Transformer Size Selection

05/16/2011 3:31 PM

I make my calculation for STP plant . During my load calculation stage , I calculated total connected load of depart was 1750KW, 380V (estimated 2150KVA @ 0.8pf). the transformer calculated according to connected load.

Now when all the motors are in operation, I checked that the running load never exceed 525KW (estimated 650KVA @ 0.8pf). Now i have added service factor of 25% on it and i selected the size of transformer as 650x1.25 = 800kVA say 1000 kVA .It means our transformer is 3 times > max connected load demand . If we talk about starting current of big motors then all the big motors of 45kW are connected with DOL. So in this case can any one help me that the size selected as 1000kVA is correct or not . Please give me technical answers for the mention subject.

My question is that what should be the best practice/rule of thumb during selection of transformer in such cases?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Transformer Size Selection

05/16/2011 4:53 PM

Déjà vu?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Transformer Size Selection

05/16/2011 7:12 PM

Next time, do it the same way.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3

Re: Transformer Size Selection

05/16/2011 9:40 PM

samsam_sam45:

You forgot one most important thing and I will tell you right now. After consideration of various things you described in the OP. Checking of motor starting against the voltage drop is neccesary. Requirement of voltage drop says it shall less than 10 percent during motor starting and less than 5 percent during normal operation.

If the requirement is met. Thing would be Ok.

__________________
Anything that can go wrong, will go wrong
Register to Reply
2
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: Transformer Size Selection

05/16/2011 10:48 PM

if your largest motor is 45kW . . .

do you have only one such motor? and if you have more than one then will all 45kW motors (or all large motors) ever start simultaneously? even if they do will they have loads with a high starting time? chances are that they wont. your calculation method is correct. keep doing what you are doing and sleep safe.

next time you can select a smaller transformer IF you have enough data to correctly estimate your ACTUAL TOTAL RUNNING LOAD (MD) and add to it the DOL starting current of your largest motor (or motors if they are expected to start simultaneously).

Register to Reply Good Answer (Score 2)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5

Re: Transformer Size Selection

05/16/2011 11:49 PM

The basic loading factor for design purpose is continuous loading at rated KVA.

The transformer loading depends on design,temperature rise at rated load , cooling medium , duration of over loading, load factor, ambient temperature and so many other factors. The transformers are designed to withstand over load for limited period however it should not any time cross 200 percent rated KVA. In case of motor load the starting current of the motor and shot circuit rating of the transformer to be used have a specific relation to calculate the actual kVA rating of the transformer to be designed. You can get a practical knowledge about the actual calculation from the link below.

http://www.powerqualityanddrives.com/short_circuit_transformer/

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Transformer Size Selection

05/17/2011 10:04 AM

Good thing that you posted it now! Very recently, I had reviewed the transformer sizing of one of my clients (a water treatment EPC Organisation) - similar to your query. The calculation is too large to post here. If you can send me your mail ID thro this forum's mailbox, I will send you the same.

Register to Reply
Associate

Join Date: May 2011
Posts: 38
#7
In reply to #6

Re: Transformer Size Selection

05/17/2011 10:22 AM

Dear Friend ,can u send me the information which u have ask to send me in your comment ,my email id is amalik.electrical@gmail.com

Thanks

Sam

Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#8
In reply to #6

Re: Transformer Size Selection

05/17/2011 10:30 AM

electricalexpert65: Could you drop it to my id? I also want to have a look at it.

__________________
Anything that can go wrong, will go wrong
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #8

Re: Transformer Size Selection

05/17/2011 10:38 AM

What is your mail ID?

Register to Reply Score 1 for Off Topic
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#10
In reply to #9

Re: Transformer Size Selection

05/17/2011 10:42 AM

Hey, I have sent you for the training package. Could you please check your inbox?

__________________
Anything that can go wrong, will go wrong
Register to Reply Score 1 for Off Topic
Associate

Join Date: May 2011
Posts: 38
#11
In reply to #10

Re: Transformer Size Selection

05/17/2011 11:01 AM

dear friend ,

I didnt receive your training package could you please send me through your personal email please find my personal email : amalik.electrical@gmail.com

Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#13
In reply to #11

Re: Transformer Size Selection

05/17/2011 11:09 AM

samsam_sam45: Sorry making you confused. I did not send you any training package. I said to EE65 only.

Please read the CR4 Code of conduct at here: http://cr4.globalspec.com/faq/cr4rules

Don't publicly put personal email address otherwise your post will be removed.

__________________
Anything that can go wrong, will go wrong
Register to Reply Off Topic (Score 5)
Associate

Join Date: May 2011
Posts: 38
#12
In reply to #10

Re: Transformer Size Selection

05/17/2011 11:07 AM

can you send me the training package Mr.Hein my email id :

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#16
In reply to #10

Re: Transformer Size Selection

05/17/2011 12:27 PM

Pl. wait till tommorrow evening.

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: May 2011
Posts: 21
#18
In reply to #16

Re: Transformer Size Selection

10/11/2011 4:37 AM

dear electrical expertise,

as i m new to this forum, i need transformer sizing calculation model as u mentioned in the previous post. Please post it in my id. I wil be very thankful to you.

Register to Reply
Associate

Join Date: May 2011
Posts: 38
#20
In reply to #9

Re: Transformer Size Selection

10/12/2011 2:27 PM

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Associate

Join Date: May 2011
Posts: 38
#14
In reply to #6

Re: Transformer Size Selection

05/17/2011 11:52 AM

electricalexpert65:PLEASE SEND ME THE INFORMATION WHICH YOU ASK ME TO SEND MY ID :

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#15
In reply to #14

Re: Transformer Size Selection

05/17/2011 12:26 PM

Pl. wait till tommorrow evening.

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: May 2011
Posts: 21
#21
In reply to #15

Re: Transformer Size Selection

10/19/2011 9:20 AM

Dear Electrical expertise,

I need the following clarifications,

1. I have done 3 times transfomer sizing for various projects for various clients. During that sizing i have done bus bar sizing calculation also. Now my new client is asking to submit voltage regulation calculation along with Transformer sizing calculation. As per the bid stage we had selected 5MVA,34.5/4.16kV, ONAN,Dyn5 with 7% of voltage impedance. My major loads are as follows,

1. One LV transformer (3MVA, 4.16/0.480kV, ONAN, Dyn5 with 6.5of %Z)

2. Two motors of rating 1050kw and 910kw, respectively.

I have done transformer sizing and busbar sizng of switchgear which is connected to this transformer. Now i want to calculate Voltage regulation for this Transformer.

Can you explain in detail to find regulation. I will be very thankful.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#17
In reply to #14

Re: Transformer Size Selection

05/17/2011 10:52 PM

samsam_sam45

If you click on your forum ID (as above, or anywhere in CR4 it appears) it will take you to your 'profile page'.

At the head you will find;

"Check Your Mailbox"

There is also a link on the right and column of every thread page under "Logged In"

To send a message to a member: Click on their ID, go to their profile, at the top right is "send a message" which links through your CR4 mail box, to theirs.

If you have received mail, it will show up here

as a box above "updated discussions" - which when clicked - takes you to your box.

Use this system - rather than posing you email address - (which no member will reply to)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Associate

Join Date: May 2011
Posts: 38
#19
In reply to #6

Re: Transformer Size Selection

10/12/2011 2:23 PM

dear electrical expert kindly please find my email id :

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply
Register to Reply 21 comments