I dont know how to connect two dg in parllel.What and all things to be considered,any interlocking will be provide with formula i can implement in real time project for an hospital...
When a constant load is to be supplied with electrical power, a single generating unit may be installed to provide the energy, its capacity being just large enough to take care of the load, since it operates at highest efficiency fully loaded. On the other hand, when the load varies greatly from one part of the day to another, it would be uneconomical to supply power from a single unit because it would be operating considerably below full load, and therefore at a low efficiency, for much of the time. Under such circumstances it is usual to provide two or more units of such capacities as will allow of their operation at as nearly full-load conditions as possible at all times. When two or more generators are furnishing power to a common load, they are said to be operating in parallel.
The two generators can be synchronized when the following conditions are set:
1. The phase rotation of both generator systems must be the same. Check
this with a phase rotation meter to determine
ABC or ACB rotation.
2. The AC voltages of both generators should be equal. In practice the
voltage of the generator required to be parallel is usually have 1-2 volts higher than that
of the operating generator.
3. The frequencies of the both generators must be equal.
In practice the frequency of the generator required to be parallel is usually have 1-2 Hzs higher than that
of the operating generator.This can be observed by using a synchroscope. By adjusting the RPM of the generator, frequency can be adjusted.
The speed (frequency) and output voltage of the incoming generator is kept slightly higher
to prevent it from becoming a load to the system when it is connected.
A synchroscope is a device that indicates the degree to which two generators are synchronized with each other. If the generator is turning at a lower frequency than the grid, the
synchroscope needle rotates continually in the direction (usually
counterclockwise) marked "slow" or "lag" on the dial to indicate that
the generator is running slower than, or lagging behind, the grid. If
the generator is running faster than the grid, the needle rotates
continually in the opposite direction, marked "fast" or "lead". As the frequency of the generator nears that of the grid, the
synchroscope needle slows down and when the frequencies match, the
needle stops rotating.
if you do not know how to do, don't do, learn first.
This is not a kind of project where we can be involved without knowledge, even with all the good wills of the posters trying to help.
I can figure that a DG is the prime source of power for this hospital. any false step will be disastrous on the equipments and the working personal, and the hospital will be devoid of its vital source of energy for a long time compromising many human lives .