Differential Protection Of Transformer

05/28/2011 6:29 AM

For YNyn0 transformer differential protection may be done by delta-delta/ star-star connected CTs. In general star-star CT connection is done. Is it 100% correct and why delta-delta connections are not done?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#1

Re: Differential Protection of transformer

05/28/2011 6:55 AM

Could you show me the star-star CT connection scheme for this transformer protection?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#6
In reply to #1

Re: Differential Protection of transformer

05/29/2011 10:09 AM

What phase shift are you talking about??

Ynyn0 transformer connection does NOT have a phase shift.

Register to Reply
2
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#2

Re: Differential Protection Of Transformer

05/28/2011 9:03 AM

The star/star CT connections are used in newer solidstate relays because they automatically correct for the phase shift of the transformer once you program the specific style.

The older electro-mechanical did not have this feature so the phase shift was corrected by wiring one set of the CT's in Delta configuration.

Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3
In reply to #2

Re: Differential Protection Of Transformer

05/28/2011 10:51 AM

As far as I know, the CT configuration depends on the transformer configuration.

__________________
Anything that can go wrong, will go wrong
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jul 2010
Posts: 11
#4

Re: Differential Protection Of Transformer

05/29/2011 4:21 AM

Numerical Relays can compensate for the phase angle difference by the setting and does not require CT secondary circuit arrangement such as delta-connection on the star-connected side of the power transformer which was common for the former transformer protection.

Setting for phase angle matching

The phase angle differences between line currents on each side of the power transformer are corrected by setting according to the hands of a clock as follows:
Rule 1:
If all the windings are star-connected, then take one of the windings as a reference winding and set 1 (= one o'clock) for it. For other winding(s), set the phase angle difference from the reference winding by the expression of the leading angle. One hour corresponds to leading by thirty degrees.

Register to Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#5

Re: Differential Protection Of Transformer

05/29/2011 8:55 AM

For YNyn0 transformer,i.e.,an autotransformer there will always be a Tertiary winding in delta formation to suppress the flow of zero sequence current due earth fault on secondary side( down - stream) from flowing to the up-stream side.[p]

Therefore to eliminate the differential protection from maloperation during through fault condition ( earth fault ), it becomes necessary to eliminate the zero sequence current from comparison.This is achieved by connecting the CT secondaries by delta connection[p]

As commented by experts previously, this has to be done manually for Electro mechanical and static relays, whereas the same can be carried out by suitably selecting the menu in numerical relays.[p]

Any way the selection of Delta is mandatory requirement for transformers of YNyn0 vector group with tertiary winding with delta connection.

__________________
There is nothing either good or bad, only thinking make it so -
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

ekiechle (1); Energy Conservation (1); hien.nguyenquoc (2); olehwi (1); Panneer Selvam (1)