HVAC Sizing

06/05/2011 6:57 PM

I have a "difference of opinion" with an hvac contractor's engineer on the size of the equipment to be installed in a 4800 sf house, 2 story, 2 hvac systems (16 SEER and 95AFUE) with all metal ducts in the conditioned space through dedicated truss chases. Location is in Dallas, TX, design temps at 70/75 indoor and 22/100 outdoor, and expected 1ACH50. All areas and volumes were correct.
The Building Analysis from the Manual J is:
1st floor: HL 35,327 Btuh and CL 17,636 Btuh. 2nd floor: HL 22,873 Btuh and CL 18,688 Btuh
The Project Summary calls for:
1st floor: HL 35,367 Btuh and CL 20,050 Btuh calling for 2.2 ton @ 70 SHR.
2nd floor: HL 22,873 Btuh and CL 21,726 Btuh, calling for 2.3 ton @ 70 SHR
1. Can you please tell me what size of equipment I should install in each floor?
2. Should the SHR be 70 in residential high efficient equipment? Maybe 85-90?
3. Should the multiplier be different than 1? as in 1.05, 1.1 etc, etc.

I don't want to give our ideas, so not to influence any response.
Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: HVAC Sizing

06/05/2011 7:06 PM

Welcome to AcronymLand!

Are the "dedicated truss chases" actually within the "conditioned spaces"? Is Dallas design dry bulb really only 100°F? Etc.?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#2
In reply to #1

Re: HVAC Sizing

06/05/2011 7:11 PM

Yes, all hvac equipment and ducts are in the conditioned space; ducts are all metal and insulated w/ R6. Design temps are correct.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: HVAC Sizing

06/05/2011 7:32 PM

That's weird; more usually the equipment and ductwork are not in the conditioned space. I found a source that agrees with your design temperatures, so that is no longer an issue.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#4
In reply to #3

Re: HVAC Sizing

06/05/2011 7:37 PM

This is a high level green building house, where all equipment is in the conditioned space. We are expecting to certify this house under 4 major green building programs at the Gold level. I've been doing this for a long time, and surprisingly, HVAC contractors are the hardest folks to bring on board with new technology...

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: HVAC Sizing

06/05/2011 10:23 PM

Well, I hope the condenser doesn't exhaust into the conditioned space....

I don't know what you are talking about, and I don't think you do, either.

The terms "high level green" and "Gold level" sound like marketing hype.

HVAC folks might get on board better if the "new technology" (whatever it is) is actually explained. Please proceed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#6
In reply to #5

Re: HVAC Sizing

06/05/2011 11:50 PM
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #6

Re: HVAC Sizing

06/06/2011 12:08 AM

Those are actually intriguing, even if some of the leakage assumptions seem overly pessimistic.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#7
In reply to #5

Re: HVAC Sizing

06/06/2011 12:01 AM

Tornado,

Well, this discussion is getting off track, but, I did not try to be arrogant in any way with my comment about high level green building or gold level, I was just making the point that today in most of the USA, green building is becoming the way to build, to the point that all this new ways are in the 2009 IRC, 2009 IECC and its becoming more stringent in the future codes. Green building is not a marketing hype but the only way to build homes in the near future if not now, as today many states and cities are regulating them.

You can find all the information you want on high performing buildings on the web, here are some you can start with:

1. http://www.buildingscience.com/documents/information-sheets/information-sheet-ducts-in-conditioned-space

2. http://resourcecenter.pnl.gov/cocoon/morf/ResourceCenter/article/1404

3. http://www.easytitle24.com/do.php?page=faq/detail&fid=1106

4. http://www.energy.wsu.edu/documents/AHT_ACEEE%20Ducts%20inside%5B1%5D.pdf

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#23
In reply to #5

Re: HVAC Sizing

06/07/2011 7:28 AM

The compressor (condenser) is of course exterior (unconditioned) I believe he is referring to the air handler, which of course should be in conditioned space, along with all ductwork.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: HVAC Sizing

06/06/2011 8:18 AM

If all the information is available at the sites you list why are you asking here?

If you have the information try reading it and make your own conclusions.

As for not wanting to influence any discussion, I think several people will be able to discuss the subject fully for a price.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Aug 2009
Location: Phoenix Arizona
Posts: 92
Good Answers: 1
#10

Re: HVAC Sizing

06/06/2011 10:26 PM

Well I can tell you standard rule of thumb, 1 ton for every 450 squre feet to be cooled.

Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#12
In reply to #10

Re: HVAC Sizing

06/06/2011 11:11 PM

There is no such a thing as a rule of thumb in AC sizing any more. By code, Manuals J,S,D & T need to be performed. The issue is whether you add more fluff than the 20% built-in the MJ, like must contractors use to upsize the equipment.

Most high performing houses are using 1 ton per 1,000 to 1,500 sq ft. A lot of the Passivhaus guidelines use even less. Read some of the links I gave before, it explains the process.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 15
#11

Re: HVAC Sizing

06/06/2011 10:59 PM

Who did the load calcs./ What was the sensible and latent load for each story?

You should use the actual sensible and latent loads to select the equipment,comparing to the detailed cooling capacities of the equipment ,rather then assuming a SHR,check the actual capacities of the equipment.

Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#14
In reply to #11

Re: HVAC Sizing

06/06/2011 11:32 PM

In my question you can tell the sensible and latent loads for each story. I also give you what the MJ calls for tonnage; it's not a guess. The SHR is not assumed, it's there written in B&W. No rule of thumbs, no guessing, no equipment outside of the conditioned space, 1ACH50 house, 2009+ Code house.

I just happen to have a difference of opinion on how to use the information from the manual J, and the size of the equipment the HVAC contractor wants to install.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 15
#16
In reply to #14

Re: HVAC Sizing

06/06/2011 11:52 PM

Thee actual Man J loads have a sensible and latent requirement for the home.

All I saw was at total with a SHR of 70%,which would be assumed,if you used an ANSI approved method ,you could answer the question,unless I'm missing something in this thread.

PS , your tone is not acceptable for someone seeking help/advice,for what it's worth! I'm new to this site but if that's the norm,I'm out of here.

Register to Reply
Commentator

Join Date: Dec 2010
Posts: 82
Good Answers: 3
#13

Re: HVAC Sizing

06/06/2011 11:24 PM

I received several differing size quotes for a replacement furnace so I did my own heat study to confirm.

See HVAC-Calc at

http://www.hvaccomputer.com/index.asp

Norm

Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#15
In reply to #13

Re: HVAC Sizing

06/06/2011 11:37 PM

Thanks Norm, I have the same program and my cooling loads are very close, but my heating loads are about 60%-70% of theirs. However, the minimum 96%AFUE furnace I can get is the same for both figures, which is a 37,000 Btuh furnace.... It's a shame that the Heating equipment has not caught up with new technology.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#18
In reply to #15

Re: HVAC Sizing

06/07/2011 12:03 AM

I really don't quite understand this statement. 96% is pretty good, you can get maybe a percent or two more,, but still that's pretty good technology.

Anyway, that being said the rest of the sizing seems about right. I have 3400 sqft, not so hot but much colder and use geothermal heat pump,, that provides 42000Btu/hr heating and 52000btu/hr cooling.,, works just fine

Martin

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 15
#17
In reply to #13

Re: HVAC Sizing

06/06/2011 11:57 PM

HVAC-Cac is very old software ,and not applicable to modern Green Homes, not ANSI approved,but is okay,not great, for older homes.

Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#19
In reply to #17

Re: HVAC Sizing

06/07/2011 12:11 AM

You are correct. It really doesn't deal with today's green homes. I've already made the comments to Don and he said he was working on an upgrade. However, it does help in getting a general idea. The HVAC contractor did his own MJ with Right-Suite (ACCA Approved)

I don't know where you live, but in most of the HVAC contractors around the country grossly upsize equipment, in part because houses are so leaky and part because of knowledge.

See here: http://www.energyvanguard.com/blog-building-science-HERS-BPI/bid/38069/Oversized-AC-Screwed-up-Manual-J-ENERGY-STAR-HVAC-Tirade

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 15
#22
In reply to #19

Re: HVAC Sizing

06/07/2011 1:04 AM

If they actually did it, it's Wright- Suite, I'm in Florida with thousands of load calcs and installs since 1975.

Register to Reply
Active Contributor

Join Date: Feb 2011
Location: GTA Canada
Posts: 15
Good Answers: 2
#20

Re: HVAC Sizing

06/07/2011 12:24 AM

Your cooling loads are both between 1.5 and 2 ton, I do not see where you get the 2.2 and 2.3 ton cooling.

From your summary, I would install a 45,000 btu/h furnace, 2 stage (modulating gas prefered), variable speed fan for the 1st floor matched with a 16 SEER 2 ton cooling system, preferably variable compressor.

The second floor would possibly be the same as I am not sure of a manuacture that makes a smaller gas fired forced air furnace.

Register to Reply
Commentator

Join Date: Dec 2010
Posts: 82
Good Answers: 3
#21
In reply to #20

Re: HVAC Sizing

06/07/2011 12:50 AM

Quote: I am not sure of a manuacture that makes a smaller gas fired forced air furnace.

My furnace is a 40,000 btu by Carrier.

Carrier Infinity 96 is a two stage 96.6% variable speed blower.

Norm

Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#26
In reply to #20

Re: HVAC Sizing

06/07/2011 9:45 AM

Thanks for your input. The 2.2 and 2.3 @ 70SHR is given by the MJ software. We are installing 16 SEERs and 96 AFUE furnaces, variable speed fans for both floors. There are 96 furnaces down to 37,000 Btuh in the market. So far we are all in agreement. Now what we disagree is with their recommendation for the size of units they want to install. They want too much, as usually done in the market, and we want the size called for by the analysis with no up-sizing.

Register to Reply
Guru

Join Date: Dec 2009
Location: Kansas, USA
Posts: 748
Good Answers: 64
#24

Re: HVAC Sizing

06/07/2011 8:22 AM

In responding to the OP; it sounds like you have an opinion that you are very strong in. You're paying the bill, do whatever you want. I have a quote on my whiteboard here in my office and it says, "learn of the skillful; he that teaches himself only, has a fool for a teacher." Benjamin Franklin. You come to CR4 for advice/extra information, then you argue with almost everyone who seeks to provide input.

Green building and all that other stuff is a bunch of marketing hype! It is simply political correctness and sensitivity to the tree huggers run amuck. Finding ways to be more efficient in the stewardship of our natural resources has always been around; calling it "green" nowadays is just fashionable in the environmentalist wachos crowd. An example of this is the high efficiency furnaces/air conditioning, 2- stage compressors/fans, etc. that were developed by people who wanted to make better use of resources and cut down operating costs long before "green this and green that" ever came along. Calling a short 4 legged aninmal with a curly tail and that wallows around in the mud a cow doesn't make it anything different that what it is, a pig.

I'm glad that you want to be as efficient as possible and get the proper equipment for what you are trying to accomplish, but you came here to CR4 for input, so be teachable.

__________________
One of the greatest discoveries a man makes, one of his great surprises, is to find he can do what he was afraid he couldn't do. Ford, Henry
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#30
In reply to #24

Re: HVAC Sizing

06/07/2011 10:29 AM

"Genuine ignorance is... profitable because it is likely to be accompanied by humility, curiosity, and open mindedness; whereas ability to repeat catch-phrases, cant terms, familiar propositions, gives the conceit of learning and coats the mind with varnish waterproof to new ideas" ~John Dewey

I don't waste my time arguing about green building, the fact is whether anyone likes it or not, all building codes are changing to apply all those methods, you may want to learn that as a Bldg Mgr. In few years, there will be no more "green building" but just good building practices, and yes, many people have been doing so without calling it green, and yes, fortunately several groups like Energy Star, USGBC and NAHB are using "green" education and marketing to make us more energy efficient, less wasteful and, hopefully someday, energy independent. (Not a bad thing for our country, isn't?)

I'm new to this website and came in my search for HVAC and/or Mech. Engineers that TRULLY understand the proper way to design HVAC systems. My bad to think that in a Mechanical Engineer blog I would find that. As a Facilities Mgr, you may want to make the time to read the links I gave before, by chance may learn something. By the way, I don't have all answers, but I've been doing this for a long time AND I do teach this stuff, including Architects, Engineers and HVAC folks.

Register to Reply
2
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#33
In reply to #30

Re: HVAC Sizing

06/07/2011 10:47 AM

Thanks for the info. You won't find a more informed and skeptical bunch. John Dewey was on crack, speaking of generalities. General ignorance is almost never accompanied by curiosity and open mindedness. The primary symptom of chronic ignorance is a lack of curiosity. Did he live in a convent?

You must know that most building codes are very difficult to change. Unless you actually build, you are just talking about what should be built. Two very different occupations. The technology of structure efficiency is far ahead of most codes, especially those enforced at the local level. So get off the horse, and get on the pig. It's a little dirty down here.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#25

Re: HVAC Sizing

06/07/2011 8:54 AM

I'm siding with the HVAC contractor.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#27

Re: HVAC Sizing

06/07/2011 10:05 AM

Rule of thumb, 400 sq feet per ton of cooling, match heat rise the same, duct as required for proper flows and balance.

__________________
To be or not to be........ok that's a trick question.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#28
In reply to #27

Re: HVAC Sizing

06/07/2011 10:16 AM

You didn't read the entire thread. The structure is more of a passive design.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#29
In reply to #28

Re: HVAC Sizing

06/07/2011 10:26 AM

Agreed, I jumped the gun. But still stand by the "rule of thumb". If after that you can reduce fenestration losses or gains the adjustment can be made by very simple calculations.

As I am sure you have been doing (based on your posted location) you too have been meeting these requirements for some time here in Cali.

So Work with the Architect, develop the Energy envelope then size accordingly. most of the calculation will be derived from that initial engineering.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#31
In reply to #29

Re: HVAC Sizing

06/07/2011 10:32 AM

Have you read California, Title 24? There is a link up above... you can't do "rule of thumb" in your state anymore.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#32
In reply to #31

Re: HVAC Sizing

06/07/2011 10:40 AM

Yes and have built by ASHRAE title 24 since 2007.

And the rule of thumb still gets you to a starting point and engineer from there.

Square feet, people loads latent heat from energy consuming equipment have not changed that much in the last 30 years. The only relative changes are the envelope that contains that space. Once you confirm those needs you will find that you are close to the rule of thumb.

BTW never design to the minimum required, be sure to add the proverbial 20% somebody might open the door!!!!!

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#34
In reply to #32

Re: HVAC Sizing

06/07/2011 11:04 AM

You're wasting your time on this guy, he already knows everything. He's just seeking validation. His design parameters are to 100F with in interior of 75F. Dallas has a record of 112F and Summer humidity that's always 80+. This design isn't about sizing for everyday of the week. It isn't being sized to account for 40 or 50 people over for a party or wedding. The idea is to provide year round comfort (most of the time) while using the least amount of energy as possible. He's arguing with his HVAC contractor over an amp or 2 draw on a slightly larger piece of equipment. I have no idea who the contractor is but I'm sure he's trying to keep the place cool when it's really under a load. Or has been offline and is trying to cool down the entire space when its 100F or more inside. The current design will run 24 hours a day more than once--count on it.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#35
In reply to #34

Re: HVAC Sizing

06/07/2011 11:17 AM

YEP!!!!

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#36
In reply to #35

Re: HVAC Sizing

06/07/2011 11:39 AM

But to opine when there is little knowledge of the subject, is regretful.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#37
In reply to #36

Re: HVAC Sizing

06/07/2011 12:32 PM

The fact that you keep seeking validation, and have thrown out many sites to go and validate your self at leads me to one conclusion, you are not sure, unclear and have no faith in your own calculations.

For that I must differ you to two previous posts from some of the wise ones that visit this site to help people. Post 9 and 34 please go back and read them they are enlightening.

you have obviously decided to be closed minded to opinions based on experience and knowledge from those that have built many building to the standards of which you speak.

I am sorry for you.

Good Day!!! I said Good DAY!!!!

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Albuquerque, NM & Dallas, TX
Posts: 14
#38
In reply to #37

Re: HVAC Sizing

06/07/2011 1:22 PM

Not, I was actually hoping to have a pier-to-pier conversation on advanced residential mechanical systems in this website and blog. Apparently, most comments are coming from good folks with good intentions but with outdated and empirical information. It's my mistake to assume such and I'm done here.

Thank you.

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#39
In reply to #38

Re: HVAC Sizing

06/07/2011 4:35 PM

I just know that the first thing the gentleman that put on a 3 day seminar on Wright Suite said was that if you use the ACCA design temps you will be getting a lot of calls from angry, hot customers. He said to use your experience and make a good business decision. Do all the name calling you want, but those comments from a teacher who was presented as an expert make me wonder why we are doing all those calculation, just to throw them out and make a good business decision. I also understood that manual J allows for misc additions to the calculation for contingencies. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#40
In reply to #39

Re: HVAC Sizing

06/07/2011 5:15 PM

I think the guy probably has a lot of knowledge on the topic but he really came off wrong. I've seen open ductwork in restaurants and other spaces many times. You have a lot more cubic feet of air to condition but it does provide a certain "look" that many like. Saves on the duct insulation too!

Without seeing the total design it's hard to say how well it would cool when a Dallas heat wave strikes for a week or so with 90+ humidity. He never used the term LEED but I assume that was the "Gold" he refereed to. I've seen more than a few LEED projects, I've never seen one that wasn't incredibly expensive.

I'm a long time HVAC contractor. Like your teacher once told you I make business choices to keep my customers happy. So when a heat wave hits this Dallas home and it's 85F inside the owner can remind himself about all the money he's saving and point to the little Green and Gold seals proudly displayed near the front door.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2011
Posts: 15
#42
In reply to #39

Re: HVAC Sizing

06/07/2011 10:24 PM

In my opinion,having done thousands of new homes ,in Florida,the guy from Wright J is totally off base. Manual J works correctly if used correctly,however equipment selection must be made using Manual S,and the ducts designed using Manual D. Without all three you might as well just guess!!

Interesting opinions and comments on this one.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#41
In reply to #38

Re: HVAC Sizing

06/07/2011 5:20 PM

"Pier-to-pier", what, we're going to stand on wharves and shout at each other?

Comments are coming from people with experience,, no house is ever built exactly as specified, and the blasted weather does not always do as predicted. When there are extremes, and there will be, when your builder or his crew didn't finish something the way it should be,,, that's when that excess capacity comes into play.

A bit too big is way better than marginal.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#43
In reply to #41

Re: HVAC Sizing

06/07/2011 10:45 PM

In general HVAC units should not be oversized. Although I twitted the OP over acronyms, I agree on this, and thought it was fairly well known. Yes, once in a while the 99.4% or 99% or 98% design conditions may be exceeded; but customers should be educated to expect this in return for greater efficiency most of the time, and less original cost.

I don't much favor mandating this by so-called "green" codes, however.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#44
In reply to #43

Re: HVAC Sizing

06/07/2011 10:57 PM

10 years ago I would have wholeheartedly agreed with you. In a world of variable speed scroll compressors, continuously variable circulation fans and powerful microprocessor controls things are different. A system can easily be larger than the 98% condition and still operate with very good efficiency at capacities less than 100%. As for cost, I would submit that it is negligible, when compared to the amount of money being spent on making the structure "green".

Martin

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#45
In reply to #44

Re: HVAC Sizing

06/08/2011 2:07 AM

Agreed. It is interesting to watch shifting codes vs. technologies over the years. It used to be that HVACR designers used a few empirical rules of thumb such as 400 ft2/ton, and then threw in a 20% safety factor for contingencies. But if I recall correctly, there was a California energy provision (mid 1980's?) that limited overdesign factors to 10%.

Then, as better part-load efficiencies came along, by the methods you mention, this could negate the 10% limitation. I'm not in HVAC, and thus may be out of date. The constant "churning" of code provisions is certainly a nuisance, along with "greenwashing" hype. (Although there is some good stuff in there.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#46
In reply to #45

Re: HVAC Sizing

06/08/2011 7:38 PM

You are all very right.

Codes in California efficiency guides have changed, however it is the customer that will sell you short in their explanation of use that usually leads to finger pointing. Case in point, Server room on the fifth floor, small room no windows no real load issues other than equipment again "rule of thumb" it is generally about a ton a rack in server rooms after calculating KW's. The customer told me that the 3 racks in the room were all he was ever going to put in there so 3 ton system 68 degrees easy and in. My gut told me go 5 tons (and I priced it for him but the customer said too much) for growth, but was assured no growth and he had a limited budget.

Two months later......the call.....its hot in here! Arrive at the location the customer managed to get an additional 3 1/2 racks in the room he's running 85 degrees. With the 5 ton system he probably would have been ok but on the edge.

Point is that most of our customers do not look to the Wedding day as Fredski mentioned when you have 25-30 people in your home and thats when the contractor that throws out the 10 - 20 percent is the hero. There are many ways today with technology to reduce operating costs with out sacrificing personal comfort.

Moral.....I guess is Don't be cheap up front, you will blame the contractor later!!!!

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 15
#47
In reply to #46

Re: HVAC Sizing

06/08/2011 8:04 PM

If you add enough tonnage for a wedding party,in a humid climate like Florida,there will be likely be humidity issues,and you won't be the hero. Some oversizing could be negated by the use of two stage systems,but best to size it correctly.

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#48
In reply to #34

Re: HVAC Sizing

06/27/2011 12:38 AM

I agree with Fredski. The contractor is opting to be safe rather than sorry. He is aware that if anything goes wrong - only he stands responsible.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Register to Reply 48 comments

Good Answers:

These comments received enough positive votes to make them "good answers".