Anonymous Poster #1

110V Line to Earth Ground

06/19/2011 9:42 PM

hi good am to all

i.ll just want to ask in regards to 110V, line to ground connection,

Our power system is 220V, 1Ø, 60hz -line line , we have a load unit with a line voltage of 110V. we try to connect our main source line to ground earth system to get a 110V source.. the result is 139V, with out load,

the problem is , when we switch on and load to 2 HP motor, the line input voltage was smoothly dropped to 90V for a certain second then continues decrease to 22V for a couple of second,

kindly give us some recommendation

tnxs

......

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Jun 2011
Posts: 8
#1

Re: 110V Line to Earth Ground

06/19/2011 11:30 PM

Good day mr. anonymous. First I would like to know how did you make your grounding system? Did you use a standard grounding rod (1/2"D X 3m)? If not you cannot solve your problem. Try to use a standard grounding rod, please let me know.

Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#2

Re: 110V Line to Earth Ground

06/20/2011 12:34 AM

You mentioned that your system voltage is 220V single phase line-to-line. To get a 110V take one hot line plus neutral. The grounding system is separate from neutral. Some urban ereas the utility power company provides 220V Line-to-neutral/ or 220V line-to-line plus neutral or simply 220V single phase 3-wire system. Minimum size of ground rod is 1/2 inch x 3m length directly driven into the earth/ground encase with inspection pit. Wrong is you can't pair hot line and ground line , right is you can pair one hot line to neutral line. Neutral line or wire is always insulated from any electrical equipment metal frame/s while ground wire is always bonded to any metal frame or panel board because it is a current continuity path when the load is energized. The correct connection of motor for 220V(line-line plus ground); for 110V(line-neutral plus ground), in short both 110V and 220V single phase rated motor are 3-wire system.

__________________
If there is a will... there is a way... No pain / No gain.
Reply
Member

Join Date: Jun 2011
Posts: 8
#5
In reply to #2

Re: 110V Line to Earth Ground

06/20/2011 8:42 AM

Thank you for your comment hentoyk, You are right, you cannot pair one hot line to the ground for a 220V line to line plus neutral system as what they did. So what is your recommendation for the problem to run the 2HP motor from the existing distribution system?

Reply
Anonymous Poster #1
#7
In reply to #2

Re: 110V Line to Earth Ground

06/20/2011 2:33 PM

hi,

with your suggestion for the standard connection of line to earth ground and a neutral line, we completely connect all the neccessary point of connection using 1/2Ø grounding bus bar considering also the interconnection of waterline pipes and structural reinforcement steel bar to add and get good earth resistance ,

what i observe and believed that i havn't get good earth resistance in our perimeter area, any recomendation where and how to get a good earth resistance...?

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: 110V Line to Earth Ground

06/20/2011 3:49 AM

The ground/earth conductor is there to operate the circuit protective device(s) in the event of a fault.

The correct connection is to live and to neutral. Current flowing ordinarily in the ground/earth conductor will eventually cause someone an electric shock.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Jun 2011
Posts: 8
#6
In reply to #3

Re: 110V Line to Earth Ground

06/20/2011 8:48 AM

I agree with you, however it was not clear in the problem if the existing line to line 220V system is a 3wire. If this is the situation what is your recommendation?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: 110V Line to Earth Ground

04/09/2025 3:03 AM

Anonymous Poster #1 would do best to engage the services of a qualified local Electrician before someone gets hurt/killed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4

Re: 110V Line to Earth Ground

06/20/2011 7:17 AM

I was going to as earlier, but I didn't--where are you? In the US, it is quite common to have what is known with variations of names like: "3 wire system", "120-0-120 system", or whatever. If you connect between the two lines you get 220-240 volts, if you connect line to the center wire (neutral), you get 110-120 volts.

If you are in some other country (or even some places in the US), you might not have that kind of system, and will have more difficulty getting 110 volts. If you're improvising by connecting between ground and one of the lines, you're creating a dangerous and unreliable system.

So, where are you, and what do you know about your power system?