TPN+E

05/25/2011 2:55 PM

We have in a project this kind of system, is this system can be called TNS as per IEC? Does the 4P circuit breaker is suitable in this kind of installation does the application of 4P CB is on the mains CB only of secondary of xformer?

I hope the gurus in this forum can shed light on this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: TPN+E

05/25/2011 3:55 PM

Yes it can be a TN-S system. If a 4 pole breaker is used the neutral should be late break. All systems I have worked on used 3 pole breakers with removable neutral links.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: TPN+E

05/26/2011 7:44 AM

In a TN-S System, the Source Neutral is earthed solidly at the source. And, the equipment earthing is thro this earthed neutral of the source. But, there are seperate conductors emanating from the earthed source neutral for distributing the neutral and for the protective conductor. So, in a three phase system, you will have L1, L2, L3, N & PE - totally five conductors or wires running thro the distribution system. The neutral may or may not be broken; in single source systems, it is not broken to save cost on a fourthe pole of the switchgear. But, in multiple source systems, it is prudent practice to go for neutral breaking - with a 4 Pole Switchgear.

But, note that in a TN-C system, you MUST NOT break the neutral.

Register to Reply
Associate

Join Date: Feb 2011
Posts: 40
#3
In reply to #2

Re: TPN+E

05/26/2011 3:03 PM

Sir

We have a low voltage switchgear with a 4P main for normal and 4P main for emergency and tie breaker of 4P the scheme is a double ended substation so the neutral of secondary of xformer will go to the 4th pole and at the same time it is solidly grounded. My question is can we apply REF (Restricted Earth Fault Relay) or ordinary ground fault protection on the 4P breaker?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: TPN+E

05/26/2011 9:04 PM

I can understand the Scheme as it is more common. The choice of either REF or BEF or both is not influenced by the arrangement in your case. YOu can have either or both. REF is mandatory if the TRF. is more than 1 MVA capacity.

Register to Reply
Associate

Join Date: Feb 2011
Posts: 40
#5

Re: TPN+E

05/27/2011 9:48 AM

electricalexperts65

thank u sir for the prompt reply. More power and godbless.

Register to Reply