Transformer Radiator Fin Defect

05/17/2011 12:59 AM

Guys,

I having a transfromer radiator fins defects during installation at site. We plan to energize it soon.

By calculation:

1 unit radiator consist of: 22 row of 9 fins

Total radiator: 10 units

where;

22 X 9 X 10 = 1980 fins

defect: 18 fins ( 9 at the back + 8 at the front)

Defect percentage : 17 ÷ 1980 X 100

= 0.86%

Can I energize this transformer?? It will effect the cooling but we plan to change it later since we urgently need to commission our Plant as schedule.

__________________
Elect & Instr
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Transformer Radiator Fin Defect

05/17/2011 1:22 AM

Does it leak? (Beware also that even if not now, leaks might develop later.)

Some of the fins look crimped enough that no oil would flow through them by convection. But if they are less than 1%, then you would lose less than 1% of cooling capacity.

It is hard to tell whether field repairs would be possible or acceptable; consult the manufacturer, and also any local codes that may govern.

I hope you can make a claim against whoever caused the damage.

"Defect" is not quite the right term here. "Shipping damage" or "storage damage" looks more likely.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Transformer Radiator Fin Defect

05/17/2011 2:37 AM

If you commission the plant and the radiator then starts to leak your in trouble. Just as an idea but could you isolate the damaged bank. I know it means loosing 10% of your cooling but temporary fans cooling the other banks could make this up for this.

There will have to be a shut down to repair the damage, but you need to be in control of the situation and not have it forced on you.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Transformer Radiator Fin Defect

05/17/2011 7:33 AM

Potentially a really bad idea. It looks like a front-end loader really hit that row very hard. What you can't see is the internal damage that may have taken place, I don't know if the inside of the tank and/or fins has any protective coating, bit if there is then any flakes of paint or dislodged pieces of welding slag from the manufacturing process could have been loosened and may find their way into the windings with disastrous consequences. We also don't know if the transformer was on its pad or in transit when it was hit, therefore there's a strong possibility of internal damage to the core and/or windings due to the mechanical shock. Some of that damage may only be found after a rigorous internal inspection. Call me super cautious but I would never sign off on energizing it until it were cleared by a competent third party.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Transformer Radiator Fin Defect

05/17/2011 7:48 AM

<...urgently need to commission our Plant as schedule...>

If it goes BANG, will it affect the schedule?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#5

Re: Transformer Radiator Fin Defect

05/17/2011 2:20 PM

Let the top management take the decision, you will be on the side of caution, waiting for the replacement fin section to be fitted. I've been in large plants where the cost and production is the main or only consideration. In your country in fact at CIMA cement, a large fan breakdown shut the line with huge losses in production and some customers went to other suppliers. It may delay commissioning of lots of other systems if power is not available, the management will be aware of all this, start-up dates, penalties, cost.

I doubt if this transformer has been designed to run immediately at full load so there should be a margin to allow for the lack of cooling. You would need to check the design calculations and original specifications.

Ask some mechanical engineer to check for fractures in the dents, if it's only bent but still mechanically sound then personally I'd go for it, with the management aware of the risk when the pressure builds up, ( I'm assuming it's a sealed transformer with a gas pocket at the top). Ask the mechanicals about some of the super strong epoxy metal materials they have these days, I've got some that's good to 300 C, oil and watertight, and cover the seriously bent bits.

Spell out the risks to the management bosses, what's the worst case scenario? If it doesn't leak then it could overheat and trip upstream, let them contemplate a sudden shut down. Have they any stand-by power?

Find out when the remedial action is likely, from insurers, carriers, manufacturers, and let the management know when the future shut down will be needed.

Another point...does the fin section have valves so that it can be isolated. If it does you could valve this section off and run it. In Saudi, really hot , hotter than Malaysia, ABB transformers were uprated by 40% with a set of fans at the bottom of the fins, so you consider some temporary fans.

Lastly, I can't believe that you have a single transformer feeder, rather than redundant two in parallel, who designed it? You may be able to run with one feeder, with this damaged transformer out of service.

Register to Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#6

Re: Transformer Radiator Fin Defect

05/18/2011 9:34 AM

Whoever broke it should buy you a new one.

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#7

Re: Transformer Radiator Fin Defect

05/19/2011 4:03 AM

Replace the damaged fins before energising the transformer. Sudden, undetected leaks could result in catastrophic damage.

Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#8
In reply to #7

Re: Transformer Radiator Fin Defect

05/22/2011 11:32 AM

Engineers vary in their attitude to a calculated risk, I never killed anyone or caused a serious accident in 50 years construction & commissioning. At the same time I reckon I've saved millions of dollars by getting things moving when others were throwing their hands up or looking the other way.

There's an old management ditty "the only guys who never made mistakes are those who never did anything". Taking a calculated risk takes knowledge and experience, so probably the fact that you are asking what to do means you had better take the safe way and wait for the repair.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#9
In reply to #8

Re: Transformer Radiator Fin Defect

05/28/2011 10:19 PM

IF NOT LEAKING ALREADY- will not leak after energizing.

If you consider "Overdesign" by the original designer-- you will never need to replace the bashed radiator.

Take a deep breath and switch on and watch for a few hours .

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Transformer Radiator Fin Defect

06/08/2015 2:39 AM

Dear Mr.Yasser,

From the photo it appears DAMAGE DURING TRANSIT.

My suggestion, Pl. do not take risk, get it repaired and use. Once energised, any leakage(likely) will interrupt your working - leading to difficulties and losses. Prevention is better than cure.

By the way - what is the caapacity of the Transformer.?

DHAYANANDHAN.S

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#11

Re: Transformer Radiator Fin Defect

06/08/2015 3:09 AM

PLEASE tell us the History

5 years we waited!

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: