HI friends
I want to know how to design required earthpits in a place? is this based on load or area of cross section.
thanks
srinivas
CR4 Admin - email address removed
From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses. You can share this information via the CR4 internal messaging system.
Re: design of earthpits
06/16/2011 5:55 AM
Follow the codes applicable in the country of installation.
06/16/2011 6:02 AM
Refer IS:3043
Learning is a never-ending process.
Re: Design of Earthpits
06/16/2011 9:18 AM
http://cr4.globalspec.com/thread/69229 Does the link helped you?
Good Answers: 170
06/16/2011 10:12 AM
First step is knowing the soil resistivity of the location where you are planning to install the earth pits.
Second step is to decide whether you are going to install Pipe Earth Electrode or Plate Earth Electrode or Rod Earth Electrode or Strip Earh Electrode.
Having decided the above, what is the dimension of the earth electrode?
There are formulae in Standards to calculate the individual earth electrode resistance for each of the above types of earth electrodes. Calculate that for the earth electrode that you have chosen to install.
Decide what is the net earth resistance you want to have for your system.
The number of earth pits required = desired earth resistance / resistance to earth of the individual earth electrode.
06/16/2011 11:55 AM
Confused with the formula given.Can you give little more explanation on parallel connection and how the formula support it.
06/16/2011 11:37 PM
formula is confusing, could you pl tell clearly
if desired resistance is 1 ohm , resistance of earth of individual is 4 ohms
then required earthpits is = 1/4 , hope some confusion in formula
also if we considered 4 earthpits in parallel i will get 1 ohm, same 4 earthpits will withstand entire area pl explain
06/17/2011 3:55 AM
It depends upon the spacing of the electrodes. If they are less than one electrode-length apart, multiplying the number of earth rods does not give a similar divisor to the resistance.
The country code still needs to be followed, "off topic" or not.
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member
06/18/2011 5:55 AM
Dear Srinivas231,
In order to design or establish earthing system in any place, you need to consider the following things:
1) Purpose Of earthing.
2) Different types of earthing systems as per IS-3043 (TNS, TNC, TNCS, TTNS, TT etc.).
3) Soil resistivity of area where earthing system is to be installed. If the
4) Type of earthing electrodes and material.
5) Size of the earth electrode, refer http://cr4.globalspec.com/comment/737522
6) Calculation of net earth resistance of the system
7) Decide no. of earthpits.
8) If necessary, go for artificial treatment of Soil.
Pl. refer IS-3043 for better and clear undeerstanding.
VInu_Answers Sure_Answers
Sure Answers Always
06/20/2011 1:06 AM
"The number of earth pits required = desired earth resistance / resistance to earth of the individual earth electrode."
I would say both "electricalexpert65" & "Vinu Answers" are correct except the above formula as mentioned in their respective posts.
The correct formula is:
No. of earth pits = resistance to earth of individual earth electrode /Desired overall earth resistance.
This is because all the interconnected earth electrodes are in parallel.
06/21/2011 12:35 AM
thank you, but if individual earthpit resistance is 2 ohms if i want desired resistance of .5ohms i need only 4 earthpits for a plant is it correct
srinivas
06/21/2011 8:26 AM
You are right; a minimum of 4 earth pits will suffice in case the individual EP resistance is 2 ohms.
Depending upon the layout of your plant you may increase the No. of EPs which will further reduce the overall resistance of the plant.But make sure that the distance between the adjacent EPs is more than twice the length of the electrode for ensuring optimum use of each EP.
01/29/2014 12:52 AM
First u have to check the earth resistivity in ur plant .
01/29/2014 11:53 PM
You are right.This value is required to work out the resistance of each earth electrode as per the formula appearing in IS:3043.This can be measured through testing at the given site or it may be readily available from the drawings/documents of the existing plant.