Feasibility of Absorption Chiller

05/26/2011 8:12 AM

Our plant is using steam for 'steam autoclaves' and 'hydraulic moulding press'.A boiler of capacity 3TON is employed for this.Steam is maintained at a pressure 7 kg/cm2. Machines doesnt use steam continously.It is released to surroundings after use.Is it possible to install a absorption chiller using this steam and of what capacity?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Feasibility of Absorption Chiller

05/26/2011 8:48 AM

Yes it is. To do what, though?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Apr 2011
Location: Located in INDIA.Kerala state,kottayam Dt,pala.
Posts: 42
#2

Re: Feasibility of Absorption Chiller

05/26/2011 11:51 AM

It is advisable.Seacrch in google for steam jet refrigerator.

__________________
Lalithambika
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3
In reply to #2

Re: Feasibility of Absorption Chiller

05/26/2011 1:02 PM

Absorption chiller may be more feasible, because it requires heat, not more pressure like steam jet refrgn.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#4

Re: Feasibility of Absorption Chiller

05/27/2011 2:14 AM

Yes you can use absorption chillers. Commercial Lithium Bromide absorption chillers are available in the market. Sanyo is one of the manufacturers. Vapor absorption systems are recommended for cooling when waste heat is available freely or at lower price.

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 11
#5

Re: Feasibility of Absorption Chiller

05/28/2011 3:28 AM

Thank you all for your extended support.

I have seen articles about using waste heat of power generators to run absorption chillers...But I didn't get how the waste heat is used...How this heat can be used as the input to an absorption chiller.Our plant is using a generator of capacity 550KVA,Diesel Type,400KW...Is this generator enough to run a absorption chiller??And can we use the waste heat of this generator and early mentioned boiler steam for the same absorption chiller??Please mention capacity of chiller that can be used...

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#6
In reply to #5

Re: Feasibility of Absorption Chiller

05/30/2011 3:15 AM

Using waste heat from diesel generator for absorption chiller is not economical because it is too small. Steam can be used and capacity of chiller will depend on quantity of steam available for it. The best way for you is to contact some absorption chiller suppliers.

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 11
#7
In reply to #6

Re: Feasibility of Absorption Chiller

05/30/2011 5:02 AM

Thank You Pritam

Register to Reply