyS: I'm sorry for the limited information. Actually the 5MVA transformer installation is in progress. The photo is the existing transformer with EF issue, and we have to follow it.

For the new transformer of 5MVA, the ip LN fault current is 211kA with 8000/5 CT.

Is it ok if I use 800/5 CT to detect the EF?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10

Re: CT Sizing of Transformer Ground Cable

05/13/2011 7:21 AM

REF requires 4 matched C/T's but you've obviously got that sorted.

As to the general E/F C/T I think you need to talk to others on the board, my main concern is saturation of the C/T under fault conditions. I've never fitted a neutral/earth C/T that was underrated.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#14

Re: CT Sizing of Transformer Ground Cable

05/13/2011 12:23 PM

it depends.. know the acceptable unbalance current as well as the maximum fault current that could pass through the current transformer.. you may change the ratio of your CT if it will lessen the burden that the CT will handle..

Register to Reply
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#15

Re: CT Sizing of Transformer Ground Cable

05/13/2011 1:07 PM

Re earth fault protection (REF) 3 nos. phase CTs are required at the line side of the LV breaker (above the breaker), 1 no. neutral CT is also required to be located at the neutral of the transformer secondary, ground should be installed below this neutral CT. The 4 nos. CTs shall be identical or same spec & turns ratio. The CTs shall be sized more than the FLA of the transformer at the secondary.

Under normal operation current will remain stabilized , full load current should be flowing through the 3 phase CTs and neutral CT, all connected in parallel including REF relay. In the event of LV line to earth fault (between phase CT to transformer secondary winding) , current will only flow through neutral CT and the REF relay. This relay could be set to operate at 10 to 20% of FLA.

During stability test, stabilizing resistor in series with the REF relay should be adjusted to avoid nuisance tripping.

thanks and regards,

rudy_fernando5r

Register to Reply Off Topic (Score 6)
Participant

Join Date: Apr 2011
Posts: 3
#17

Re: CT Sizing of Transformer Ground Cable

05/15/2011 11:52 AM

Dear friend,

There are two things, one is EARTH FAULT i e it is a line protection,second REF it is for transformer winding earth fault protection.

It is not necessary to provide C.T. in neutral conductor for line earth fault detection but earth fault current can be sense by providing an earth fault relay in between common point of R_Y_B O/C element and C.T.star point.

For REF protection we needs all C.T. of same ratio and same protection class generally it is PS class having ratio near to but more than full load of the protected object.

RAKHOLIA B.K.

CR4 Admin - email address removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system.

Register to Reply