Transformer Neutral Earthing

06/16/2011 3:23 AM

During inspection of electrical installations envisaged under a modernisation project in a steel plant in India,prior to charging, the concerned Electrical Inspector from CEA made an observation that the Neutral of the 6.6/11 kV ,7.5 MVA,DELTA/STAR Transformer should be connected to two separate Earth Electrodes through 50mmX6mm copper strip in place of galvanised steel strip even though the relevant regulation of CEA does not specify the material of the earth conductor.

My question is whether it is technically OK ? If yes, What should be the arrangement for connection between the copper strip and the galvanised steel clamp welded to the 100 mm dia G I pipe electrode in order to ensure proper contact with minimum resistance ?

Whether any bimetalic strip comprising of copper on one side and GI on the other side is available in the market ? If not,can a bimetalic strip of copper & aluminium be recommended for such application ?

Thanks in advance.

__________________
Learning is a never-ending process.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: Transformer Neutral Earthing

06/16/2011 9:37 AM

The EAF that i studied in our steel complex limited has four tap positions in which 1,2 positions are in star-star and 3,4 positions in star-delta(5MVA,11KV/250V)power transformer.Phase to Phase arching is done on molten metal bed.There was Amplidyne controlled and Thyristor controlled EAF.Don't know about earthing material dimensions.

Register to Reply Off Topic (Score 3)
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Transformer Neutral Earthing

06/16/2011 10:26 AM

The CEA is grossly incorrect in demanding a Copper Strip in place of a GI Strip. Indian Standard IS 3043 recommends Copper or Aluminium or Steel as Earthing Conductor or Protective Conductor Material - as long as appropriate sizing is done. You can quote from IS 3043 to the CEA Inspector.

But, the problem is these Inspectors think that they have jumped from heavens and you cannot argue with them. To satisfy his ego, you can tin or silver plate the Copper Strip and connect it directly to the GI Clamp, without any Bimetallic Washers.

Register to Reply Good Answer (Score 4)
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#4
In reply to #2

Re: Transformer Neutral Earthing

06/18/2011 5:17 AM

Thank you electricalexpert65 !

__________________
Learning is a never-ending process.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#3

Re: Transformer Neutral Earthing

06/18/2011 5:06 AM

As Per IS-3043, Earthing electrode when made up of GI or steel shall be not less than 6.3mm in thickness and when made up of Copper (Cu) shall be not less than 3.15mm in thickness.

In your case, You have used copper strip of size, 50mmX6mm, then there will be no problem.

Also I agree with ee65, that you can apply tin or silver paint on Copper Strip.

Vinu_Answers Sure_Answers

__________________
Sure Answers Always
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); hithuanand (1); spradhan (1); Vinu_Answers (1)

Previous in Forum: 690V Drives vs 6.6KV Drives   Next in Forum: Design of Earthpits

Advertisement