Steam Seal Pressure Variation

06/23/2011 2:51 PM

We are operating 8.19 MW Nuovo Pignone Extraction/Induction/condensing type steam turbine having HP/LP turbines.

We are facing problem of fluctuating seal steam header pressure, for which our observation is sluggish response of supply seal steam control valve but the condition continue to persist after bypassing the valve.

What are the possible causes of fluctuating seal steam header pressure?

What are the consequences of operating steam turbine at its full capacity with such variation in seal steam header pressure? It gauge pressure varies from 0.1 kg/cm2 to 0.9 kg/cm2 .Normal operation value is 0.2kg/cm2.

Any one having experience same problem, expert opinion required.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#1

Re: Steam Seal Pressure Variation

06/23/2011 5:04 PM

How old is the system and what is the typical Si content of the boiler make-up water?

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Reply
Active Contributor

Join Date: Jun 2011
Posts: 14
#2
In reply to #1

Re: Steam Seal Pressure Variation

06/24/2011 7:31 AM

system is 20 years old and Si content of the boiler make up water is less than 10ppm.

__________________
aleeehsan@gmail.com
Reply
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#3
In reply to #2

Re: Steam Seal Pressure Variation

06/24/2011 9:34 AM

My initial instinct is to say your regulator is gummed up. My first course of action would be to disassemble it, clean each part, and check to make sure they're all free to move as designed.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#4

Re: Steam Seal Pressure Variation

06/24/2011 11:41 AM

The valve can have a gumming issue, or buildup.

You can also try to modify the control parameter once the valve has been checkd to make it act a bit like a PD controller.

Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#5

Re: Steam Seal Pressure Variation

06/24/2011 12:57 PM

Loss of vacuum an obvious answer due to too much air being sucked in at the LP end. What is or where is source of steam to header? Any impediment there?

Generally running source is from inlet end of LP or from inter-stage tap to the exhaust end with start-up steam supplied from system. Is this your arrangement? Normally additional supply not required while operating. The HP should provide it's own outflow and should need only a supply when starting up or at idle.

The high number says that you have plenty of supply (0.9). The low number would be my concern. Perhaps your LP labyrinths are worn and need replacement.

__________________
Spinco
Reply
Power-User

Join Date: Dec 2010
Posts: 377
Good Answers: 20
#6

Re: Steam Seal Pressure Variation

06/25/2011 1:56 PM

Normally sealing steam is required during start-up to maintain the vacuume and it is cut off after normal loading of turbines. Is it mendatory in your turbine to keep sealing steam on? High sealing steam pressure cause lot of steam comming out of of seals and can enter in the bearing housing causing condensate contamination problem in oil.

If you are drawing sealing steam from a high pressure steam header, control valve may not be able to control the out let pressure as flow remains very low. You can try putting some orifice at up stream of control valve so that limited flow comes to control valve.