Problem in Stardelta Starting

06/08/2011 12:03 PM

hi friends we have five low stage compressors,having motor 150 kw,stardelta starter having mccb 400 amps,in=400,instantaneous=12in.Now the problem is that when compressors come to star to delta MCCB got triped.Two compressors are running fine form the date of commissioning.Rest three having this problem frequently not regular.Out of these three one is most critical.In this compressor MCCB got burnt two times and we cant find the conclusion yet.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Problem in Stardelta Starting

06/08/2011 2:13 PM

It's an unfortunately common problem with star-delta starting, one they never tell you about until after you have it. There is a phase shift when changing from star to delta and sometimes that happens when the field in the motor has not fully collapsed, essentially creating a situation similar to connecting two generators out of phase with each other. there is a massive voltage and consequent current spike, theoretically in excess of 2000% of the motor FLA, well above the instantaneous trips of the circuit breaker.

The best way to avoid it is to never use star-delta starting, that's my preference. but since you already have it you can try one other thing. You can either rebuild your starter to be a "Closed Transition" version, which is expensive, or you can try a cheaper fix. It's called "rolling" the conductors to try to shift that phase sequence to where you have a leading phase relationship instead of a lagging one.

Take ALL THREE of the conductors on the Delta contactor and move them over one pole; A to B, B to C, C to A. It doesn't change the rotation but it changes the phase shift relationship. Sometimes it works, sometimes it doesn't, you might get lucky.

Personally I would junk it and install a solid state soft starter, they are MUCH better.

There is a link to a paper that describes the problem.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Participant

Join Date: Jun 2011
Posts: 2
#2
In reply to #1

Re: Problem in Stardelta Starting

06/09/2011 1:48 PM

thanks for your valuable comments.I will change the connection 2mmarow and get back to you.I want to know one thing?.. same type of motor ,same starters,same mccb working fine for two compressors then what happen to this one?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Problem in Stardelta Starting

06/10/2011 12:26 PM

Luck (bad) of the draw I suppose; you have only a 33% chance of getting it wrong, 67% chance of getting it right. You have 3 systems, you hid the odds dead on!

That's actually an indication that rolling the conductors may work for you however.