we all know that for velocity, the equation is:
v = Sq. rt of (2gh).
but i came across a calculation where there is density used in the denominator, thus making the equation:
v = Sq. rt of ((2gh)/ density)
i don't understand why density is used in the equation. The calculation is for findin the velocity of flue gas in duct. the value of h is given mm WC.
help in this regard most appreciated. thank u all..
Varun Passi
Pathfinder Tags: duct velocity flue gas velocity
Re: fue gas velocity in duct
05/25/2011 1:45 AM
Volume flow would not account for the density; mass flow would account for it.
Good Answers: 67
05/25/2011 3:13 AM
The eqetions you have referred is generally used for liquid.
v = Sq. rt of ((2gh)/ density) is a general equetion for any liquid, but when used for water density = 1.
Good Answers: 137
05/25/2011 6:51 AM
There's some confusion here.
Firstly, what do you mean by h? The formula applies when h is a head difference across some element, and usually v is lower than Sq. rt of (2gh) as the coefficient of discharge is < 1. E.g. for an orifice plate under most conditions CD = 0.62.
If h is in m fluid, v is in m/s. If you want the mass velocity kg/(m2*s) you need to multiply v by the density, not divide.
But you're dealing with gas flow, and you wouldn't (normally) have pressure drop in m fluid. It would be in pressure units, Pa (= N/m2). In that case the formula is
v (m/s) = CD*√(2*ΔP/ρ) where ρ = density kg/m3 about 1.2 for air.
or mass velocity vm (kg/(m2*s)) = CD*√(2*ΔP*ρ)
Cheers........Codey