Anonymous Poster #1

Power Loss In A Relay

05/29/2011 3:32 AM

hi everyone ,

i was asked by a client to calculate the power loss in a relay (4 c/o). the rated thermal current of that relay is 6A, voltage being 240v AC. the power consumption of the relay coil was 1.2 VA. so how to calculate the loss in the relay. is it by this way.

the total power = 240x6 =1440 VA. therefore the loss =1440VA-1.2VA=1439 VA.

i am not sure about this calculation. can you guys help me out.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#1

Re: power loss in a relay

05/29/2011 4:28 AM

It is even not clear which losses the client meant - the ones lost by load in the contacts (probbaly, mostly heat), or the ones lost by the relay construction (heat, stray currents, sound). The both are negligeable - only worth consideration if there were thousands of the relays, and anyway, little can be done here.

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: power loss in a relay

05/29/2011 4:50 AM

Your wrong but the answers in the information you gave.

Think about what's using power in the relay

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #1
#4
In reply to #2

Re: power loss in a relay

05/29/2011 5:33 AM

so you are saying the consumption of the relay coil is the power loss?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #4

Re: power loss in a relay

02/14/2023 7:01 AM

Well, what other ones are there?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: power loss in a relay

05/29/2011 5:30 AM

The power loss in such a relay would be :

1. Loss in the coil - 1.2VA

2. Thermal loss in the contact system - I²*(4*R) where R = Ohmic value of each current-carrying path of the relay. (Generally this will be in milliohms.)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#5
In reply to #3

Re: power loss in a relay

05/29/2011 5:44 AM

The ralay does the useful work of the connection of the load to the supply. The losses in it is just a fraction of the power consumed by it.

I overlooked the "rated thermal current" in the OP. At less load the 6A rated thermal elements will produce less heat, at more load, more heat. So in them losses will depend on load (in the coil do not depend).

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: power loss in a relay

05/29/2011 6:09 AM

It is not desirable to operate the relay at any current higher than what the manufacturer specifies. The thermal current is usually the highest of the rated values, the rated operational current under different duties are less. The user must never exceed these ratings when using the relay. So, the question of higher currents should not arise in usage.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #5

Re: power loss in a relay

05/29/2011 9:19 AM

What thermal elements?

It's a NO / NC relay, not an O/L or MCB. The only heat from the current will be via the volt drop across the contacts and other internal bits.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10
In reply to #9

Re: power loss in a relay

05/29/2011 9:44 AM

Quite right you are Tony. But in the bigger picture of energy conservation, it is the duty of designers to keep the perpetual loss low. Every bit counts.

Here is what ABB declares for their 6A control relay...

Negligible maybe, still, shows that they are trying....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#7

Re: power loss in a relay

05/29/2011 7:46 AM

Sorry but I don't think that there would be a customer who requests his vendor to calculate this for him. Just in case this customer is the other student.

Do you know what is called power loss? That power is not useful while you are calculating the power consumption. Which?

__________________
Anything that can go wrong, will go wrong
Reply Off Topic (Score 4)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: power loss in a relay

05/29/2011 8:55 AM

In these days of energy conservation initiatives, it is quite normal for customers to ask, and manufacturers to provide power-loss-per-pole figures for most equipment. Here is one example of an electronic relay from ABB

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Active Contributor

Join Date: Feb 2010
Posts: 16
Good Answers: 2
#11
In reply to #8

Re: power loss in a relay

05/29/2011 9:59 AM

KVS - Interesting! I have "learnt" something today.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #11

Re: power loss in a relay

05/29/2011 10:24 AM

Thank you, you made my day

However, this table refers to an electronic motor-protection relay. The OP really was referring to a "control relay", a 2NO+2NC small contactor ... the wattage wasted there in the current path is naturally much lower, please see post # 10.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#14
In reply to #8

Re: power loss in a relay

05/30/2011 9:10 AM

Thanks kvsridhar for this excellent information in regard to power consumption of the relay. In fact, in today's world, everyone is trying to save energy whether small or large quantum; for example,like relays ,engineers prefer low power consumption HRC fuses,choice of LED indication lamps instead of filament indication lamps etc. in panel building works.

__________________
Manindra
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13

Re: Power Loss In A Relay

05/29/2011 7:17 PM

As was said in the beginning, you must first determine the intent of the question.

If all they want to know is the power losses as a result of the coil being energized, most relay mfrs will state that in their data sheets, usually referred to as the "Sealed" VA or W consumption. Basically because of the nature of a relay, all of the sealed power is going to be rejected as heat, so you could say it is 100% losses.

If they want to know the total aggregate power loss, as in watts for determining heat rejection, then you would add the relay power consumption and the resistance losses of the contacts.

If they want to know the losses inserted into the circuit flowing THROUGH the relay contacts, sometimes called "insertion losses", for the purposes of determining true power consumption at a load down stream, that's a different matter and a little more complex.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); hien.nguyenquoc (1); JRaef (1); JSCadman (1); kvsridhar (5); manindra (1); PWSlack (1); TonyS (2); Yuri B. (2)