Joining Two MSBs

06/08/2011 4:11 AM

Dear Sirs and Mdms,

Event

MSB-01 and MSB-02 are assigned to be joined for one output with considerably high-ampere rating. Cable size assigned is 400 mmsq LSOH/XLPE/FR + 240 mmsq LSOH/FRT CPC.

The cable assigned to be (16*400) phase cables and (1*240) CPC cable. One MSB is N/C condition and another in N/O condition.

Question

The purpose of this connection and concept of power sharing due to connection.

Thank you.

Best Regards,

vi ra

Register to Reply
Pathfinder Tags: Joining two MSBs
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Joining two MSBs

06/08/2011 6:44 AM

Wha....?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Joining two MSBs

06/08/2011 7:48 AM

One of those rare occasions you get the chance to read pure GIBBERISH!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2011
Posts: 21
#3

Re: Joining Two MSBs

06/08/2011 8:36 AM

The purpose of this connection is for redundancy to obtain continuous operation. If one incomer (e.g. MSB-1) is failure the other one will supply power by closing the MSB-2 manually or automatically. There must be interlock between these MSBs to ensure that at a time one of the MSB will be in closed condition.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Joining Two MSBs

06/08/2011 10:31 AM

Are you absolutely sure about that?

The post doesn't make anything clear, if you stick around CR4 you will soon find out how obtuse questions can be.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Oct 2010
Posts: 7
#5
In reply to #3

Re: Joining Two MSBs

06/08/2011 11:02 AM

sure, there is an interlock between them. And I also accept your reason that for redundancy. Thank you so much. now what I want to know is why we have to use 16 cables (16x 400 mmsq XLPE) + (1x250 mmsq) CPC to join these two MSBs.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Joining Two MSBs

06/08/2011 11:34 AM

For the current to pass?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 21
#7
In reply to #5

Re: Joining Two MSBs

06/08/2011 2:21 PM

If you do cable sizing means you will get the solution. I am not clear this 16 runs of 400 sq.mm cable is for both MSB or Individual MSB. that 250 sq.mm cable is for neutral. always neutral cable shall be half of the main cable..

If u want more idea give me the details of load, incoming supply, distance and technical data of the cable..

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Joining Two MSBs

06/08/2011 2:26 PM

"now what I want to know is why we have to use 16 cables (16x 400 mmsq XLPE) + (1x250 mmsq) CPC to join these two MSBs."

So are you unclear as to why they selected that quantity and size of cables? If so, as compared to what?

You must have conductors that are;

  1. rated to carry the current, and
  2. easy enough for installers to handle

If for example you wanted to do it with one or even two conductors per phase, have you given thought as to how big that would be and how difficult it would be for an electrician to handle it?

Bus bar would likely be a better choice, but is not always practical, especially in retrofit situations.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#9

Re: Joining Two MSBs

06/09/2011 6:21 AM

With four 400mmsq per phase looks like you have a design problem, distance, volt drop and cost. Needs an engineer to look at a new substation, a higher volts supply.

First you say the two supplies are joined, and power sharing, is this in parallel? Not a trivial matter if it's coming from two separate transformers.

Then there's talk of a changeover with one taking over from the other, i.e. main supply and a standby which comes in on failure of the main supply, with interlocking.

Register to Reply
Member

Join Date: Oct 2010
Posts: 7
#10
In reply to #9

Re: Joining Two MSBs

06/09/2011 11:01 PM

thank you for your sharing. here is the detail of the two MSBs that is going to join with the circuit numbers 1-15 and 2-17. Both MSBs have same rating with 4000AF/2800AT. and MSB1 has separate transformer.

Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#11

Re: Joining Two MSBs

06/10/2011 1:46 PM

The two incomers are interlocked with the bus-tie breaker, you'll find it's not possible to parallel the two feeders. It's normally two out of three, so one feed can supply both boards or each board runs separately which effectively shares the load.

What are you trying to achieve? If you are overloading on one board you might change the loads around from one MSB to the other.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

engineertony (2); JRaef (1); PWSlack (2); rathakrishnan05 (2); TonyS (2); vi ra (2)