i have a three phase motor 11Kw, 21 A for delta & 12 A for star
i want to know what is better for this motor DOL starter or star delt starter,
and how can i select the correct ratings for the contactors and overload and the main circuit breaker.
Re: DOL or star delta starter
06/21/2011 7:13 AM
Star delta starting is better for the wiring and the upstream supply.
The motor's full load current is used to select control components. That and British Standard 7671.
Good Answers: 170
06/21/2011 9:45 AM
There is no hard and fast rule as to the option of going for a DOL Starter or a Star-Delta Starter for a given motor. If you draw power from an LT Mains, then the line voltage drop due to DOL motor starting, might affect your neighbouring customer, causing a social issue. If you draw power from a HT supply, there are no such issues but nevertheless, the motor would be subjected to incrased thermal stress on a DOL starting, thus reducing its life. But, DOL is cheaper. Whereas, star-delta starting reduces the starting current and thus the thermal stress on the motor, but, it is costly and also the starting torque would reduce by 3 times. Genral practice in industry for a 11kW motor is to go for a DOL starter.
06/22/2011 2:28 AM
Use star-delta starter with closed transition resistors to avoid surge during c/o
pnaban
06/24/2011 8:13 AM
Well for your selection to your contactor and overload relay you can select based according to the delta connection ,Please note if you are design is on star / delta connection then you can select u r components as according to delta or if your going to dol connection then you have to select based on your name plate full load current.
06/24/2011 7:36 PM
For selection of contactors refer "Telemecanique" product catalog and for CB refer "Hager" product catalog.