Displacer and DP LT are both dependent on specific gravity of the fluid in a drum / vessel. Please let me know the selection criteria or when I shall go for Displacer rather than DP measurement?
Thank you all in advance.
Pathfinder Tags: Displacer DP level transmitter
Re: Displacer vs. DP LT
06/15/2011 5:55 AM
A displacer can only operate relative to atmospheric pressure above the liquid level. So if the vessel is sealed and pressurised, a displacer cannot be selected, whereas a differential pressure instrument can be.
Good Answers: 53
06/15/2011 11:45 AM
Sorry PW, this is not correct. Displacers are successfully deployed into many pressurised applications. Boiler steam drums are one example and the reason they are preferred to DP cells for this purpose is that the dry leg of a DP level transmitter can gradually fill with condensation which will show a false low level.
06/16/2011 3:39 AM
Stream drum level by dP always has 'a wet leg' reference.
penttijp
Venezuela - Member - New Member
06/16/2011 7:56 AM
Friends,
I´m agree totally with Ace Boeringa, In our plants there are a lot of displacer working in pressurized vessels.
Regards
JP
Instruments-guy-SAV
06/16/2011 8:25 AM
This depends greatly on the type of vessel, turbulence, ease of making outside connections among many other things. Much like what type of car to buy. If you give your application(s), I can help.
penttijp
06/30/2011 11:26 PM
reference leg of DPT for STM DRUM is always wet. Condensate pot is provided.
07/01/2011 6:40 AM
Yes, I said the same before. Sadly some of the people replying do not know much about these systems.