132/33kV YNd Transformers in Petrochem

05/16/2011 4:26 PM

Hi,

I recently came across YNd1 and YNd11 transformers at 132/33kV (or similar) in new petrochemical installations. The 132kV system is solidly earthed at the star points of the generator transformers. The 33kV system is resistance earthed using zig zag transformers.

Question 1: What are the benefits of using this configuration instead of the more common one with Dyn11 or Dyn1 transformers?
Question 2: If the 33kV system supplies transformers only, does it have to be resistance earthed or solidly earthed is acceptable?

Thanks in advance...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: 132/33kV YNd Transformers in Petrochem

05/17/2011 2:39 AM

Dyn is preferred and YNyn is more common at 132/33kV level. YNd will mean higher voltage stress in 33kV system during single phase-to-ground faults necessitating use of cables and surge arresters having hiher specifications.

__________________
Raghunath
Register to Reply
Participant

Join Date: May 2011
Posts: 3
#2
In reply to #1

Re: 132/33kV YNd Transformers in Petrochem

05/17/2011 2:45 AM

So why then most of the petrochem installations I have seen recentrly use YNd transformers for these voltage levels? That's the thing I don't understand...

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3
In reply to #2

Re: 132/33kV YNd Transformers in Petrochem

05/17/2011 2:52 AM

It could be stipulation from grid authority!!

Grid authorities don't allow YNyn transformers in the consumer premises for thefear that an uncleared earth fault in 33kV system within consumer premises could cause trip of 132kV OHL(s).

However, there should not be a problem from their side if the trafo vector group is Dyn. You may like to check.

The Dyn trafos are generally costlier than Ynd trafos, when compared one-to-one.

__________________
Raghunath
Register to Reply
Participant

Join Date: May 2011
Posts: 3
#4
In reply to #3

Re: 132/33kV YNd Transformers in Petrochem

05/17/2011 3:03 AM

That's what I thought initially. But the installations I am looking at operate in island mode. They are remote and don't have any connection to the grid so the grid code does not apply...

I realise that Y primary needs less insulation so it's cheaper...

Does the fact that the 33kV system supplies power to three winding transformers of large VSDs have to do anything with it (reduction in harmonics)?

If not, the only thing I can think of is that YNd transformers are used for phase shifting purposes or just because they are cheaper (although a zig zag earthing transformers needs to be added)...

By the way, does the 33kV have to be resistance earthed? Is solidly earthed acceptable?

Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#6
In reply to #4

Re: 132/33kV YNd Transformers in Petrochem

05/18/2011 9:11 AM

Does the fact that the 33kV system supplies power to three winding transformers of large VSDs have to do anything with it (reduction in harmonics)?

Yes,you are right.Delta secondary winding is meant for harmonic reduction.

The Zig zag earthing transformer connected to the Delta Secendary side is meant to obtain a STAR point for system earthing.The same can be resistance earthed or solidly earthed .The Earth fault protection of the system may be designed accordingly.

__________________
Learning is a never-ending process.
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 22
Good Answers: 1
#5

Re: 132/33kV YNd Transformers in Petrochem

05/17/2011 9:47 AM

Check to see if they have a resistor in line with each of the Zig Zag transformer grounds. They use the Zig Zags for reference point for the protective relays for the undervoltage, overvoltage, and 50/51's. You also see these similar set ups in Water Treatment Plants. You are correct in that cost is probably a factor. Maybe ferro issues? I don't know if this set up would be more or less beneficial in terms of preventing ferroresonance in terms of loss of a phase and a floating reference point. Search under this topic in the forum. Usually ferroresonance takes place upstream of this setup at the main feed point where the utility comes into the main plant due to capacitance of the long cables and other factors and because they are too cheap to purchase the right type of input transformer for isolation.

Register to Reply