Explosion Proof Motors with Internal Temp Cutoff?

06/23/2011 8:42 AM

I am swapping motors in an existing plant built in the 60's. There are a bunch of motors which have temp switches internally wired to high temp shutoff relays in the motor connection head.

Has anyone seen one of these recently? Any manufacturers make them? The starters and existing conduit runs don't have a PTC / Temp Switch cable to run back to the starters.

My motor supplier doesn't seem to help. Any leads would be helpful.

Register to Reply
Pathfinder Tags: Explosion Proof motor safety XP
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/23/2011 9:43 AM

It is more common of late to contruct a motor with (a) temperature device(s) embedded in the windings, and to run a cable from it/them to the motor starter cubicle to carry out the control functions there.

The difficulties of changing-out heritage motors that are configured differently are appreciated.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Apr 2011
Posts: 27
#2
In reply to #1

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/23/2011 10:27 AM

Yes, this it the way we would build new plants.

Baldor has the internal high temp disconnect in the motor connection head but only up to 1 1/2 hp. I need 2 and 3 hp motors.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 1:37 AM

I remember seeing these in the mid 70's, these days motors have temp probes connected to relays that shut down the motor at the MCC.

As a suggestion which you have realised I guess, that new motors and that extra bit of control cabling is now required to have new motors with temp protection.

It is unusual to have Ex motors with moving internal contacts/relays these days.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 5:07 AM

I think it boils down to your going to have to run a new control cable to the motor for whatever type of temperature sensor you decide to use.

I've never come across FLP motors with internal disconnects, but the motors I worked on were a lot bigger

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 17
#5

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 6:43 AM

Dear Sir,

Such totally enclosed flameproof motors 550 volt, 120 KW were being used by

me in early 1973 to 1976. Motors were Russian make heavy duty,water cooled

with temperature sensor inside windings with tripping relay like relay contacts

in a FLOAT switch. Relay had gone defective sometime in 1974. It had to be

bypassed as there was no alternative. But motor was running very effectively.

At that time motor was dissambled and rotor & windings were looking like a NEW

Motor. If necessary motor can be used by convinient temperature sensors and

taking out control cable outside to starter panel.

Just for acedemic interest these heritage motors may be saved.

Register to Reply
Associate

Join Date: Apr 2011
Posts: 27
#6

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 8:25 AM

Yes, I can add a temp sensor to the motor case and high temp interlock, but will it be considered "safe", as safe as a new UL / FM approved motor?

I install temp sensors and interlocks all the time, but is there anything else which makes it meet code other than the "nameplate"?

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8
In reply to #6

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 1:47 PM

you should be able to get an EX motor with the temp probe fitted in the stator, that would be more in line with the code rather than a DIY job of fitting the temp probe and trying to retro-fit the correct Ex junction box etc for the probe terminations.

The pre-fitted probe terminations would then be in the motor terminal junction box, all you need to do, as TonyS suggested, is install the correct type of cable plus EX glands for motor power and an additional Ex gland on your temp feedback cable to your MCC.

Yes, you have to run another cable, but as I see it there is no other option, not these days. Better safe than sorry!!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #8

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 1:55 PM

Any modification to the motor negates the FLP certificate!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10
In reply to #9

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 4:14 PM

I wasn't suggesting that he makes any mods, the probe should be fitted to the stator, the terminations should be in the terminal box, and the knock outs for the temp probe cable should be there. What I did say was DO NOT attempt to modify it...

you should be able to get an EX motor with the temp probe fitted in the stator, that would be more in line with the code rather than a DIY job of fitting the temp probe and trying to retro-fit the correct Ex junction box etc for the probe terminations.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/24/2011 1:33 PM

The main thing is that the cable and glanding meet FLP requirements. If it doesn't the whole thing is invalid.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 17
#11

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/25/2011 12:08 AM

Agreed with comments of Mr. Tony S. FLP features,cable glands and terminal cover gaps should not be disturbed. Then it's ok.But why the temperature disconnect inside the motor required when it can be conviniently tripped from the starter.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12
In reply to #11

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/25/2011 2:55 AM

If you read the original posting, its and OLD motor built to a design standard no longer with us, the OP want to replace these old motor and still wants to keep the thermal protection, which you already know. Thats how and why the thermal trip is inside the motor, not as todays modern motor's, with the trips located remotely.

__________________
The square root of nothing is what you make it!
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 17
#13
In reply to #12

Re: Explosion Proof Motors with Internal Temp Cutoff?

06/25/2011 3:59 AM

Thank you Brich. Heritage motors must be kept intact till it is possible.

Register to Reply