06/05/2011 2:09 PM
how can i calculate the rating of CT/VT rating in a circuit?can you send it to me the link or the formula how to calculate it.
thank you in advance
Re: CT/VT Calculation
06/05/2011 11:01 PM
First you should measure the burden (if you cannot calculate accurately) including the leads.
pnaban
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member
06/06/2011 5:30 AM
First Of all, you have to decide the purpose of the CT/ VT. Whether you may use it for measuring or protection purpose.
Measuring CT:
Measuring current transformers are normally class 0.5 or 1 for general use. Class 0.1 or 0.2 for precision and tariff measurements.
Protection CT:
Protection current transformers provide signals to protective relays to enable correct operation under steady state and transient conditions.
For More Information, Visit
http://myelectrical.com/wiki/ct-dimensioning/revision/7.aspx
http://cr4.globalspec.com/comment/733931
Vinu_Answers Sure_Answers
Sure Answers Always
02/08/2013 5:53 AM
One of the above links has changed to:
http://myelectrical.com/notes/entryid/99/how-to-size-current-transformers
For anyone who is still looking for current transformer sizing information.
Good Answers: 170
06/06/2011 8:17 AM
Ratio, Accuracy Class, Burden, Insulation Level, Type, No. of Cores, etc. need to be finalised first.