Bus Bar

05/29/2011 1:29 AM

how to calculate bus bar voltage drop calculation in genral.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Bus bar

05/29/2011 1:50 AM

This has to be a homework or take home exam question. I hope all of these lazy bums fail their class.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: Bus bar

05/29/2011 2:02 AM

E = IR (for DC or single phase). I think it is E = √3IR/2 for 3-phase, but I haven't done this for a while. For bus bars of short length, R is almost zero, so I am surprised that anyone bothers to calculate it (as opposed to long conductors with small cross-section).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#3

Re: Bus bar

05/29/2011 2:44 AM

Voltage drop at bus bars are neglegible because it is the point wherein close to supplied loads. What you need to calculate is the feeder cables from the power source where your MDB busbars is getting its power. Allowable Voltage drop from point "0" or power source to the farthest circuits not in the MDB or busbar point but to the farthest supplied circuits- shall not be more than 5% of supply voltage.

Voltage drop formula:(English system)

Vd = (2xKx I x L)/CM - SINGLE PHASE 2 or 3wire

Vd = (1.732 x K x I x L)/CM - three phase

where:

K = resistivity of cable per 1000feet, value changes with temperature and size of cable.

L= Length of cable/conductor in feet

CM = Circular mil area of the conductor

I = Load current in amperes

__________________
If there is a will... there is a way... No pain / No gain.