Anonymous Poster #1

Genset Neutral Cable

06/06/2011 9:32 AM

Hi All,

We have rented new genset to supply the temporary office. The electrician connect the nuetral cable from the genset to earth, is this thing is correct?

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Genset nuetral cable

06/06/2011 9:59 AM

The electrician knows the local wiring code.

CR4 doesn't even know the country of installation. Is that correct?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #2
#2

Re: Genset nuetral cable

06/06/2011 3:38 PM

No that is not correct

Reply Off Topic (Score 3)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #2

Re: Genset nuetral cable

06/07/2011 11:41 AM

Really Janus?

Reply Off Topic (Score 5)
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#3

Re: Genset Neutral Cable

06/06/2011 11:18 PM

The neutral carries the unbalanced current [vector sum of Ia+Ib+Ic, of the 3 phases] or the earth fault current. As long as the cable has adequate current carrying capacity for these currents, it is OK.

This neutral current can be limited by including an impedance in the neutral. Primarily this is done to limit short circuit current in case of earth faults.

In the absence of neutral grounding[Infinite impedance in neutral path], there will be no path for earth fault current for this generator. Earth fault current contribution from this generator will be 0. Protection engineers may prefer at least small magnitude earth fault current to isolate the fault.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Genset Neutral Cable

06/07/2011 2:05 AM

Not only neutral but metal frame/body of genset too should be earthed.

__________________
pnaban
Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#5
In reply to #4

Re: Genset Neutral Cable

06/07/2011 2:13 AM

yes.. just in case insulation of the winding fails.

The frame of all electrical equipment needs to be grounded to protect operating personnel

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#6

Re: Genset Neutral Cable

06/07/2011 2:36 AM

The electrician has technical knowledge of earthing systems.

There are many variations in system design and for any particular application, the precise method of energy source earthing is subject to the recommendations of the machine manufacturer, the system parameters and where main supplies are also involved, the agreement of the concerned supply authority.

As per BS-7671, clause no-23.2.2.1 (Generator operating in isolation from mains and other supplies) - Generator neutral point should be connected to an earthing conductor and the independent earth electrode.

Also,

As per Regulation-8.3-b of "The Electricity Safety, Quality and Continuity Regulations 2002", - A generator or distributor shall, in respect of any low voltage network which he owns or operates, ensure that-every supply neutral conductor is connected with earth at the source of voltage or at another point nearer to the source of voltage.

Vinu_Answers Sure_Answers

__________________
Sure Answers Always
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#8

Re: Genset Neutral Cable

06/07/2011 11:42 AM

Yes, that's correct. Where would you propose they connect it? (easy now!)

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cuba_pete (2); pnaban (1); PWSlack (1); raghunath7 (2); Vinu_Answers (1)