UTE145E PT
05/13/2011 11:58 AM
Is there any one has some information as where can I buy this PT in north america. or if any one has a used one. I am looking for one to replace the existing PT as it exhibits some crack on the housing
Type:
UTE145E
Serial #:
831204/3
Year:
1984
Primary:
84000
Sec. T.
X2-X3 Y2-Y3 X1-X3 Y1-Y3
Sec. V.
70 70 120 120
VA:
W.X.Y.Z W.X.Y.Z W.X.Y.Z W.X.Y.Z
CL:
0.3 0.6 0.3 0.6
Total W.
350
Oil W.
75
KV:
145/275/650
Hz:
60
Re: UTE145E PT
05/13/2011 12:43 PM
Good Answers: 61
Re: UTE145E PT
05/13/2011 6:17 PM
The UTE145 series is from ABB/Kuhlman Electric, built at their instrument transformer facility in Versailles, KY. Contact information is here. Although your nameplate values are a bit non-standard, the ratios are standard (700:1 & 1200:1). They've done custom work for me in the past with good results.
Re: UTE145E PT
05/13/2011 7:56 PM
Very good answer. Your experience has found a good use - that is, if the OP even makes it back here. Since the OP didn't register, he/she won't get any email notification.
Anyway, GA.