Current Liminting MCCB Coordination

06/01/2011 9:00 PM

I have read that a current limiting fuse can achieve coordination by selecting 2:1 ratio of its ampere from upstream to downstream.

What if we use current limiting MCCB? Can we achieve coordination too?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Current Liminting MCCB Coordination

06/01/2011 10:47 PM

Yes, one manufacturer claims discrimination with a 2.5:1 ratio. Another company claims 1.6:1 ! Apparently even better than fuses.

ECT201

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2
In reply to #1

Re: Current Liminting MCCB Coordination

06/01/2011 11:12 PM

Instead of depending on manufacturers the authorities(BS/IEC/NEC/IEEE/VDE/NEMA etc) should lay down standards to be complied with.

__________________
pnaban
Register to Reply
3
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Current Liminting MCCB Coordination

06/01/2011 11:24 PM

i have always felt that the standards (IEC in my case) specify the minimum level that an equipment must satisfactorily achieve. The designer must strive to do better than that. So, in this case, if i was a system designer, i would choose the newer MCCB which gives me a better ratio (1.6:1) thereby further reducing the stress on my system, and is also a more economical solution perhaps.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #3

Re: Current Liminting MCCB Coordination

06/02/2011 5:40 AM

For fuses we consider pre-arcing I^2t values.For CBs tripping characteristics of both drawn in the same graph paper will be useful.

__________________
pnaban
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Current Liminting MCCB Coordination

06/02/2011 6:57 AM

All good manufacturers of current-limiting MCCBs give this data in two ways:

1. As discrimination and cascading tables with the larger MCCB and smaller MCCB, etc.

2. Also as curves on log-log graph.

However, at the maximum short-circuit level, both will open under contact repulsion, though only the downstream one will trip and clear the fault. The upstream one may open momentarily, and reclose. This momentary opening actually helps in restricting the let-thru energy.

Yes, but when the contacts reclose in that upstream MCCB, the tips are in molten state. The company's expert assured me that they will not weld. i hope so

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Current Liminting MCCB Coordination

06/02/2011 3:53 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Current Liminting MCCB Coordination

06/02/2011 5:28 AM

i am intrigued. i would have thought that discrimination is not something that can be specified in a standard, since a cost-conscious user may choose cascading for example. Do you mean BS7671 really specifies this ? It would be very interesting to learn, for me as well as many others on CR4. May i request you to spare a little of your time and tell us more on this ? Thank you.

i would hasten to assure you that i am sincerely in the quest for knowledge, and that this is not a "Oh yeah? Prove it to me!" post. i have tremendous respect for you.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Current Liminting MCCB Coordination

06/02/2011 7:11 AM

The application of BS7671 can answer a great many postings in this forum.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Current Liminting MCCB Coordination

06/02/2011 8:46 AM

Of course. i found this article from Eaton MEM on BS7671 and discrimination.

http://edmundson-electrical.voltilink.co.uk/news/3544/cm/guide-to-discrimination.html

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#10

Re: Current Liminting MCCB Coordination

06/03/2011 5:05 AM

To all,

Thanks for the information that you have shared.

It helps me a lot in my design.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#11
In reply to #10

Re: Current Liminting MCCB Coordination

06/03/2011 6:49 AM

Here are attached the time-current characteristics of various fuses and circuit breakers.
May this will help you.

__________________
Sure Answers Always
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jonald (1); kvsridhar (5); pnaban (2); PWSlack (2); Vinu_Answers (1)