Anonymous Poster #1

MCB for AC and DC

06/09/2011 10:31 AM

Hi All,

Can it be 3TPN DC breaker to AC supply VAC, or AC 3TPN breaker to DC supply 120VDC.

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: MCB for AC and DC

06/09/2011 12:01 PM

Due to the absence of a current zero in DC, it is quite usual to use permanent magnet blowouts in DC MCBs.

In AC MCBs, these are not required.

i don't know what you want to ask, but i am sure the above answers some part of what you want. Whether you know it or not.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: MCB for AC and DC

06/10/2011 5:56 AM

kvsridhar, would a breaker fitted with AC blow out coils work in the same way with DC?

This is just out of curiosity.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: MCB for AC and DC

06/10/2011 6:22 AM

Of course yes ! Better sometimes...

Permanent magnet blowout can be polarised, demanding that the +ve and -ve terminations be in specific way. Some clever designs are there which overcome this handicap.

Permanent Magnet field strength being fixed, the blowout effect is dependant on the field strength of the current flowing.

In a blowout coil,

(a) the blowout effect is impervious to the connections, it is always upwards, and

(b) the blowout force would be proportional to the square of the current, since it would flow both thru the coil and the arc. At low currents, this can become low, causing the arc to stick in one place. Such a current is called 'critical current' at which the CB may not work.

In larger CBs, where space is no problem, coils can be used, but in small MCBs, the tiny space prohibits the coils, and so permanent magnets are usually used.

But then, you probably know all this already, if so, sorry .

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #3

Re: MCB for AC and DC

06/10/2011 8:34 AM

Thanks kvsridhar, it's been years since I've worked on a DC breaker (it was a beast of a thing), I thought I was right in thinking there were coils in it. It burnt my legs when it opened under fault.

Again thanks.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: MCB for AC and DC

06/10/2011 9:07 AM

Oh, i am sorry to hear that. Must have been pretty bad.

Hold on, your legs got burnt? The arc blew downwards? Strange. Can happen if the winding direction gets reversed. No poka-yoke in those days perhaps.

More likely to happen with Shunt blowout coils, not with Series ones.

Shunt:

Series:

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: MCB for AC and DC

06/10/2011 7:32 AM

Why on earth are three phases needed on DC?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply