Klixon Motor Overtemperature Protection

06/06/2011 12:46 AM

We have had a 300kw 500V DC motor burn out its shunt field winding. The cooling air supply was inadvertently restricted.

The motor was supposedly built to IEC 600434-5 to IP 44 level. I do not have this specification.

I would expect the klixon mounted in the shunt field to open before there was any permanent damage.

Do any of you have access to the specification?

Is it reasonable to expect the klixon to open before permanent damage?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Klixon motor overtemperature protection.

06/06/2011 2:31 AM

Not unreasonable to expect it to work. In a motor of that size I would expect a series connected temperature sensor in each of the stator windings. To be honest for all sensors to fail seems unlikely, I would look to the external controls.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3
In reply to #1

Re: Klixon motor overtemperature protection.

06/06/2011 11:22 AM

The klixon shut the motor down.

There were both Klixon and Thermistors installed in the motor.

The thermistors had not been wired up.

The klixon did shut the motor down, but not before permanent damage. There was one klixon in the top shunt field, one thermistor in the same coil, and one thermistor in the interpole. Armature and pole face and interpole coils are OK. Shunt field is toasted.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Klixon Motor Overtemperature Protection

06/06/2011 10:52 AM

Do you know for sure there even is a Kilxon? It's not automatic. In addition, a "Klixon" is usually a power interrupt device and is wired in series with the field power. It may have had thermistors, which are not in series with the power, they need a thermistor monitoring device outside of the motor in the control system, as TonyS indicated. If you assumed those were Klixons and they were thermistors, that right there might be your problem.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#4
In reply to #2

Re: Klixon Motor Overtemperature Protection

06/06/2011 11:27 AM

It was for sure a Klixon in the shunt field.

The two thermistors had not been wired up.

The klixon was wired into a DC drive that shutdown the system.

I would really like to know the IEC definition of the protection it was to provide.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Klixon Motor Overtemperature Protection

06/06/2011 3:15 PM

IEC 600434-5 does not show up in a Wikipedia list of current IEC standards. You sure of that number?

List of IEC current standards...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#6
In reply to #5

Re: Klixon Motor Overtemperature Protection

06/06/2011 4:11 PM

60034-5 and -11 appear to be the ones of note...expensive to get a read through copy!

http://webstore.iec.ch/webstore/webstore.nsf/mysearchajax?Openform&key=60034&sorting=&start=11&onglet=1

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#7

Re: Klixon Motor Overtemperature Protection

06/07/2011 2:36 AM

Your wright in assuming the Klixon over tempt. device should have tripped before permanent damage is incurred. Have you at any time had time to check the performance of the klixon unit? Just as you never fine time to clean the filters of the cooling air fan, you might have assumed all is well with the klixon temperature unit. The klixon modules are mostly unreliable when exposed to hazardous conditions, particularly in abnormal ambient temperature areas. The room temperature where the driver or control panel is installed is of vital importance to the performance of klixons. More so there is nothing wrong in having a double protection such that the motor can also trip on Over current. Take Care.

__________________
There is peace in silence and achievement in plans.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8
In reply to #7

Re: Klixon Motor Overtemperature Protection

06/07/2011 3:27 AM

Installed for 3 months.

Air inlet at com end, outlet at drive end.

Pole face windings and commutator windings are OK.

Thermo about midway along shunt coil. As you can see the drive end was much hotter than com end, mid coil was somewhere in between. Therefore insulation was damaged at drive end by the time the thermo opened.

Register to Reply