Help on 5th Harmonic Tuned Filter Required

06/23/2011 12:55 AM

Dear Designer Guru (s) !

Need your help in designing 5th Harmonic Tuned Filter for VFD Powered Machine Application, wherein two machines are powered by 240 KW UPS (made out of 3 No. APC Silcon 80 KW UPS running in parallel load sharing mode). Even though the UPSs have low THDi at Input (about 4%) due to PWM Front End; the THDi of current drawn by the the Machines powered by the UPS is high resulting in regular failure of UPS Output Capacitors and at times it's Electronics. The actual site data on single machine load is as follows :

KW

KVA

KVAr

P.F.

DPF

Frequency

Voltage

THD (V)

Current

THD (I)

KF

%age

3rd Harmonic

5th Harmonic

7th Harmonic

9rd Harmonic

11th Harmonic

13th Harmonic

17th Harmonic

19th Harmonic

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

Freq.

Current

%age

Degree

R-Phase

UPS-I

1010.63.200.90.9549.7240.21.8%47.332.4%5.994.6%149.60.02.70.0249.113.127.8%127.0348.86.012.8%-4.0448.41.32.7%56.0548.13.88.1%153.0648.42.14.4%-119.0847.01.63.4%75.00.00.00.0%0.0

UPS-II

9.6510.23.300.910.9549.8239.91.8%43.524.7%3.496.7%0.00.00.00.0248.99.922.9%138.0348.23.47.8%4.0447.30.51.2%-7.2546.21.12.6%159.0646.71.22.7%-50.00.00.00.0%0.00.00.00.0%0.0

UPS III

9.810.33.110.920.9549.8239.91.7%44.524.0%3.397.1%0.00.00.00.0248.79.721.9%-142.0348.23.98.9%5.20.00.00.0%0.0547.21.02.2%156.0646.70.92.1%-62.00.00.00.0%0.00.00.00.0%0.0

Y-Phase

UPS-I

1010.32.260.920.9849.92402.0%45.230.0%4.995.5%149.90.91.9157.0249.811.625.4%-162.0349.75.411.1%-11.0450.01.43.0%90.0550.02.55.5%87.0650.01.73.8%150.0850.01.32.8%110.00.00.00.0%0.0

UPS-II

10.110.42.400.930.9749.8240.12.0%45.026.8%4.096.4%149.51.32.810.0249.111.024.3%-150.0348.83.88.3%0.0448.41.22.5%-159.0548.61.94.2%127.0648.41.12.4%143.00.00.00.0%0.00.00.00.0%0.0

UPS III

10.310.82.900.920.9649.8240.11.9%47.125.1%3.696.7%149.30.91.9-420.0248.910.823.1%-144.0348.44.08.7%220.0448.00.81.8%159.0548.01.53.2%142.0647.70.92.1%-99.0847.01.02.2%57.00.00.00.0%0.0

B-Phase

UPS-I

1010.43.010.920.9649.7239.71.8%45.428.3%4.295.9%149.20.81.7123.0248.711.224.8%-150.0348.25.111.3%14.0477.70.71.6%150.0547.22.14.7%120.0646.61.63.4%101.0845.70.61.2%36.00.00.00.0%0.0

UPS-II

1010.42.770.930.9649.7239.71.8%44.425.3%3.996.8%150.10.61.4177.0250.09.621.8%-151.0349.74.19.3%23.0449.10.92.0%52.0548.61.12.4%122.0647.71.22.8%102.0847.01.02.3%40.00.00.00.0%0.0

UPS III

9.8410.32.990.920.9649.8239.71.8%44.524.5%3.697.0%149.31.12.5-45.0248.910.022.4%-130.0348.43.37.4%-6.0448.01.94.3%-139.0547.52.65.9%164.0647.01.02.1%-140.0847.01.22.7%68.00.00.00.0%0.0

Thanks & Regards,

Sanjeev

__________________
Karma is Dharma
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Feb 2007
Location: Aberdeen, Scotland
Posts: 393
Good Answers: 21
#1

Re: Help on 5th Harmonic Tuned Filter Required

06/23/2011 4:06 PM

Would love to help Sanjeev but you've lost me. Don't have a clue what you are on about.

Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#7
In reply to #1

Re: Help on 5th Harmonic Tuned Filter Required

06/25/2011 1:39 AM

Gurudev !

Just need some references & concrete tutorials to design Tuned Filter for 200 KW Machine Load (having THDi & other data as in the original question) powered by 240 KW UPS (Power Source)...As you see only 5th Harmonic is about 26-27%, tuned filter for 250 Hz to counter the existing 250Hz current will serve the purpose.

Hope I could revive your loss of attention..... Just a emotion.. I am actually feeling suffocated for not being able to solve this... my college notes have also been thrown in the dustbin by my dear wife..... please help me all you noble souls... pleeeeeeeeze..

Rgds

Chhotu

PS : If this spoils your weekend mind-share, please ignore the request... luv u all !

__________________
Karma is Dharma
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#2

Re: Help on 5th Harmonic Tuned Filter Required

06/23/2011 10:56 PM

You are getting high harmonic current because of - 1. the UPSs are not generating a sine wave, . . or . . 2. the load not being linear.

I would assume that the generated voltage is more trapesoidal - than sinusoidal, . . . resulting in all of the harmonic currents.

You are not getting 3-rd, 9-th, and similar harmonics because of thee-phase operation.

Installing a 5-th harmonic filter - will do more harm than good.

Correct the voltage waveshape.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Help on 5th Harmonic Tuned Filter Required

06/24/2011 1:28 AM

you need a new drive, your THD should be less that 5% I to conform with 519 IEEE.

I doubt if you will achieve that with the drive you have

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#8
In reply to #3

Re: Help on 5th Harmonic Tuned Filter Required

06/25/2011 2:30 PM

I hope that you meant 5% THD V (which they seem to meet). The THD I can easily be in the 10%-15% of the feeder capacity (Total Demand) depending on the installation.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#4

Re: Help on 5th Harmonic Tuned Filter Required

06/24/2011 2:17 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Power-User

Join Date: May 2011
Location: Chennai, TAMIL NADU, INDIA
Posts: 108
Good Answers: 1
#5

Re: Help on 5th Harmonic Tuned Filter Required

06/24/2011 10:24 AM

Dear Chhotu,

I agree with view of Mr. olehwi (COMMENT No.2) that 3rd Hormonics and Multiples of 3rd Hormonics are NULLIFIED or ANNULLED on account of STAR WINDING of ALTERNATOR. Therefore 3rd and 9th Hormonics as referred in your Table is TO BE IGNORED.

SINUSOIDAL WAVE FORM for the OUT-PUT SUPPLY is a MUST. Pl. get it checked. Pl. provide a circuit diagram and what is the size of Earting Conductor provided and what is the Earth Resistance.

What does the equipment supplier says.?

I have also phased a similar problem but EARTHING was defective, and after setting right the problem is solved. But personally I feel some thing more is to be done.

However our CR4 members will be in a position to share their knowledge and advise.

Thanks,

RAJESWARI

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: Help on 5th Harmonic Tuned Filter Required

06/24/2011 4:37 PM

There are 4 answers to your question:

1,. The UPS and its capacitor was never specified for such an application. Capacitors are specified and limited for such purposes in any switching power supplies.

2,. The harmonics exceed manufacturer's specification.

The next two involves you in design, testing and manufacturing, so be advised.

3,. Properly sized chokes in all legs will cut down on harmonics

4,. A diplexer: high pass / low pass combination. The low pass puts power thru, the high pass terminates harmonics in a resistor.

I would assign 70% to 1,. 25% to 2,. and less than 5% to 3,. and 4,. success.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9

Re: Help on 5th Harmonic Tuned Filter Required

06/25/2011 2:33 PM

Any supplementary filter will have some degree on interaction with the UPS. Refer to the UPS manufacturer for the specific.

Do not follow the casual advises of simply installing a tuned capacitor bank. It is much more difficult than this. Have a real pro look into this problem and design a proper passive filter. It must be sized properly and tuned to avoid resonances with the UPS control loops.

From my experience, do not install an active filter on the load either. Its control loop is likely to interact violently with the UPS control loop. Not happy mix.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.