1 Phase Miss

06/20/2011 12:19 PM

Hi dear,s,

please tell me that for example 1 phase miss of an E.L.C.B and load is divided on 2 phases then what will be in circuit. is it flashed after some time. or reduce it,s efficeincy.

Thank,s.

__________________
Ikram Shehzad
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 1 Phase Miss

06/21/2011 3:49 AM

A residual current circuit breaker looks for the instantaneous vector sum of all the currents flowing through it. If one phase is missing, and the vector sum of the remaining phases and neutral do not exceed its trip setting, the device will not operate. If they do, it will.