Dyn11 vs Dyn5

06/20/2011 11:26 PM

Anyone,

What the advantage or disadvantage of Dyn11 compare to Dyn5?

thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Dyn11 vs Dyn5

06/21/2011 1:04 AM

There is a good Wikipedia article on transformer vector groups. Each difference of one in vector number represents a 30° phase shift. A difference of 4 (or 8) is a 120° phase shift, and thus (I think), differences of 4 (or 8) can be made compatible by "rolling" the phases. Other differences are incompatible if paralleled.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Dyn11 vs Dyn5

06/21/2011 10:01 AM

Have you referred to J & P transformer book?

Register to Reply
Participant

Join Date: Jun 2011
Posts: 2
#3

Re: Dyn11 vs Dyn5

06/22/2011 12:34 AM

With regards to theory, there are no special advantages of Dyn11 over Dyn5. Practically when seen, the relative places of the phases remain same in Dyn11 as when compared to Dyn5. This is to say that if we are on the the HV side of the Transformer, and if we denote the phases as R Y B from left to right, the same phases on the LV side will be R Y B, but from Right to left.

This will make the Transmission lines have same colour (for identification) whether it is input to or output from the Transformer.

Register to Reply
3
Member

Join Date: Jul 2009
Posts: 5
Good Answers: 1
#4

Re: Dyn11 vs Dyn5

06/22/2011 4:51 AM

The only difference is the phase change as the 3 phase voltages go thro the transformer. A Dyn11 transformer, if abc terminals are connected to rst phases, will shift the output from "12 o clock" to "11 o clock" ie 30 degrees back.

A Dyn5 if connected the same way will advance the output to "5 o clock" ie 150 degrees forward.

The difference in output between the Dyn11 and Dny5 and is therefore 180 degrees.

In isolated applications there is no advantage or disadvantage. If however you wish to interconnect the secondary sides of different Dny transformers, you must have compatible transformers, and I dont think that can be achieved if you have a Dyn11 among a group of Dyn5's and vuce versa.

If you cross phase a Dny1 by connecting acb to rst, you can create a secondary 3 phase system which is 60 degrees displaced from the Dyn1, equivalent to a Dyn11.

Register to Reply Good Answer (Score 3)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); rbnwatson (1); Tornado (1); vijaykumarkosuri (1)

Previous in Forum: three phase motor to single phase supply   Next in Forum: Motors and Controllers Price Range..

Advertisement