by:
K.Sivakumar, Manager-Training, Larsen & Toubro, Switchgear Training Centre,
Coonoor (T.N.)
*****
Introduction: About 70% of the electrical engineers working in industry happen to
work mainly on the Low Voltage Switchgear. But, unfortunately, this subject is
not paid enough attention in our electrical engineering academic curriculum.
Hence, when the field electrical engineer goes through the manufacturers'
catalogues/data sheets of low voltage switchgear, they are bemused. The
switchgear specification terminology appears a big jargon for them. An attempt
is made in this article to demystify the switchgear jargon.
Every type of switchgear will have certain set
of characteristic quantities associated with it. These characteristic
quantities are normally stated in form of ratings or specifications in the
product catalogue supplied by the manufacturer. A few of the specifications are
also marked on the nameplate of the equipment. For a user of switchgear, it is
important to know about what these characteristic quantities mean. Following is
the brief description for commonly used characteristic qualities.
Voltages: An equipment is defined by the following
voltages:
Rated Operational Voltage (Ue): It is that value of voltage, which
combined with a rated operational current, determines the application of the
equipment and to which the relevant tests and the utilization categories are
referred. For single pole equipment, the rated operational voltage is generally
stated as the voltage across the pole. For multiple pole equipment, it is
generally stated as the voltage between phases.
Rated Insulation Voltage (Ui): It is the
value of voltage to which dielectric test voltage and creepage distances are
referred. In no case shall the maximum the value of Ue should be
more than Ui.
Rated Impulse Withstand Voltage (Uimp): It is the peak value of an impulse
voltage of prescribed form & polarity, which the equipment is capable of
withstanding without failure under specified conditions of test & to which
the values of the clearances are referred. The rated impulse withstand voltage
of an equipment shall be equal to or higher than the values stated for the
transient over voltages occurring in the circuit in which the equipment is
fitted.
Over voltage category
Preferred Values of Uimp, kV
(1.2/50µs)
IV
Origin of installation level
6
III
Distribution circuit level
4
II
Load (equipment) level
2.5
I
Specially protected level
1.5
Table 1: Preferred values of Uimp
for a nominal supply system voltage of 240/415V, in case of over voltage
protection by surge arrestors according to IEC:
Rated Control Circuit Voltage (Uc):
It is the
voltage, which would appear across the "a" contacts in the control circuit.
Rated Control Supply Voltage (Us): It is the voltage at which
generally auxiliary circuits and more precisely the control circuits are
operated or to which they must be connected for correct operation. A
distinction is made between Uc & Us. Us
may be different from Uc, due to presence of built in transformers,
rectifiers, resisters etc. The rated control circuit voltage and the rated
frequency, if any, are the values on which the operating and temperature rise
characteristics of the control circuit are based. The correct operating
conditions are based upon a value of the control supply voltage not less than
85% of its rated value, with the highest value of control circuit current
flowing, nor more than 110% of its rated value.
Currents: An equipment is defined by the following
currents:
Conventional free air thermal current (Ith): It is the maximum value of current
as stated by the manufacturer to be used for temperature-rise tests of
unenclosed equipment in free air. The switching device must be capable of
conducting this test current without the temperature rise limits given in the
relevant Indian Standard being exceeded (temperature rise limits of terminals
as per IS is 70oC for silver plated copper for all switchgear
(except circuit breaker). It must be at least equal to the maximum value of the
rated operational current of the unenclosed equipment in eight-hour duty. It is
not a rating & is not mandatorily marked on the equipment.
Conventional enclosed thermal current (Ithe): It is the value of current stated
by the manufacturer to be used for the temperature-rise tests of the equipment
when mounted in a specified enclosure. Such tests are mandatory if the
equipment is described as enclosed equipment in the manufacturer's catalogues
& normally intended for use with one or more enclosure of specified type
& size. It shall be at least equal to the maximum value of the rated operational
current of the enclosed equipment in eight-hour duty. If the equipment is
normally intended for use in unspecified enclosures, the test is not mandatory,
if the test for Ith has been made. It is not a rating & is not
mandatorily marked on the equipment.
Rated Operational Current (Ie): It is stated by the manufacturer
and takes into account the rated operational voltage, the rated frequency, the
rated duty, the utilization category & the type of protective enclosure, if
applicable. Switchgear may have several rated operational currents. In the case
of equipment for direct switching of individual motors, the indication of a
rated operational current may be replaced or supplemented by an indication of
the maximum rated power output, at the rated operational voltage considered, of
the motor for which the equipment is intended.
Rated uninterrupted current (Iu): It is a value of current, stated
by the manufacturer, which the equipment can carry in uninterrupted duty (a
duty in which the main contacts of equipment remain closed, whilst carrying a
steady current without interruption for periods of more than eight hours i.e.
weeks, months or even years).
Rated current (In): This rating is defined for circuit
breaker & fuses. For circuit breaker, the rated current is the rated
uninterrupted current (Iu) & is equal to the conventional
free-air thermal current (Ith). For fuse-link, the rated current is
that value of current, which it can carry continuously without deteriorating,
under specified condition.
Rated Frequency: It is the supply frequency for which equipment is designed & to
which the other characteristic values correspond. The same equipment may be
assigned a number or a range of rated frequencies or be rated for both A.C. and
D.C.
Utilization Category: It is a
combination of specified requirements related to the conditions in which the
switching device or the fuse fulfills its purpose, selected to represent a
characteristic group of practical applications. The specified requirements may
concern, for example, the values of making capacities (if applicable), breaking
capacities & other characteristics, the associated circuits & the
relevant conditions of use and behavior.
Normal Load & Overload
Characteristics: The ability to make & break currents under normal load
& overload conditions is stated in terms of following two ratings:
Rated Breaking Capacity: The rated breaking capacity
of an equipment is a value of current, stated by the manufacturer, which the
equipment can satisfactorily break under specified breaking conditions. The
breaking conditions which shall be specified are: a) the phase-to-phase voltage
across the supply terminals of the equipment after the breaking of the current
& b) the characteristics of the test circuit. The rated breaking capacity
is stated by reference to rated operational current, according to relevant
Indian Standard (IS) on the product. An equipment shall be capable of breaking
any value of current up to and including its rated breaking capacity. For A.C.,
it is expressed by the r.m.s. value of the symmetrical component of the
current.
A temperature rise test is not compulsory. The breaker may not be
capable of carrying its rated current continuously. Limited shift of the
overload release characteristic curve is permissible.
A temperature rise test is to be performed with rated current. The
breaker shall be able to conduct its rated current without prior maintenance.
Shift of O/L characteristics not permissible.
Rating Making Capacity: The rated making capacity of an
equipment is a value of current, stated by the manufacturer, which the
equipment can satisfactorily make under specified making conditions. The making
conditions which shall be specified are: a) the phase-to-phase voltage across
the supply terminals of the equipment just before the making of the current
& b) the characteristics of test
circuit. The rated making capacity is stated by reference to rated operational
voltage & rated operational current, according to relevant Indian standard
(IS) on the product. An equipment shall be capable of making any value of
current up to and including its rated making capacity. For A.C., it is
expressed by the r.m.s. value of the symmetrical component of the current.
Short Circuit Characteristics: Short circuit currents
may be encountered during current making, during current carrying in closed
position & during current interruption. The ability of the equipment to
make, carry & break short circuit currents is stated in terms of one or
more of the following ratings:
Rated Short-Circuit Making Capacity (Icm): The rated short-circuit making
capacity of an equipment is the maximum value of short circuit current, stated
by the manufacturer, which the equipment can satisfactorily make at the rated
operational voltage, at rated frequency and at a specified power factor of A.C.
It is expressed as the maximum prospective peak current, under prescribed
condition.
Rated Short Time Withstand Current (Icw): It is the current
that an equipment can carry without damage during specified short time under
prescribed conditions of use and behavior.
Rated Short-Circuit Breaking Capacity (Icn): The rated short-circuit breaking
capacity of an equipment is the maximum value of short circuit current, stated
by the manufacturer, which the equipment can satisfactorily break at the rated
operational voltage, at rated frequency and at a specified power factor of A.C.
It is expressed as the r.m.s. value of the a.c. component, under prescribed
condition.
Rated ultimate short circuit breaking capacity
(Icu): It is the value of ultimate short circuit breaking capacity (a breaking
capacity for which the prescribed conditions according to a specified test
sequence do not include the capability of the circuit breaker to carry its
rated current continuously) assigned to that circuit breaker by the
manufacturer for the corresponding rated operational voltage, under specified
conditions. It is expressed as the value of the prospective breaking current,
in kA (r.m.s.).
Rated service short circuit breaking capacity
(Icn): It is the value of service short circuit breaking capacity (a breaking
capacity for which the prescribed conditions according to a specified test
sequence include the capability of the circuit breaker to carry its rated
current continuously) assigned to that circuit breaker by the manufacturer for
the corresponding rated operational voltage, under specified conditions. It is
expressed as the value of the prospective breaking current, in kA (r.m.s.),
corresponding to one of the specified percentages of the rated ultimate short
circuit breaking capacity.
Utilization Category A (Ics as a % of Icu)
Utilization Category B (Ics as a % of Icu)
25
50
75
100
-
50
75
100
Table 3: Standard ratios between Icu
& Ics
Time Intervals: Closing & opening
operations of a switching device may be defined by following times:
Opening Time: It is the interval of time between
the specified instant of initiation of the opening operation & the instant
when the arcing contacts have separated in all poles. The instant of initiation
of the opening operation means the instant of the application of the opening
command, e.g. energizing the release etc. In case of a directly operated
circuit breaker, the instant of initiation of the opening time is the instant
of initiation of a current large enough to cause the circuit breaker to
operate. In the case of a circuit breaker operated by any form of auxiliary
power, the instant of initiation of the opening time is the instant of
application of the auxiliary power to the opening release. For circuit breakers
opening time is commonly referred to as tripping time, although, strictly
speaking, tripping time applies to the time between the instant of initiation
of the opening time and the instant when the opening command becomes irreversible.
Arcing Time: It is the interval of time between
the instant of initiation of the arc in a pole or a fuse & the instant of
final arc extinction in that pole or that fuse. In a multiple-pole switching
device, it will be the interval of time between the instant of the first
initiation of an arc & the instant of final arc extinction in all poles.
Break Time: It is the interval of time between
the beginning of the opening time of a mechanical switching device (or the
pre-arcing time of a fuse) & the end of the arcing time.
Make Time: It is the interval of time between the
initiation of the closing operation and the instant when the current begins to
flow in the main circuit.
Closing Time: It is the interval of time between
the initiation of the closing operation and the instant when the contacts touch
in all poles.
Pre-arcing Time: It is the time between the
commencement of a current large enough to cause the fuse element(s) to melt
& the instant when an arc is initiated.
Operating Time: It is the sum of pre-arcing &
the arcing time.
Operational Life: It is the duration for which electrical equipment
operates reliably (or is expected to operate reliably) under normal specified
operating conditions. The operational life of a switching device is expressed
as the number of make-break operations the device will
perform.
Electrical Life: It is the number of on-load
switching operations, which the device can perform without any repair or
replacements. The electrical life depends on the utilization category, the
rated operational current & the rated operational voltage.
Mechanical Life: It is the number of no-load switching operations
(i.e. with no current flowing through the poles) which the switching device can
perform without mechanical failure.
Service Conditions: The switchgear manufacturer claims
the ratings after testing as per the procedures specified in the standards. The
standards also specify the service conditions under which the tests are to be
carried out. Following are the service conditions considered:
Ambient air temperature: It is the temperature existing in
the vicinity of the equipment if supplied without enclosure or in vicinity of
the enclosure if supplied with an enclosure.
Altitude: It is the height above the sea level where
the equipment is going to be installed.
Humidity: It is the moisture content in air expressed in
percentage (i.e. relative humidity).
Pollution degree: The pollution degree refers to the
environmental conditions for which the equipment is intended. For equipment
intended for use within an enclosure or provided with an integral enclosure,
the pollution degree of the environment in the enclosure is applicable. Unless
otherwise stated by the relevant product standard, equipment for industrial
application is generally for use in pollution degree 3 environment according to
which conductive pollution occurs, or dry non-conductive pollution occurs which
becomes conductive due to condensation.
Service Conditions
Normal Values
Ambient temperature:
Max. allowable value
Max. allowable value of 24 hour average
Lowest allowable value
+ 40°C
+ 35°C
- 5°C
Humidity: Relative humidity
50% at 40°C
Altitude: Max. altitude (above sea level)
2000m
Table 4: Normal service conditions in terms of
Indian Standards.
Switchgears intended to be used in conditions
other than normal service conditions, should be designed accordingly or used
according to the relevant product standard, where applicable, or according to
agreement between manufacturer & user. Many times certain correction
factors are employed in case actual service conditions differ from normal.
Conclusion: It is hoped that at least some of the
switchgear jargons are clarified above. Further reference can be made to IS
13947 (Specification for Low Voltage Switchgear & Controlgear) & IS
13703 (Specification for Low Voltage Fuses).