Anonymous Poster #1

Sub Distribution Board Types

06/08/2011 8:14 AM

Hi,

I just need to ask you what is a sub distribution panel board CIRCUIT BREAKER TYPE.

Does it mean that no isolating switch will be provided on the incoming cable feeding the sub distribution board?

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Sub distribution board types

06/08/2011 8:17 AM

It would be rare for an isolation switch of some sort not to be provided on a distribution board. After all, how is one supposed to change a breaker - do it live (rhetorical question)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Sub distribution board types

06/08/2011 8:24 AM

Exactly,

but do you know anything about this type of sub distribution board? I read it in Specs but don't know what they mean by it.

Thanks.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Sub distribution board types

06/08/2011 8:46 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #2

Re: Sub distribution board types

06/08/2011 8:47 AM

Would there not be one incomer device (switch, MCB, etc) in the board which receives the incoming power supply? This then feeds a small busbar system on to which some MCBs may be plugged in. In this case, the incomer device would be the isolator....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: Sub Distribution Board Types

06/08/2011 8:47 AM

It is quite normal in North America to have sub-distribution panel boards to not have a main overcurrent device in them. They are protected by their overcurrent device located on the main distribution panel.

In this case... their should be no neutral to case ground (bond) connection at the sub panel as the neutral to case ground is created at the main panel of the service.

Having a second neutral to case ground point at the second panel introduces a redundant path for fault current back to the source. Such a redundant path, because of impedance differences in the second path relative to the first, can cause a voltage potential to exist between the bonding systems during a fault event.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply